Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Esmi Ultima Function Buttons Programming

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Esmi Ultima Function Buttons Programming
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Sandeep_Kumar006
    Sandeep_Kumar006

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
906 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Esmi Ultima Function Buttons Programming

Sandeep_Kumar006 Troubleshooter
‎2025-02-26 10:19 PM

 

Issue

How to program the function buttons in Esmi Fire Panel

Product Line

ESMI Fire Detection

Environment

  • FFSULH1001.
  • FFSULH1002.
  • FFSULH1003.
  • FFSULH1005.

Cause

Customer wants the specific buttons for specific actions.

Resolution

Up to 24 customer specific, on-screen function buttons may be configured to provide control, disablement and engineering functions.
The function buttons can be configured to be either available or hidden for each log-in profile.
The following procedure describes how to:

  • Set function button attributes/properties.
  • Allocate function buttons to user groups. 
  • Create password specific user accounts for inclusion within a nominated user group.

Setting attributes

Function buttons (inputs) may be set to operate by association to output devices with the same properties e.g. a security input will activate any device that has security ticked as part its output properties, or as part of a cause-and-effect rule where the function button is the “Cause”.

 

  1. With Loop Explorer open, select the Configure menu button and select System Manager to open the function button configuration page.

    Skumar1_0-1740635275941.png

  2. Select the 'Details' button to open the properties section of the function button that you wish to configure.

    Skumar1_1-1740635328412.png

    Note: Input Properties
    The properties page allows the user to configure the input action and associated messages, to set individual colours and either to work as a latched (cleared on user interface reset) or toggled action (press function button to operate and again to turn off). Mapping to zones is optional, and the location text is the name given to the function button when completed.

    Skumar1_2-1740635837455.png

Feature Groups

There are 4 default user groups that can be configured with specific permissions for different users.

 

Skumar1_3-1740635892397.png

 

When configured, the function buttons will be included as selectable options in each of the feature groups. It should be noted that if a function button is allocated to the Logged-out group, then it will be present alongside the User Options button when all other user groups have been logged out. Note that at this level then the user options are limited to system information and basic panel tests such as display colour and LED function.

Sandeep_Kumar006_0-1741582457841.pngSandeep_Kumar006_4-1741582681138.png

Function buttons allocated to User level 2 and 3 may be accessed using the default login codes. If users are to be allocated unique numerical codes, then it would be advisable to change the panel default level 2 and/or 3 codes where required.

Labels (1)
Labels:
  • ESMI Fire Detection
Tags (1)
  • Find more articles tagged with:
  • SandeepKumar25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore