Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,840
  • TAC IA Series 1,823
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 329
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 505
    • 506
    • 507
  • Next »

EBO Cloud Connectivity Certificate Errors

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue Validation of SSL Certificate does not work Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Building Operation Space-Logic Server (AS-X) Cause Cloud Connectivity makes use of the Baltimore CyberTrust Root Certificate for communication to the cloud, and often this certificate is not updated due to lack of maintenance routines on the Windows Server. Resolution Run Windows Update: On the server running the ES/EC, run Windows Update and make sure the Operating System is updated to the latest maintenance version available. Manually update certificate:  On the server running the ES/EC, go to https://curl.se/docs/caextract.html using a web browser and follow the instructions to download a collection of the most commonly used certificates on the web that are up to date. Click on the start-menu, type in ”certmgr” and press enter. Navigate to Trusted Root Certification Authorities/Certificates Under Trusted Root Certification Authorities, right-click the Certificates folder and select ”All Tasks > Import…” Follow the guide, click ”Next” and then locate the file you downloaded in Step 2a (make sure you filter to All Files). Click ”Next” on all steps and then click ”Finish”.
View full article
Lieutenant JG LocNguyen Lieutenant JG
‎2025-04-15 04:35 PM

on ‎2025-04-15 04:35 PM

Labels:
  • EcoStruxure Building Advisor
  • EcoStruxure Building Expert
  • EcoStruxure for Retail - IMP
293 Views

Mixing Low and High voltage on same side of an CRS-HH-REL-10

Warning Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source. Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices. Issue Why is it recommended to not mix high and low voltage connections on the same side of an CRS-HH-REL-10? Product Line EcoStruxure Building Operation. Environment Building Operation Room Controller (RPC) 24 V Building Operation Room Controller (RPC) 230 V Cause According to the documentation, it is not recommended to mix high and low voltage connections on the same side of the device.   Resolution There must be a minimum distance between terminals connected to High Voltage and terminals connected to Low Voltage of at least 5.5 mm to prevent the chance of voltage creep between the terminals.
View full article
Kirk MikaelKrantz Kirk
‎2025-04-14 04:20 PM

on ‎2025-04-14 04:20 PM

Labels:
  • EcoStruxure Building Operation
294 Views

Niagara 4.15 Station Bog File Encryption Changes

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue Bog File Encryption Changes in 4.15 Product Line TAC IA Series Environment I/A Series N4 Enterprise Server I/A Series N4 Jace 9000  Cause In Niagara 4.15, to continue to provide the best security practices, the user password hashes are now included in the encryption by the system passphrase. Resolution The system passphrase was introduced in Niagara 4 to provide additional protection to sensitive data from the Niagara system. Prior to Niagara 4.15, this included all reservable passwords (such as Niagara Network, database connection passwords, etc.), excluding the user's passwords as those are protected by being hashed. If you do not have the system passphrase for a station and need to unlock it through Workbench, both the user and encrypted data such as passwords will be removed where prior to Niagara 4.15 the user were left untouched as they are hashed. If you are copying a station from a remote host which you do not have the system passphrase for, you will need to reset the passphrase to successfully copy the station onto a new remote host. You will be required to enter the passphrase to edit or modify users or encrypted properties such as password fields for email, Niagara Network, etc. Prior to Niagara 4.15, you could edit and modify users without the passphrase, in Niagara 4.15 this will require the passphrase to decrypt the users.   Operation Niagara 4.14 Niagara 4.15 Modifying users in offline station bog file Users can be modified without entering the station bog file passphrase Station bog file passphrase is required to modify users Reset station bog file passphrase Removes reversable client passwords such as email, Niagara Network, etc. Hashed user passwords are not impacted Removes both reversable client passwords and hashed user passwords Understanding the System Passphrase in 4.15 Workbench or Supervisor When Niagara is installed on the engineering or supervisor device for the first time, the user will set the passphrase for that device. NOTE: When setting system passphrases, make sure that you take note of what they are. These should be shared with the owner of the building/site as the passphrase is owned by the device. You can change the system passphrase in the Platform Administration screen. You will be required to enter the current passphrase in order to successfully change it to a new passphrase, highlighting the importance of providing it to the owner of the building/site. JACEs & Remote Niagara Devices The passphrase is set during the commissioning process of the remote device. The remote device's passphrase can also be changed through the Platform Administration view with the same requirements as changing the Supervisor/device's passphrase.   Station Bog File Passphrases In 4.15, you will have the option to encrypt the new station with either the local system passphrase or a custom passphrase in the New Station Wizard. This passphrase is required to unlock the bog file in the user home when configuring encrypted properties as well as when copying this station onto a remote host. New Station Wizard: Note: When selecting the "Use the system passphrase" option, this is the passphrase for the local host (Workbench) Unlocking the station in the User Home: Copying the Station to a remote host with a different passphrase: Understanding how the station passphrase changes when using the Station Copier When a station from a remote host to your local host, the passphrase which is encrypting the data will be the system passphrase of the remote host. Copying a station from your local host to a remote host: For a station that originated on your local host with a passphrase encrypting its sensitive data, once you enter the current station bog file passphrase and successfully copy the station onto the remote device, it will utilize the system passphrase of the remote device when copying from the remote device back to your local host. Copying a station from a remote host to your local host: When a station is copied from the remote host, it will automatically be encrypted with the system passphrase of that remote host.   What do I do if I do not know the system passphrase of the remote host I copied the station from? In the user home,  you are able to reset the passphrase of the station, however, you will lose the encrypted sensitive data including system and user passwords. In this workflow, you have the option to remove all users except for one new super user which you provide the new username and password in the Bog File Passphrase dialog:  
View full article
Guinan RandyDavis Guinan
‎2025-03-26 01:37 PM

on ‎2025-03-26 01:37 PM

Labels:
  • TAC IA Series
283 Views

How to move Infinet devices from one port to another in the same Automation Server

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue It is sometimes necessary to move a previously configured Infinet i2 device from one Infinet network to another in the same parent Automation Server. EcoStruxure Building Operation does not provide an automatic way to move an i2 device; it must be done manually. Product Line  EcoStruxure Building Operation Environment Building Operation Automation Server Cause Guidance on steps to move Infinet i2 device from one Infinet network to another in the same host Automation Server Resolution In this example, we are going to move multiple Infinet i2 devices from the Infinet network on COM-A to the Infinet network on COM-B.   Backup Make sure to make a backup of the Automation Server before attempting the steps below. This is in case there is a need to revert the changes for whatever reasons. Export Devices from COM-A From COM-A Infinet network, display a List View of the devices, making sure to have columns displaying the Infinet ID and Serial Number. Write down the Infinet IDs and Serial Numbers of the devices to be moved. In the List View, multi-select the devices to be moved, right click and perform an 'Export', leave the Export Reference Filter at default (Export). After successful export, right click on the selected devices again and delete them from COM-A Infinet network. Prepare COM-B for Import From COM-B Infinet network, display a List View of the devices, making sure to have columns for Infinet ID and Serial Number. Observe the Infinet ID column, and compare with the notes taken above of the moving devices' Infinet ID, for IDs that are already in use in COM-B, you will need to assign a new ID to the device moving from COM-A Infinet network to COM-B, update your notes to include an available ID on COM-B. (see example below of what the notes might look like)   Import Devices to COM-B ***  In the System Tree, select the COM-B Infinet network and perform an import of the XML file created via export above. Physically move the devices from COM-A Infinet to COM-B Infinet. When doing so, avoid introducing duplicated Infinet IDs into COM-B Infinet. Make sure to power down the devices you are moving, connect them to COM-B Infinet, and only then power up the devices. On power up, the devices perform an ID check and stay off the bus if they detect their IDs are already in use. Configure Devices in COM-B From COM-B Infinet network, display a List View of the devices making sure to have columns for Infinet ID and Serial Number. Right click each device moved from COM-A Infinet to COM-B Infinet, and select "Properties", in the "Advanced" tab, enter the appropriate Infinet ID and Serial Number for the device then click "OK". In the List View, right click the device from previous step again, select "Device->Commission", after successful commission the device should go ONLINE Final Steps After all the moved devices are online, you should download ALL (whether moved or not) the devices to have their programs recompile and rebuild their Import/Export tables. Fix any references that were lost due to devices changing Infinet network and Infinet ID *** NOTE Due to an issue that was corrected in EBO 6.x, import may fail with error "Invalid InfinetId", the workaround for this problem is to manually create the Infinet devices on the destination port using the appropriate name, serial number and Infinet ID, then do the import selecting the option to merge on conflict.
View full article
Captain AbeMeran Captain
‎2025-04-15 04:55 PM

Last Updated: Administrator CraigEl Administrator ‎2025-05-05 04:22 PM

Labels:
  • EcoStruxure Building Operation
277 Views

Duplicate BMS System Data Source in Building Advisor

Issue Attempting to update the System Identifier to align with the newly created ID in the EBO system, is causing a 'Duplicate BMS System Data Source' error. Product Line EcoStruxure Building Advisor Environment Building Advisor Cause A duplicate ID has been identified in Building Advisor. This may correspond to an older system ID or one from a different site.   Resolution The error indicates the site where the duplicate ID is found, which usually corresponds to the site you are attempting to update. - Go to the admin menu, select the site, then choose 'Clear' on the BMS System and click 'Save'. - Click the pencil icon to add or edit the BMS System. Enter the new ID and then click 'Save'.    
View full article
Lieutenant Katha Lieutenant
‎2025-03-11 01:44 AM

Last Updated: Janeway PeterEdvik Janeway ‎2025-03-11 01:44 AM

Labels:
  • EcoStruxure Building Advisor
277 Views

What are the troubleshooting steps involved if EcoStruxure Building Activate Flex Server fails the required Wi-Fi Signal Strength test.

Issue EcoStruxure Building Activate Flex Server fails the Wi-Fi Signal Strength test.   Product Line EcoStruxure Building Activate Environment EcoStruxure Building Activate Flex Server EcoStruxure Building Activate Partner Portal Cause If the Flex Server Gateway is configured on Wi-Fi, it must achieve a RSSI value greater than -75 or value does not go below -80 more than 3 times. If these conditions are not met, Gateway will fail the test.   Resolution Below steps should be checked/followed to check the issue: Check Network Type: Ignore this issue if gateway is using a GSM network Verify Wi-Fi Receiver: Ensure the Wi-fi receiver is properly inserted into the USB port of the gateway Optimize Placement: Make sure the Gateway is near or in line of sight with the router to improve signal strength. Restart Router: Restart the router and check with your network provider for any issues.
View full article
Ensign Mukesh_Sangwan Ensign
‎2025-03-03 12:29 AM

on ‎2025-03-03 12:29 AM

Labels:
  • EcoStruxure Building Activate
256 Views

Stainless steel pockets for use in seawater/saltwater applications

Issue Are stainless steel pockets suitable for use in seawater/saltwater applications? Product Line Field Devices. Environment STR Sensor. Cause Customer asking if stainless steel pockets are suitable for use in seawater/saltwater applications. Please note that the answer would need to cover both static (stationary) water and flowing water in the pipe, because seawater/saltwater has different effects on metals depending on whether it is moving or not. Resolution Highest corrosion class is Class III for stainless steel, which seems not suitable for intended application.   ISO 12944 Impact Interior Exterior C1 Very low Heated buildings with clean air, such as offices, shops, schools, hotels, etc. None C2 Low Buildings not heated, where condensation may occur, such as warehouses and sports halls. Atmosphere with low pollution. For example in the country. C3 Middle Buildings for production with high atmospheric humidity and some air pollution such as food manufacturers, breweries, dairies and laundries. Urban and industrial areas, moderate sulphur dioxide pollution. Coastal areas with low salt content. C4 High Chemical manufacturers, swimming baths and ship- and boatyards by the sea. Industrial areas and coastal areas with moderate salt impact. C5-I Very high - Industry Buildings or areas with almost permanent condensation and with high pollution. Industrial areas with high humidity and aggressive atmosphere. C5-M Very high Buildings or areas with almost permanent condensation and with high pollution. Industrial areas with high humidity and aggressive atmosphere.  
View full article
Kirk MikaelKrantz Kirk
‎2025-02-20 07:34 AM

on ‎2025-02-20 07:34 AM

Labels:
  • Field Devices
242 Views

Building Commission (EBC) closes at Login screen

Issue Building Commission (EBC) self closes at Login screen in Windows. It seems to be after application is unused for an extended period of time. Product Line EcoStruxure Building Operation Environment Building Commission Tool Cause There is a fault in Microsoft.ui.xaml.dll as observed in the Windows Event Viewer. Resolution Uninstall the application via Windows Add or Remove Programs Reinstall the application via the Microsoft Store Open this link in a browser Building Commission - Free download and install on Windows | Microsoft Store Click Open in Store App button in upper right by sign-in
View full article
Picard David_Purser Picard
‎2025-03-14 05:53 PM

on ‎2025-03-14 05:53 PM

Labels:
  • EcoStruxure Building Operation
232 Views

EcoStruxure Building Activate Flex Server is unable to synchronize time with RTC.

  Issue There are issues for Flex Server to synchronize time with the Real Time Clock (RTC). Product Line EcoStruxure Building Activate Environment EcoStruxure Building Activate Flex Server EcoStruxure Building Activate Partner Portal Cause The RTC parameter fails the synchronization test.  Resolution Check the voltage of the coin cell using a multimeter. If the voltage is less than 3.3V, replace the coin cell. If the voltage is equal to or greater than 3.3V and the test still fails, report the issue to technical support.
View full article
Ensign Mukesh_Sangwan Ensign
‎2025-03-30 05:56 PM

on ‎2025-03-30 05:56 PM

Labels:
  • EcoStruxure Building Activate
235 Views

Esmi Ultima Function Buttons Programming

  Issue How to program the function buttons in Esmi Fire Panel Product Line ESMI Fire Detection Environment FFSULH1001. FFSULH1002. FFSULH1003. FFSULH1005. Cause Customer wants the specific buttons for specific actions. Resolution Up to 24 customer specific, on-screen function buttons may be configured to provide control, disablement and engineering functions. The function buttons can be configured to be either available or hidden for each log-in profile. The following procedure describes how to: Set function button attributes/properties. Allocate function buttons to user groups.  Create password specific user accounts for inclusion within a nominated user group. Setting attributes Function buttons (inputs) may be set to operate by association to output devices with the same properties e.g. a security input will activate any device that has security ticked as part its output properties, or as part of a cause-and-effect rule where the function button is the “Cause”.   With Loop Explorer open, select the Configure menu button and select System Manager to open the function button configuration page. Select the 'Details' button to open the properties section of the function button that you wish to configure. Note: Input Properties The properties page allows the user to configure the input action and associated messages, to set individual colours and either to work as a latched (cleared on user interface reset) or toggled action (press function button to operate and again to turn off). Mapping to zones is optional, and the location text is the name given to the function button when completed. Feature Groups There are 4 default user groups that can be configured with specific permissions for different users.     When configured, the function buttons will be included as selectable options in each of the feature groups. It should be noted that if a function button is allocated to the Logged-out group, then it will be present alongside the User Options button when all other user groups have been logged out. Note that at this level then the user options are limited to system information and basic panel tests such as display colour and LED function. Function buttons allocated to User level 2 and 3 may be accessed using the default login codes. If users are to be allocated unique numerical codes, then it would be advisable to change the panel default level 2 and/or 3 codes where required.
View full article
Ensign Sandeep_Kumar006 Ensign
‎2025-02-26 10:19 PM

Labels:
  • ESMI Fire Detection
214 Views

Building Activate Partner Portal displays 'error: There is no change in the configurations'.

  Issue While performing the verification tests, an error is displayed: 'error: There is no change in the configurations' as shown below:   Product Line EcoStruxure Building Activate Environment EcoStruxure Building Activate Partner Portal Cause This error occurs under the following conditions: The user made changes in the Partner Portal but later reverted to the original settings/configuration, assuming there should be some changes, and then started the verification tests again. The user chose to perform the test and verification process once post-submission, resulting in this error message. Resolution When the verification process is initiated, it goes through four checkpoints. The user can safely ignore this error message and proceed with the tests directly. Clicking on the 'Load Mapping' button will remove this error message.
View full article
Ensign Mukesh_Sangwan Ensign
‎2025-02-26 10:14 PM

on ‎2025-02-26 10:14 PM

Labels:
  • EcoStruxure Building Activate
203 Views

How to identify in the Partner Portal if the EcoStruxure Building Flex Server has gone offline due to a power failure for a specific time period.

  Issue Identifying a potential power supply/source failure to the Flex Server for a specific time period.  Product Line EcoStruxure Building Activate Environment EcoStruxure Building Activate Flex Server EcoStruxure Building Activate Partner Portal Cause The Flex Server went offline for some time and then came back online again. There is a need to identify if this happened due to a power source failure to Gateway.  Resolution Login to the Partner Portal and select the customer from the settings icon in the top right corner. Navigate to the Controller section in the left pane and select the particular Gateway from the dropdown. Navigate to 'Plots' tab and select 'PowerSource' Gateway stream under 'MSP430'. The 'PowerSource' stream value should always be equal to '1' as shown above. If this indicates '0' at any time, this suggests a potential loss of power supply to the Gateway.
View full article
Ensign Mukesh_Sangwan Ensign
‎2025-03-30 11:36 PM

on ‎2025-03-30 11:36 PM

Labels:
  • EcoStruxure Building Activate
199 Views

ESMI Ultima User Profile Configuration

Issue How are user profiles (accounts) configured in Esmi Ultima Fire Panels? Product Line ESMI Fire Detection. Environment FFSULH1001. FFSULH1002. FFSULH1003. FFSULH1005. Cause Access levels allow permissions to be assigned to different user types. Resolution User Accounts Maximum Accounts: Up to 63 user accounts can be created. Permissions: Access group or singular permissions as set out within each user group. Profile Configuration User Levels: The example above shows User Level 2 in Group 1. Group numbers increase as more groups are added. Session Timeout: Range from 1 to 255 seconds for the function button availability after login. Function Buttons: Selected according to users who need access to the group. Panel Permissions: Additional permissions can be set in the User Menu Options section. Event Log: Records individual user activity. User Profile Example Username: Up to 20 characters. Passcode: Should contain 5 or 6 numerical characters. User Level: Mike Allerton is the 4th user, placed in User Level 3. User options Panel Control Interface: User activates the interface and enters their passcode to unlock screen and panel permissions. Function Option Button: Provides access to the buttons as described earlier.
View full article
Ensign Sandeep_Kumar006 Ensign
‎2025-03-12 05:47 PM

on ‎2025-03-12 05:47 PM

Labels:
  • ESMI Fire Detection
194 Views

Capture a SEAL log

  Issue How can I troubleshoot communication issues between SEAL app and EBO server? Does the SEAL app provide a detailed log for troubleshooting communication issues between the app and the EBO server? Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Building Operation Enterprise Server Ecostruxure SEAL Cause When troubleshooting SEAL communications issues to an EBO server, it may be helpful to get deeper information about the communication between the server and the SEAL application. To do this the following lines can be added to the appsettings.json application settings file as described below in the resolution Resolution Browse to C:\Program Files\Schneider Electric\SEAL Open the file appsettings.json. Depending on your user rights, you may need to copy and edit this file in another folder Go to line 26. After the closing brace }, enter a comma ,  Paste the following: "Serilog": { "Using": [ "Serilog.Sinks.File" ], "MinimumLevel": { "Default": "Information", "Override": { "Microsoft": "Warning", "Microsoft.Hosting.Lifetime": "Information", "SE.SEAL": "Debug", "SE.SEAL.Web.Auth": "Verbose" } }, "WriteTo": [ { "Name": "File", "Args": { "path": "%LOCALAPPDATA%/SEAL/logs/SEAL.txt", "rollingInterval": "Day", "shared": true } } ], "Enrich": [ "FromLogContext" ] }   Save the file. Try logging into the SEAL app and connecting to the EBO server Save the log found under: %LOCALAPPDATA%/SEAL/logs/SEAL.txt Restore the appsettings.json file to its original state.   Attached to this article is a ready-made file for use. Move the original file to another folder Place the attached file in C:\Program Files\Schneider Electric\SEAL After saving the logs, delete the attached file Move the original file back to its original location   In addition to this, it is always recommended to take an event view - Application log
View full article
Lieutenant Katha Lieutenant
‎2025-04-24 04:47 AM

Labels:
  • EcoStruxure Building Operation
189 Views

Niagara N4.15 Mobile Profile Removal

Issue Removal of the Mobile Profile in N4.15 Product Line TAC IA Series. Environment I/A Series N4.15 Jace I/A Series N4.15 Enterprise Server Cause The Niagara Mobile Profile has been removed from Niagara 4.15 Resolution Since the Niagara Mobile APIs were deprecated and replacements provided in N4.6,  Niagara Mobile has been removed in N4.15. The standard HTML5 Hx Profile is mobile friendly and users configured with the BDefaultMobileWebProfile will automatically be switched to the HTML5 Hx Profile. When you start up a N4.14 station in a N4.15 environment for the first time and it was configured for using the mobile profile, you should see this warning:   "WARNING [14:06:11 22-May-24 EDT] [web] Support for the "Default Mobile Web Profile" has been removed. Users with this profile have been switched to the "Html5 Hx Profile".
View full article
Guinan RandyDavis Guinan
‎2025-04-09 05:54 AM

on ‎2025-04-09 05:54 AM

Labels:
  • TAC IA Series
176 Views

Embedded license activation failed - Device ID included in the banned list

Issue Cannot activate a license on an Automation Server although the entitlement works on other Automation Servers. The Device Administrator output is similar to the following:   Activate failed: ASEmbeddedAPI internal error: Binary response does not contain feature information Error status information: FNO server response: =V(BACK_OFFICE%DEBACK_OFFICE+]\fK%MDEVICEID|0}~;DEVICEID/jlSk\}K qq7!vi%DCH'~A%05pQWN]G|3^Jk+yaz_Kx/:Dy&w F7BWWN#`Ex|6S.d<Y^nV~@?*C.D0])"KO?[pS#GH|aMe+i|@4's9kNE\7gfocfVbRf$1VuH>sdp_JN6%4B.n|Zm$]wi9M|F8#Hrw~/L4%XU<?8o="P1S$uW6Fu5vAsAz|l>8.@XA|.'[v_ekh_P}c7 Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium (AS-P) Building Operation Automation Server Bundled (AS-B) Building Operation Automation Server (AS) Cause When an Automation Server fails in the field an RMA (Return Material Authorization) request is made, and the license is returned for re-use in the replacement Automation Server. Once this occurs the serial number of the faulty Automation Server is blacklisted to ensure that it cannot be licensed and reused. Resolution If the device was mistakenly added to the blacklist please supply the Automation Server serial number to Support. If an RMA number does not exist in the licensing system for this Automation Server, the support team can make a request to have the server removed from the blacklist.
View full article
Commander Hernan_Urueña Commander
‎2025-05-14 07:42 AM

Last Updated: Administrator CraigEl Administrator ‎2025-05-14 04:06 PM

Labels:
  • EcoStruxure Building Operation
169 Views

Collect log files from Project Configuration Tool 2.0 (PCT 2.0)

Issue How to collect log files from the Project Configuration tool 2.0. Product Line EcoStruxure Building Operation Environment Project Configuration Tool Cause When contacting Product Support about issues with the PCT, log files should be provided. Resolution Collect log files through the Web interface on both Windows and Ubuntu installations: Logon to PCT server, Click Diagnostic  Click Collect logs Log starts collecting. After the log collection process is complete, the file will either be saved to the browser's default download location or a window will pop up asking where to save the ZIP file. Select the desired location then click Save   Log collector tool for PCT for Ubuntu: If the PCT web interface is unavailable, you can use the Log Collector tool to gather log files. This tool is included with the PCT installation on Ubuntu, eg. pct-2.1.1.8-log-collector-ubuntu. Give the file proper permission to be able to run as an executable either using chmod command:  chmod +x pct-2.1.1.8-log-collector-ubuntu​ or via file properties, as shown in below screenshot: Run the log collector tool. ./pct-2.1.1.8-log-collector-ubuntu​ A zip file containing the required log files will be saved in the same folder where the log collector tool is located.
View full article
Admiral StephenYang Admiral
‎2025-05-12 08:12 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2025-05-14 07:21 AM

Labels:
  • EcoStruxure Building Operation
  • Project Configuration Tool
174 Views

Steps to follow to unlock SIM PIN when using SIM Card under Flex server

Warning Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source. Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices. Caution While removing gateway cover: Open the gateway screws and delicately remove the top cover. Take extra care during this step, as the top cover is connected to the antenna cable via a thin wire. After opening the top cover, you will be able to see the top view of the board, please insert the active SIM card in the designated slot. Once the Sim Card is properly inserted, fix the screws back and ensure that the 4G&Wi-Fi Antenna is attached properly. If the antenna cable remains disconnected from the board, then the GSM will not work. Issue SIM card not being detected and internet is not connecting automatically when SIM card is inserted inside the Gateway.   Product Line EcoStruxure Building Activate Environment EcoStruxure Building Activate Flex Server EcoStruxure Building Activate Partner Portal Cause Some network service providers have a username, password and SIM PIN set by default when they issue the SIM to the customer. If the Gateway is using the SIM for internet, it requires any username, password and SIM PIN to be disabled before inserting the SIM inside the Gateway.  Resolution Contact the Network service provider directly to disable the username and password. The Network service provider can disable the username and password from the backend. For disabling the SIM PIN follow the below procedure: Steps to follow to unlock SIM PIN An example YouTube video on the steps detailed below can be seen at: How to unlock your SIM Card Upon receiving the SIM kit (note down the PUK number and also note down the SIM PIN if available) Insert the SIM card to a Mobile device/cellular device Type in the SIM PIN from the Step 1 and Unlock the SIM Navigate to the settings page – Network section - SIM settings - SIM PIN - Disable the SIM PIN option SIM CARD SETTINGS           SIM PIN DISABLED Reconfirm if the SIM PIN is disabled by reinserting the SIM from the SIM tray and check if it asks for PIN. If the SIM PIN is successfully disabled, it will not ask for SIM PIN at startup. If it still asks, repeat Step 4. Insert the SIM inside the Gateway SIM Slot and check for network connectivity and that the gateway goes online. After inserting the SIM card properly, power up the gateway and allow the gateway to boot up. This process may take up to 5 minutes. Once completed, the device should come online and can be provisioned through a partner portal   In case the SIM PIN is unavailable An example YouTube video on the steps detailed below can be seen at: How to Unlock Sim Card / Sim locked by Pin Code or PUK Code  Insert the SIM card into a Mobile device/cellular device Type in incorrect PIN more than 4 times till it asks to enter PUK code. Contact the Network Service Provider and perform the verification and obtain the PUK Code for the SIM from the Network provider directly Type the PUK code into the mobile device in the PUK code page Navigate to the Network settings - SIM PIN - Set a SIM PIN inside the settings Use this SIM PIN to Disable the SIM PIN lock. Reconfirm that the SIM PIN is disabled by reinserting the SIM from the SIM tray and check that it does not request a PIN.
View full article
Shuttle Bay pranavkumar003 Shuttle Bay
‎2025-05-12 12:49 AM

on ‎2025-05-12 12:49 AM

Labels:
  • EcoStruxure Building Activate
154 Views

Jace 9000 and NRIO Failures

Issue This issue is described in Tridium's internal case NCCB-71360. Users will notice that the default Nrio Device Manager view (Ux/web media) of the NrioNetwork driver in N4.14 looks identical to the previously existing workbench AX view; however, due to this defect, devices discovered and added through the web view will not function as expected.  Product Line TAC IA Series Environment I/A Series N4 Jace 9000 I/A Series N4.14 Framework Version Cause With the release of the Jace 9000, users may notice that the IO-R-16 and IO-R-34 devices will not function properly when discovery and configuration are performed through the web views. Resolution To tell if the device was added through the correct view, there are a few indicators. Malfunctioning devices will not show up with an Installed Version or a Sec version in either view: Working devices will display these values with no issue in either view: The malfunctioning devices' health section will read 'fail' even with a status of ok: Users in N4.14 should only use the Workbench AX Nrio Device Manager view to discover and add devices to a station. This use case is currently not supported in the browser for N4.14. All other use cases function in the UX Web Views, such as viewing devices, adding points, and commanding points.  
View full article
Guinan RandyDavis Guinan
‎2025-05-15 05:07 PM

on ‎2025-05-15 05:07 PM

Labels:
  • TAC IA Series
153 Views

Esmi Ultima Media Gateway Card Firmware Update

Warning Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.   Issue Fire Panel unable to display the Media Gateway Card version in system information. Product Line ESMI Fire Detection. Environment FFSULH1007. Cause Panel message output on Media Gateway Card TCP/IP port not functioning and impacting BMS integration with the panel.  Resolution The Media Gateway Card firmware needs to be updated. Follow the steps below to update the Media Gateway Card firmware.   Prerequisites An SD card and SD card reader is required to make a bootable SD card for the firmware update files.   Prepare the SD card The first stage to update the firmware of the media gateway card is to prepare and install the firmware file onto the SD card. The media gateway card requires a micro-SD card. The firmware file is approx. 320MB, so select an SD card with suitable memory size. Format the SD card. Open up Win32Diskimager software. You should see the screen appear below. Click on the open file tab and then select the firmware file. When the firmware is selected it will populate the image file box. Click on the ‘Write’ tab and you should then get a pop-up screen shown below. Click on the ‘Yes’ tab. The firmware will now install onto the SD card. When you see the pop-up screen ‘Write Successful’ appear click on the ‘OK’ tab. The firmware is now loaded onto the SD card. Close down the Win32Diskimager software and eject the SD card form the PC. Install the Firmware Install jumper link onto the middle and top pin of X7 (as per the image below). There is a sliding cover on the socket. First slide the cover to unlock it, then hinge it up. Place the SD-Card in the socket. Hinge down the cover, then slide it to lock it as below The media gateway must be restarted to initiate the installation of firmware. This is done by pressing the reset button, shown in the picture below. The Media Gateway card has a set of 6 LEDs that indicate the status of the card. During normal operation one of the LEDs flashes regularly once each second. After a few seconds you will see a moving pattern progressing through the six LEDs. This indicates that the installation is in progress. The installation will take a few minutes to complete. Note: During this time the panel may display a fault condition that the media gateway card is not present or not working correctly. You can ignore this fault indication. When the firmware installation on the media gateway card is complete, the pattern displayed on the six LEDs will change. Instead of a moving pattern progressing through the six LEDs, all six LEDs will flash on and off together. Once you see this pattern, with all the LEDs flashing together, you should uninstall the jumper, remove the micro-SD-card, and then press the reset button. The media gateway will restart then running the newly installed firmware. It will take a few seconds for the media gateway board to achieve its normal operating state. If the panel displayed a fault indication that the media gateway board was missing, this fault should clear. The ESMI ULTIMA panel now needs to be rebooted to accept the updates from the media gateway card.13. Once the ESMI ULTIMA panel has initialised the firmware installation is now complete.  
View full article
Ensign Sandeep_Kumar006 Ensign
‎2025-05-05 10:30 PM

on ‎2025-05-05 10:30 PM

Labels:
  • ESMI Fire Detection
156 Views
  • « Previous
    • 1
    • …
    • 505
    • 506
    • 507
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now