EWS / Smart Connector Duplicate Hosted Objects and Binding Issues

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • EWS / Smart Connector Duplicate Hosted Objects and Binding Issues
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
778 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

EWS / Smart Connector Duplicate Hosted Objects and Binding Issues

Picard RobertAndriolo Picard
‎2025-06-11 10:23 PM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:31 AM

Issue

When hosting objects from EWS/Smart Connector, such as Security Expert, into EcoStruxure Building Operation (EBO), additional or mismatched object names can result in unresolved bindings and duplicate EWS IDs.

Common symptoms include: 

- Duplicate EWS IDs with different names
- Unresolved or broken bindings
- Binding loss after deleting containers

 

Duplicate EWS IDs with different namesDuplicate EWS IDs with different namesDuplicate EWS IDs with different namesUnresolved or broken bindingsUnresolved or broken bindingsUnresolved or broken bindings

 


 

Product Line

EcoStruxure Building Operation, EcoStruxure Security Expert.

Environment

  • EcoStruxure Building Operation Enterprise Server (ES)
  • Security Expert
  • Smart Connector Integration
  • EcoStruxure Web Service (EWS)

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

Typical reasons for this to occur:

  • Hosted object names do not match those in Security Expert.
  • Deleting containers without proper renaming can cause binding loss.

Resolution

 

Best Practices for Future Hosting

  • Always rename the hosted object in EBO before rehosting from the hardware folder.
  • This ensures that existing bindings are preserved.
  • Avoid hosting the entire `SecurityExpertServer` container—only host changed or new objects.

For Unbound or Irrelevant Objects:
- If objects have no bindings, naming is not critical from an EBO perspective
- Delete the container and rehost the object from the **Hardware folder**.

 

To Retain Existing Bindings 

  1. Identify the correct object name in the Hosted Containers folder 
  2. Copy the name to avoid typos.
  3. Delete the duplicate object with the correct name.
  4. Rename the existing EWS ID to match the copied name.
  5. Save the rename
  6. Verify bindings:
    1. Right-click the renamed object
    2. Select Delete
    3. Click Show References
    4. Confirm bindings are still valid.
    5. Click No to cancel deletion.
  7. Repeat this process for each object (inputs, outputs, doors, etc.) that has existing bindings.

 

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • EcoStruxure Security Expert
Tags (1)
  • Find more articles tagged with:
  • RobertAndriolo25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore