Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Stainless steel pockets for use in seawater/saltwater applications

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Stainless steel pockets for use in seawater/saltwater applications
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • MikaelKrantz
    MikaelKrantz

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
574 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Stainless steel pockets for use in seawater/saltwater applications

Kirk MikaelKrantz Kirk
‎2025-02-20 07:34 AM

on ‎2025-02-20 07:34 AM

Issue

Are stainless steel pockets suitable for use in seawater/saltwater applications?

Product Line

Field Devices.

Environment

STR Sensor.

Cause

Customer asking if stainless steel pockets are suitable for use in seawater/saltwater applications. Please note that the answer would need to cover both static (stationary) water and flowing water in the pipe, because seawater/saltwater has different effects on metals depending on whether it is moving or not.

Resolution

Highest corrosion class is Class III for stainless steel, which seems not suitable for intended application.

 

ISO 12944 Impact Interior Exterior
C1 Very low Heated buildings with clean air, such as offices, shops, schools, hotels, etc. None
C2 Low Buildings not heated, where condensation may occur, such as warehouses and sports halls. Atmosphere with low pollution. For example in the country.
C3 Middle Buildings for production with high atmospheric humidity and some air pollution such as food manufacturers, breweries, dairies and laundries. Urban and industrial areas, moderate sulphur dioxide pollution. Coastal areas with low salt content.
C4 High Chemical manufacturers, swimming baths and ship- and boatyards by the sea. Industrial areas and coastal areas with moderate salt impact.
C5-I Very high -
Industry
Buildings or areas with almost permanent condensation and with high pollution. Industrial areas with high humidity and aggressive atmosphere.
C5-M Very high Buildings or areas with almost permanent condensation and with high pollution. Industrial areas with high humidity and aggressive atmosphere.

 

Labels (1)
Labels:
  • Field Devices
Tags (1)
  • Find more articles tagged with:
  • MikaelKrantz25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore