Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Operation
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,851
  • TAC IA Series 1,825
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 332
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 149
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 10
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building operation"

View in: "Building Automation Knowledge Base" | Community

1847 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 93
  • Next »
Label: "EcoStruxure Building Operation" Show all articles

EBO Data Collection Summary

Issue There is currently no summary KB article for all the data collection available in EBO systems. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Building Operation Workstation Building Operation Webstation Building Operation Automation Server Premium Building Operation Automation Server Bundled Cause Identified the need to review data from EBO to analyze performance or issues. Resolution Purposes for Data Collection Provide visual information about the issue Screenshots (from Windows Snip & Sketch or other tools) Video Capture or Mobile Device Video Device LEDs, provide any information about them and when they change. Provide information about your configuration/installation Network devices, including routers, switches, and any configuration you can provide BMS Routers Site Topology, including all devices included in the communications path Provide server (EC/ES/AS) XBK backup Configuration only is smaller and useful when investigating configuration, bindings, and/or programming All Data is larger and recommended when need to see trends or events to help investigate the issue's timeline. Provide any information to replicate the issue. Provide as specific as possible steps used to create that outcome Provide VERSIONS of ALL software, hardware, and protocols involved If submit any captures or logs, perform the following: Provide any steps performed in EBO during the capture or log with the date & time, so these events can be matched.   Servers (EC/ES/AS) Collect logs from an Automation Server Collect logs from the Enterprise Server and Enterprise Central Backing Up EcoStruxure BMS Servers Manually  (Configuration Only or All Data) Server Fieldbus Protocols Infinet: Gathering Trace Log information for the Infinet bus in EBO Lon: (Video included) Analyze Lon communication using trace log in EBO Modbus: Capture a Modbus trace log in EBO/SBO   Software EBO Webstation Collect EBO Webstation browser logs EBO Workstation Collect EBO Workstation logs EBO Project Configuration Tool (PCT) Collect log files from Project Configuration Tool (PCT) Windows Review the Windows Event Logs. What specifically happens when an error occurs? Follow this KB article to view and save the Windows Events: Viewing, Saving, Sharing Windows Event Logs for Troubleshooting Purposes Wireshark For extended period capturing, use this article to set up a Ring Buffer in Wireshark. Wireshark capture ring buffer for continuous capturing Hardware b3/Infinet Controller Collect log from a b3 or Infinet controller BACnet/IP Controller Workstation method - BACnet/IP Controller Diagnostics Building Commission method - Viewing and Exporting Diagnostic Files (WebHelp) or Viewing Diagnostic Files (YouTube)   Protocols & Electrical Interfaces Ethernet Capture any ethernet traffic, including IP: Using WireShark to analyse communications on an Ethernet network Capture Loopback (127.0.0.1) traffic between applications and/or servers running on the same host OS: How to capture localhost traffic with Wireshark to help troubleshoot EWS communication issues Lon Using Loytec LPA with SpaceLogic Server AS-P RS-485 Fieldbuses include BACnet MS/TP, I/Net, Infinet, Modbus RTU BACnet MSTP Capture Application - Communities (se.com) aka mstpcap.exe BACnet - PicoScope Basics Picoscope Configuration for Modbus RTU capturing and decoding Modbus RTU capturing in Wireshark
View full article
Picard David_Purser Picard
‎2022-08-29 12:04 PM

Labels:
  • EcoStruxure Building Operation
4356 Views

Modbus RTU capturing in Wireshark

Issue Need to analyze Modbus RTU communication packets for SpaceLogic controllers. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Building Operation Multi-purpose Controller (MPC) Building Operation Room Controller (RPC) Cause MP and RP controllers do not support packet logging or viewing on their modbus serial ports. Additionally, RP controllers lack transmit/receive LEDs for Modbus, making diagnostics more difficult. For differences between Automation Server and MP/RP controller Modbus operations, refer to the article: Modbus in the MP and RP Controller Introduction  Resolution Wireshark Installation Install the latest Wireshark application from: Wireshark • Go Deep | Download Click on the "download" icon and select your operating system Launch the downloaded setup file to install Wireshark. The default installation options can typically be used, unless the user has a specific reason to select others. Modbus RTU capture extension for Wireshark The Github project can be found at: GitHub - jzhvymetal/WiresharkSerialAdapter: Wireshark Serial Adapter for Windows Navigate to the latest version and download WireSharkSerialAdapter.exe  With this file downloaded, navigate to the Wireshark application folder and locate the following subfolder. If it does not exist, create it.  Copy WireSharkSerialAdapter.exe into this folder. NOTE: This is not an executable to be launched by the user. Wireshark will execute it as an additional capture option. USB-to-RS485 communications adapter Install the USB-to-RS485 adapter to PC. Wire the RS-485 adapter to the SpaceLogic RS-485 port to be captured. Check Device Manager -> Ports to determine the COM port number it is using. Wireshark Configuration Launch the Wireshark application. The initial start-up screen will list the available capture ports. This list will be different for each user’s computer, depending on its configuration. Below is an example of what this screen looks like:  In this list, Serial Port Adapter (WireSharkSerialAdapter.exe) should be an option. Click on the settings icon  to the left to bring up the setup options:  Launch Windows Device Manager to confirm the COM port assigned to the connected USB-485 adapter Select this COM port and set the baud rate, byte size, parity and stop bits of the Modbus RTU channel to be monitored. Use the Interframe settings shown in the screenshot above. Select User DLT 147 as the Wireshark DLT. Save these settings. Returning to the main screen, select Preferences from the Edit pull-down menu and navigate to Protocols:  Expand Protocols and select DLT_User. Click on Edit to add an entry to the Encapsulation Tables. Click the “+” button to add a DLT  Select User 0 (DLT = 147) and manually edit the Payload dissector to be mbrtu:  Click OK and return to the main screen Wireshark Capturing With the COM port properly configured, a traffic capture is initiated by double-clicking the selected COM port. The content of the capture will depend on the connected devices. The following is an example of the active window panes:  The main pane is an overall summary of the Modbus RTU traffic, with a brief description of each message type. When a frame is selected in this pane, the lower-left pane contains a breakdown of the packet content by field-type, and the lower-right packet is the packet content in hexadecimal format. The selected frame number is displayed in the packet details frame on the lower left, as well as the contents of the Modbus message. In this example, the results of the Modbus Read Holding Request for 6 registers is shown. The Wireshark capture is stopped by clicking on the red square, second from the left
View full article
Picard David_Purser Picard
‎2025-07-22 03:34 PM

on ‎2025-07-22 03:34 PM

Labels:
  • EcoStruxure Building Operation
120 Views

Modbus Property Status Shows "Attention"

  Issue When viewing the Modbus property in EcoStruxure Building Operation, the status displays "Attention". Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Building Operation Enterprise Server Cause The "Attention" status is not documented in the Web Help, which can make it unclear what is causing this state. This status typically indicates that there is an issue occurring within the Modbus system. One common cause is an unrealistic poll rate set on a Modbus group. . Resolution If the poll rate on a Modbus group is set too fast for the server to handle—especially in large Modbus networks—this can trigger the "Attention" state. Recommended Action: Review the poll rate configured for the Modbus group. If it is set to a very low value (e.g., 1 second), increase it to a more realistic interval. For busy networks, a poll rate of 5 seconds or more is typically more achievable. Once the poll rate is adjusted to a manageable value, the Modbus status should return to "Online".
View full article
Spock PeterLarsen Spock
‎2025-07-21 08:14 AM

on ‎2025-07-21 08:14 AM

Labels:
  • EcoStruxure Building Operation
75 Views

Collect logs from an Automation Server

Issue When troubleshooting server issues, it can be helpful to look at the logs that are recorded within the Automation Server. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server  Building Operation Automation Server Premium Building Operation Automation Server Bundled Cause Within the Automation Server logs are many records that are logged as a part of normal operations and unexpected events. Resolution Automation Server: Automation Server error logs can be retrieved using Workstation, Device Administrator, or WebStation. Device Administrator can be used in case of crash information is required, ex. dump files, or if the Automation Server is not accessible via WebStation or WorkStation. Workstation: Connect to EBO system with EBO WorkStation. Select the target Server  Expand the System folder Expand the Modules folder Expand the Trace folder and see Trace Settings For EBO 3.1 or higher, Double-click both Trace Log and System Log to open separately  For EBO 3.0 and lower, including SBO 1.x Right-click in Trace Settings Select Trace Settings in the menu Select Get System Log Repeat to select Get Trace Log  Device Administrator: Follow this WebHelp article: Getting Automation Server Debug Information If requested to retrieve a core dump, use this method to retrieve the Device Administrator Debug Information zip file. Then perform the following to make sure the zip file contains a core dump with a relevant timestamp for the event being investigated. Open Zip Open the folder containing the server name and IP address Open Server folder One should see file(s) with filename in this format core_dump_<Serial Number>_nsp_servers_<Timestamp>.tgz WebStation: EBO 4.0 (2022) and higher NOTE: You may have to enter Private Browsing mode to disable extensions, as you may see a blank page when viewing logs. Ensure credentials used are for a local 'admin' user or have access to the ~/System folder of the EBO Server you are connected. Click the 3-bar menu to navigate Select System, then Modules, then Trace One will see System Log and Trace Log in the menu, and clicking on System Log or Trace Log will open them in a new tab. NOTE: Please be patient as it may take some time to transfer the file. Once you see text in the tab, right-click on a blank area and select Save Page As... (Firefox) or Save As... (Chromium-based browser). It should recommend saving as SystemLog.txt or TraceLog.txt automatically; however, to be helpful, please add the EBO Server Name and Date to the filename. EBO 3.2 and earlier See the Webhelp Topic on collecting these logs from Automation Servers: Viewing and Downloading Automation Server Log Files. This process is now similar to that described above for WorkStation.   Credentials used to log in must be a member of a group that allows the policy of Web Configuration: Allow members to access Automation Server Web Configuration. Launch a web browser that is compatible with the installed EBO version as mentioned Webstation Specification Sheet. Type the IP address of the automation server to open the Webstation. Log into the Automation Server.                   Once logged into the Automation server, go to the Settings menu in the top right corner and click on Device Configuration. Click on the Server Log tab to view the automation server's log files. To save a copy of the log to your PC, click on the Get all log files link. The log files are compressed into a zip file and exported to downloads folder. Enterprise Server and Enterprise Central: For more information, check this article: Error logs from the Enterprise Server and Enterprise Central - Communities  
View full article
Picard Product_Support
‎2018-09-06 02:52 PM

Last Updated: Picard David_Purser Picard ‎2025-07-14 08:31 AM

Labels:
  • EcoStruxure Building Operation
8841 Views

Root User in EBO

Issue Unrecognized user connection in EBO Product Line EcoStruxure Building Operation Environment Building Operation Webstation Building Operation Enterprise Central Building Operation Enterprise Server Building Operation Automation Server Cause When browsing through System>Diagnostics>Users in Webstation, an unrecognized "root" user appears in the user session list. Resolution The 'root' user is a built-in system account used to help different parts of EBO—like EC, ES, and AS—communicate with each other. It’s automatically used when the system is not running in standalone mode. This account allows the systems to connect and share data securely in the background.
View full article
Admiral StephenYang Admiral
‎2025-07-07 11:41 AM

Last Updated: Administrator CraigEl Administrator ‎2025-07-07 05:17 PM

Labels:
  • EcoStruxure Building Operation
163 Views

Clearing the Smart Connector Hardware Container in Building Operation Server

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue After making changes to object names in the system, outdated or incorrect names may still appear under the Hardware folder in EcoStruxure Web Services (EWS).     Product Line EcoStruxure Building Operation, EcoStruxure Security Expert. Environment EcoStruxure Building Operation Enterprise Server (ES) EcoStruxure Security Expert Smart Connector Integration EcoStruxure Web Service (EWS). Cause When significant changes are made to object names in the system, the Smart Connector may retain outdated data. If a standard Discovery does not update these names, the most effective solution is to clear the Smart Connector database and re-establish the connection.   Resolution To clear the outdated data from the Smart Connector:   Step 1: Access the Smart Connector Portal Open a browser and navigate to http://localhost:8082 (assuming Smart Connector is installed locally). Log in to the Smart Connector Portal. Step 2: Delete the Existing Processor Configuration Go to Configurations → Processor. Locate the Security Expert Discovery Processor. Click the Delete (bin icon) next to it. ⚠️ Do not delete other processors (e.g., Alarm Processor). Step 3: Delete the Existing EWS Server Navigate to the EWS Servers section. Locate the SecurityExpertServer. Click the Delete (bin icon) to remove it.   Step 4: Reconfigure the Processor and EWS Server Follow the instructions in Section 4.4 of the referenced document [1] to: Add a new Security Expert Discovery Processor Configure a new EWS Server Allow 10–15 minutes for the initial discovery process to complete. This will create a fresh snapshot of the current Security Expert database. Once the discovery is complete: Refresh the Hardware folder in EcoStruxure Building Operation. Rehost the new EWS objects as needed. Step 5: Verify Alarm Processor Configuration After re-adding the EWS Server, ensure the Alarm Processor is correctly configured to reference the new server. Refer to Section 4.5 of the same document [1] for detailed steps.   Reference [1] Refer to the official integration guide documentation for more information. Security Expert SmartConnector Version 1.1.0.8 - Installation & User Manual  
View full article
Guinan RobertAndriolo Guinan
‎2025-07-06 06:12 PM

Labels:
  • EcoStruxure Building Operation
  • EcoStruxure Security Expert
90 Views

"MutationEvent is not defined" Javascript error after browser update to Chrome/Edge v127 and Firefox v140

  Issue Using graphics in WebStation, “MutationEvents not defined” error messages and/or data in not shown correctly, after the web browser used is upgraded to latest versions.     Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation WebStation Google Chrome v127 and later Microsoft Edge v127 and later Firefox v140 and later Cause After upgrading to the latest web browser versions EcoStruxure Building Operation web-based user interface, WebStation, in all released and supported versions may no longer operate correctly when graphics are attempted to be displayed. The symptoms include, but may not be limited to, failure for graphics to show data correctly and error prompts such as “MutationEvents not defined” being shown. As referenced in Mutation events will be removed from Chrome  |  Blog  |  Chrome for Developers, Google has deprecated these Mutation events and replaced them with a different function. Also as referenced in Firefox 140 for developers - Mozilla | MDN The  MutationEvent  interface and its associated events have been removed from Firefox build 140 onwards. Resolution Consolidation point releases are available for supported EBO versions to resolve these compatibility problems with the latest browsers. These releases are available to authorized Schneider Electric EcoXperts and employees only from the EBO Hotfix List in the EcoExpert Community and the Software and Firmware Center of the EcoXpert Extranet. Other customers should contact their local Schneider Electric EcoXpert or Schneider Electric office and arrange a service visit.   The issue is addressed in the following releases: EcoStruxure Building Operation 3.2.4 : EBO 3.2.4.7003 (CP5) onwards EcoStruxure Building Operation 4.0.5 : EBO 4.0.5.5001 (CP4) onwards EcoStruxure Building Operation 5.0.3 : EBO 5.0.3.12005 (CP11) onwards EcoStruxure Building Operation 6.0.3 : EBO 6.0.3.2001 (CP1) onwards EcoStruxure Building Operation 7.0 Unsupported versions such as EBO 3.1 and earlier will not be addressed. Upgrading to the latest version of EcoStruxure Building Operation is strongly recommended to ensure full compatibility with current web browsers and to benefit from the latest features and security updates.
View full article
Administrator CraigEl Administrator
‎2025-07-06 08:02 PM

on ‎2025-07-06 08:02 PM

Labels:
  • EcoStruxure Building Operation
445 Views

Field bus (Infinet or MSTP) will shut down as soon as device is connected

Issue Infinet/MSTP was running fine until a device was added or replaced, after wiring in the new device it brings down the Infinet/MSTP field bus when powered up, disconnecting the new device from the bus makes the bus resume operation. When the new device is connected the green (RD) LED goes solid instead of blinking and all communications to all devices on the bus stops, in some cases the master controller will reset. Product Line Andover Continuum, EcoStruxure Building Operation Environment Infinet devices i2s MSTP devices b3s Cause Power lines reversed. Continuum field devices (i1s, i2s and b3s) have their RS-485 communication lines connected to ground via an isolator as seen in the diagram below, if the LIVE and GND lines are inverted then LIVE is connected to the 485 communication lines instead of GND. This will make the field bus electrically unable to communicate and, in some scenarios, can even cause hardware damage. Resolution Ensure Correct Wiring: When powering 24VAC devices off the same transformer, make sure to continue the wiring chain LIVE to LIVE and GND to GND. In the field, it may not be very obvious that the 'Live' and 'GND/Neutral' wires have been swapped. A multi-meter can be used to verify the wiring. Set the multi-meter as appropriate to measure 24VAC. Place the black lead of the meter on the GND/Neutral termination at the power connector of the field device.  Use the red lead of the meter to measure the voltage at the +/- termination at the RS-485 (Infinet or MSTP) on the controller. The measured voltage should be very low, between 0 VAC and 1.1 VAC, a voltage reading of about 10 VAC indicates the Live and GND/Neutral wires have been swapped.
View full article
Picard Product_Support
‎2018-09-11 06:27 AM

Last Updated: Administrator CraigEl Administrator ‎2025-07-06 06:21 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
1920 Views

DUIC-5P-12V Digital Input Expander and use with SpaceLogic Controllers

Issue Programming for the use of Smartware Technologies DUIC-5P-12v input multiplexer Product Line TAC IA Series, EcoStruxure Building Operation Environment Building Operation Multi-purpose Controller Building Operation Multi-purpose VAV Building Operation RP-V VAV Building Operation Room Controller I/A Series N4 Jace 8000/9000 I/A Series N4 Enterprise Server Building Operation Automation Server Premium Cause Define the application programming and configuration of the DUIC-5P-12V in various enviroments using SpaceLogic contollers Resolution The DUIC-5P-12V Card allows for conversion of a single universal input channel to accept up to five voltage free contacts of any mixture such as mercury wetted, Triac, etc., which may have inherently large and varying resistances. The DUIC-5P-12V on-board circuitry allows the controller inputs to have a consistent input reading, unaffected by long lead lengths, varying resistances, etc.  Smartware Technologies Documents includes programming for use in SpaceLogic devices under an AS-P in the form of a Function Block program. When SpaceLogic controllers are used in the Niagara Frameworks Jace 8000/9000 or hosted directly under a Niagara Frameworks Enterprise Server, the programming is done in a Visual Script Programming format utilizing the Schneider MPX modules in Workbench. The documentation addresses the original use for the I/A Series MNL and MNB contollers as well. NOTE:  The device requires half wave 5 -12 DC or 24 VAC only to prevent damage
View full article
Guinan RandyDavis Guinan
‎2025-06-30 12:04 PM

on ‎2025-06-30 12:04 PM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
193 Views

How to identify Automation Server(AS) ID node count

Issue Fail to apply CP or HF on AS Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Workstation EcoStruxure Building Operation Automation Server (ASP/ASB) Cause The Automation Server is not installed next to the Power Supply. The requirement is stated in the Hardware Reference Guide, Position 1 is reserved for a power supply. Position 2 is reserved for an automation server. Resolution When the update process fails, please collect the DebugInformation. Next, check the System.log for the node ID. If the node ID is not  2 , it indicates that the AS is not installed at the correct address. In that case, the physical location of the AS needs to be corrected. Example of incorrect ID location Relevant Resource: Multiple Automation Servers on the same backplane
View full article
Admiral StephenYang Admiral
‎2025-06-30 07:47 AM

on ‎2025-06-30 07:47 AM

Labels:
  • EcoStruxure Building Operation
111 Views

How to check PCT 2.0 disk size

Issue PCT 2.0 shows "503 Service Temporarily Unavailable" error when trying to reach to PCT server. Product Line EcoStruxure Building Operation Environment Project Configuration Tool Cause The PCT 2 disk has a fixed size limit of 200GB and cannot be expanded by users. Once the disk reaches full capacity, access to PCT 2 becomes unavailable. Resolution Check the size of the "data.vhdx" file: The file resides in the "Virtual Hard Disks" folder. This folder can be found in the path selected during the installation. Folder location: Navigate to the installation path to locate the "Virtual Hard Disks" folder. File location: Inside the "Virtual Hard Disks" folder, locate the "data.vhdx" file. Check the size of the "data.vhdx" file.   If the disk size is over 200GB, contact local support and attach the information.   
View full article
Admiral StephenYang Admiral
‎2025-06-25 06:23 PM

on ‎2025-06-25 06:23 PM

Labels:
  • EcoStruxure Building Operation
  • Project Configuration Tool
171 Views

Where to find Evaluation license for TAC Vista and EcoStruxure Building Operation

Issue Locate the Evaluation license for TAC Vista or EcoStruxure Building Operation Product Line EcoStruxure Building Operation, TAC Vista Environment TAC Vista EcoStruxure Building Operation Cause EBO 7.0 and later: Building Operation 7.0 introduces the Engineering license, which enables a system to run during the project phase without the need for commercial licenses or what has previously been referred to as demo licenses/evaluation licenses which have a short validity and require frequent updates and re-engineering.   EBO 2024 (6.0) and earlier: There is an evaluation license for EcoStruxure Building Operation valid 3 months.    TAC Vista: Starting September 1, 2025, the evaluation license will only be available upon request for Schneider Electric employees using the support@Schneider portal. Should an EcoXpert™ partner require an evaluation license, they must request this from their Schneider Electric contact. Resolution EBO 7.0 and later: Engineering licenses can be downloaded from the EcoStruxure Power & Building Software Companion during the project phase, and when the time comes to commission and hand over the project to commercial operation, the portal provides the ability to convert Engineering licenses to Commercial licenses by simply submitting a license purchase order. No replacement or re-engineering of the license is required thanks to this one step operation.   Engineering licenses have a validity of 6 months, after which it is possible to extend for another 6 months if the project timeline demands it.   *Note that Demo licenses are still available for WorkStation Pro, enabling a limited time operation of WorkStation Pro use. For full uninterrupted operation, please use a commercial WorkStation Pro license.   EBO 2024 (6.0) and earlier: Evaluation license files are available for licensed partners on the EcoXpert Extranet. Follow the link and search for "evaluation". You must first register using your business email (i.e. CustomerName@partnerdomain.com) address to gain access to these files. Note: You may use any email address to register and view content, but downloads will only be granted to approved partner domain names.   TAC Vista: Only be available upon request for Schneider Electric employees using the support@Schneider portal To request a TAC Vista evaluation license, follow the steps outlined below: Open a case on ”Digital Offer Sales & Provisioning App Request” - What is your request related to? > Digital Supply Chain – Request - Please Select the Environment > Production - Please select the Offer > TAC VISTA - Please enter the SESA ID… > The SESA ID of the Schneider employee creating the ticket - Please select the type of Request > Create - Please select the type of Create new request > Demo license creation - Please select your country > The country of the person creating the ticket - Please provide business justification > Reason why the license is needed When submitting the ticket as above, the ticket will be handled automatically, and an email will be sent to the user. Subsequently the ticket will be closed automatically.
View full article
Picard Product_Support
‎2018-09-11 06:30 AM

Last Updated: Administrator CraigEl Administrator ‎2025-06-25 06:04 PM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
4008 Views

PCT doesn't update "Added to parent" column after detaching child server

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue The added to parent column shows incorrect information. PCT 1.X  PCT 2.x Product Line EcoStruxure Building Operation Environment Building Operation Project Configuration Tool (PCT) Cause PCT doesn't detect detachment in WorkStation. Resolution Do not detach the child server from its parent in PCT 1.x and 2.x. Webhelp information: Adding a Virtual EcoStruxure BMS Child Server to a Parent Server.
View full article
Admiral StephenYang Admiral
‎2019-11-26 01:33 PM

Labels:
  • EcoStruxure Building Operation
  • Project Configuration Tool
1606 Views

EWS / Smart Connector Duplicate Hosted Objects and Binding Issues

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue When hosting objects from EWS/Smart Connector, such as Security Expert, into EcoStruxure Building Operation (EBO), additional or mismatched object names can result in unresolved bindings and duplicate EWS IDs. Common symptoms include:  - Duplicate EWS IDs with different names - Unresolved or broken bindings - Binding loss after deleting containers   Duplicate EWS IDs with different names Unresolved or broken bindings     Product Line EcoStruxure Building Operation, EcoStruxure Security Expert. Environment EcoStruxure Building Operation Enterprise Server (ES) Security Expert Smart Connector Integration EcoStruxure Web Service (EWS) Cause Typical reasons for this to occur: Hosted object names do not match those in Security Expert. Deleting containers without proper renaming can cause binding loss. Resolution   Best Practices for Future Hosting Always rename the hosted object in EBO before rehosting from the hardware folder. This ensures that existing bindings are preserved. Avoid hosting the entire `SecurityExpertServer` container—only host changed or new objects. For Unbound or Irrelevant Objects: - If objects have no bindings, naming is not critical from an EBO perspective - Delete the container and rehost the object from the **Hardware folder**.   To Retain Existing Bindings  Identify the correct object name in the Hosted Containers folder  Copy the name to avoid typos. Delete the duplicate object with the correct name. Rename the existing EWS ID to match the copied name. Save the rename Verify bindings: Right-click the renamed object Select Delete Click Show References Confirm bindings are still valid. Click No to cancel deletion. Repeat this process for each object (inputs, outputs, doors, etc.) that has existing bindings.  
View full article
Guinan RobertAndriolo Guinan
‎2025-06-11 10:23 PM

on ‎2025-06-11 10:23 PM

Labels:
  • EcoStruxure Building Operation
  • EcoStruxure Security Expert
182 Views

Forgotten or unknown password

Issue Unable to log into Workstation because the user password is unknown. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Automation Server (AS, AS-P, or AS-B) Building Operation Enterprise Server Building Operation Enterprise Central Building Operation Project Configuration Tool (PCT) Cause The password for an Automation server or Enterprise server/Central has been forgotten. Resolution IMPORTANT: The session ID is unique for this session of WorkStation. You cannot close WorkStation until the password has been reset. If you close WorkStation, before the password has been reset, a new session ID is generated that cannot be used with the temporary password provided by your local Schneider Electric Buildings support team.       The following are the steps to populate the session ID, which is required for doing the password reset.   For servers with EBO older than V3.1.X In the WorkStation logon page, while holding the shift key, left-click the area near the EcoStruxure Building Operations Icon.   This will populate the Session ID. Copy the Session ID.   For servers with EBO V3.1.X:   In Device Administrator, select the server you need to perform the reset to. Check the box and click the hyperlink   From the top bar select Password Reset Select OK when you get the “Password reset token created” pop-up Now, on the WorkStation logon page, while holding the shift key, left-click the area near the EcoStruxure Building Operations Icon. This will populate the Session ID. Click the Copy button.    For servers with EBO V3.2.X and higher In Device Administrator, select the server you need to perform the reset to From the top bar, select the “Edit Connection Password/Reset password” and press OK Now, on the WorkStation logon page, while holding the shift key, left-click the area near the EcoStruxure Building Operations Icon. This will populate the Session ID. Click the Copy button.   For servers within PCT 2.X Start the server Left click on the Server Menu  Select "Set password reset mode"  Now, on the WorkStation logon page, while holding the shift key, left-click the area near the EcoStruxure Building Operations Icon. This will populate the Session ID. Click the Copy button.    NOTE (for servers with EBO V3.1.X and higher)  For the Automation Server password reset, ensure that the Automation Server is connected to your PC machine via a USB cable. For the Enterprise server and Enterprise Central password reset, add the server to the Device Administrator using the “Add Server” button on the top bar. Please note even if you enter the wrong password, the Server would still be added to the Device Administrator.     After having the Session ID:   Send the Session ID to your local Schneider Electric Buildings support team Once PSS provides you with the unlock key In WorkStation, ensure that the Session ID is still visible, enter: User Name: admin Password: paste the result from the webpage Domain: Local and click Log On This will pop-up the Change-Password form Fill in the “old password” field with the unlock Key Put in a new password you want to use and then enter the new password in again. Click OK   NOTE:  When attempting to reset the password and unlock with the sessionid/temp password, you receive the error: "Your account has insufficient permission to use the system. Contact your administrator. "  Open a case with your local Product Support group and submit a request to unlock the user.   NOTE: WebHelp article 6749   The following video shows the password reset procedure for EBO older than V3.1.X. It covers most of the important steps for newer versions. Quick-Help video    
View full article
Picard Product_Support
‎2020-09-25 09:38 AM

Last Updated: Admiral StephenYang Admiral ‎2025-06-10 10:23 AM

Labels:
  • EcoStruxure Building Operation
29673 Views

Password reset for EBO versions 3.1 and later

Issue In EcoStruxure Building Operation (EBO) version 3.1 and later the password reset function have changed, how does it work, and what is changed from before? Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Building Operation Project Configuration Tool (PCT) Cause The changes have been done due to cybersecurity issues. The basic workflow is the same as before but the generation of the reset token has changed. Resolution IMPORTANT: The session ID is unique for each session of WorkStation. You cannot close WorkStation until the password has been reset. If you close WorkStation, before the password has been reset, a new session ID is generated that cannot be used with the temporary password provided by your local Schneider Electric Buildings support team.  See online help topic: Copying the Session ID when Resetting the Password   To get a password reset token in version 3.1 and later you need to set the server in password reset mode(valid 24 hours)   For Automation Server(AS, AS-P, AS-B) this is done using the Device Administrator(DA), a USB connection is required between the computer and the server   For the Enterprise Server(ES) administrator privileges on the PC where the ES is installed are required. The ES is set in password recovery mode using the DA, the DA needs to be started as an administrator.   For the virtual server environment, Project Configuration Tool (PCT) tool is used. To get access to the password reset mode, the server needs to be started.     For detailed information please see the video: 
View full article
Janeway Jonas_Brissman Janeway
‎2021-08-19 04:34 PM

Last Updated: Admiral StephenYang Admiral ‎2025-06-10 10:23 AM

Labels:
  • EcoStruxure Building Operation
8586 Views

Running multiple BACnet Applications on same Windows machine

Issue BACnet requires applications to listen on the same port across the IP subnet to receive BACnet discovery broadcasts. Two applications running on the same machine can not use the same port as the Listening Port. Product Line EcoStruxure Building Operation, Continuum, TAC I/A Series Environment Building Operation Enterprise Server I/A Series WorkPlace Tech Continuum Cyberstation Cause The site can not provide a separate machine or VM for each BACnet application, which is recommended for independent operation. Resolution With this configuration, one application will act as BBMD to receive and distribute BACnet Broadcast Messages. The other application will act as a Foreign Device, relying on BBMD to relay BACnet Broadcast messages. Once BACnet devices and the Application, configured as Foreign Device, have shared their IP and Port, messages between them will be unicast and will not pass through the BBMD. Ensure one application can be configured as a BACnet BBMD and the other as a Foreign Device. Configure one as BBMD, usually EBO Enterprise Server Configure the other application as a Foreign Device referencing the BBMD IP and Port
View full article
Picard David_Purser Picard
‎2025-06-05 12:09 PM

on ‎2025-06-05 12:09 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • TAC IA Series
313 Views

Capture a Modbus trace log in EBO/SBO

Issue How can I troubleshoot a communication issue with the Modbus protocol Is there a log available within the AS or ES that shows the Modbus communication between Modbus devices Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Automation Server Building Operation Enterprise Server Cause When troubleshooting Modbus issues in an AS or ES it can be helpful to see the communication between devices to help identify this issue. The trace log within both server types is available and is configured as described below in the resolution. Resolution Open Workstation and navigate to [AS/ES name]/System/Modules/Trace/Loggers/nsp/nsp.pin. Right-click "nsp.pin.modbus" and choose Properties. Under Level, change from "Information" to "Debug", then click ok. In EBO 7.0 and higher, "Debug" will report 1 line per transaction, where "Trace" will report 8 lines for the same transaction. In EBO 7.0 and higher, instead of logging all Modbus with "nsp.pin.modbus," you can log separately Modbus TCP and Modbus Serial using either "nsp.pin.modbus.CommunicationLayer.ModbusCommsLogger.Serial" or "nsp.pin.modbus.CommunicationLayer.ModbusCommsLogger.TCP" Let it run a few minutes. If there are some user input needed to recreate the Modbus issue, then perform these steps now. Retrieve the log by right-clicking [AS/ES name]/System/Modules/Trace/TraceSettings and choose Trace settings->Get trace log.  Save the log file. A useful tool available on the Community, the Modbus decoder can be used to assist in viewing/debugging the Modbus trace log file information saved in the previous step. Once debugging is complete remember to change log level back to "Information" (reverse of step 3). Note: If the ES or AS is reset, i.e. cold started or warm started, the log level will return to 'Information', so if further increased logging is required, the procedure will need to be repeated. Note2: From v6 (2024), adding the trace below can be helpful for Modbus RTU /[ASName]/System/Modules/Trace/Loggers/nsp/nsp.pin/nsp.pin.sport/nsp.pin.sport.DeviceRS485   Here is a video showing the above process. 
View full article
Picard Product_Support
‎2018-09-06 09:00 AM

Last Updated: Picard David_Purser Picard ‎2025-06-03 12:12 PM

Labels:
  • EcoStruxure Building Operation
11969 Views

WorkStation Search Function (F3) Does Not Return Notification File Results

Issue The F3 Search function in EcoStruxure Building Operation (EBO) WorkStation does not return results for Notification File objects (e.g., .xlsx, .pdf, .txt), even when using wildcards.     Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation WorkStation Search Cause This behavior is functioning as designed (FAD). Notification files generated using the "Write to File" option are not stored in the EBO database. Therefore, they are not indexed and cannot be retrieved using the F3 search function. Resolution Although these files are not searchable within EBO, they are saved locally in a fixed directory: ...\db\notifications To assist users in locating these files:  Create a Hyperlink Object in EBO that points to the above folder. Users can then open the folder directly within WorkStation and use the operating system’s search functionality to locate specific files. Note: The notification file path is not configurable. For more information, refer to the official documentation in WebHelp: Accessing a Notification Written to a File
View full article
Commander Hernan_Urueña Commander
‎2025-05-27 09:26 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2025-05-27 09:38 PM

Labels:
  • EcoStruxure Building Operation
181 Views

RSTP Troubleshooting for BACnet/IP Controllers

Issue BACnet/IP controllers are not configured in RSTP Mode by default, therefore must be configured during installation. Having RSTP Mode disabled by default allows one to connect BACnet/IP controllers to any switch, even with port security configured to detect BPDU packets and disable the port. Product Line EcoStruxure Building Operation, TAC IA Series Environment Multi-purpose Controller (MP-C) Multi-purpose VAV (MP-V) Room Controller IP-IO I/A Series N4 Jace8000 SmartX IP Driver for Niagara Cause RSTP protocol requires that controllers, switches, and network architecture are configured to ensure the protocol will operate as expected.  Resolution Setting RSTP Mode for BACnet/IP Controllers ALL devices in the RSTP loop MUST BE IN RSTP MODE to function properly. This is not a huge issue because during startup you can unplug 2nd side of the loop and it will function properly in a daisy chain. Ensure the SmartX Controllers are configured correctly Configuring BACnet/IP Controller Device Settings A factory or network reset returns the RSTP setting to Disabled. Important: Whenever you change RSTP settings, the controller MUST be WARM START. If you fail to perform this restart, the BACnet/IP controller will continue communicating using its previous RSTP settings. 'Activate IP Changes' does not affect RSTP mode. Ensure the switch is configured correctly per Configuring RSTP on a Managed Switch for SmartX IP Controllers. If asked to review this for a case, please provide PSS screenshots from the switch configuration page(s).  Bridge Priority = 4096 Hello Time = 2 sec Max Age = 40  (40 is the maximum value allowed by the protocol. Default is 20) Forward Delay = 21 sec Bridge Priority Considerations Change Bridge Priority by adding 4096 as switches get further away from AS. (8192, 12288, 16384, 20480, 24576, 28672) DO NOT set the priority as 32768 or higher because that is the built-in Bridge Priority of BACnet/IP Controllers. First, configure the Root Bridge Switch (closest to the Automation Server) settings. Then, configure the additional Switches in order of increasing Bridge Priority. Plug in 2nd side of the RSTP Loop If all devices stay online, then it is working properly. Now test line breaks or controllers that are powered off. If all devices go offline and/or the switch LED is flashing rapidly, then go to RSTP Troubleshooting. Managed Switch Troubleshooting Consult the documentation or contact the vendor or manufacturer to assist with configuration for the items below. Ensure the switch is IEEE 802.1D - 2004 capable. BACnet/IP Controller Networking Term Definitions RSTP Ring mentions the Rapid Spanning Tree Protocol is specified in IEEE 802.1D - 2004. Ensure the firmware is up-to-date by contacting the vendor or manufacturer or downloading it from its website. Ensure ports not participating in RSTP are configured as Edge Port, Admin port, or have STP disabled. Nomenclature for those settings on your specific managed switch may vary. Adding BACnet/IP controllers to site-managed switches, work with Local IT to add these devices to their network. They will need to work with their switch vendor/manufacturer/support group to ensure the configuration of those switches because it could be more complex than changing the minimum recommended four settings above. Also, since RSTP Protocol is limited to Max Age = 40 (hops including site switches and BACnet/IP controllers), each loop's size may be limited based on their site switch network configuration and architecture.  Determined the proper configuration (or disable) for the following features. DHCP snooping Dynamic ARP inspection Denial-of-service (DOS) mitigations BPDU Guard BPDU Filter RSTP Troubleshooting Check each BACnet/IP Controller -> Diagnostics -> Device Report to confirm in RSTP Mode MANUAL CHECKOUT Double-click MP - Diagnostics Files - Device Report It will open in the default text editor Review the Device Settings section near the bottom. In firmware 1.00.0x, the report should report RSTP Mode: Enable In firmware 2.00.0x or higher, RSTP: Enabled and RSTP Status: Operational If it reports disabled, then perform Setting RSTP Mode for BACnet IP Controllers Step 1 until RSTP is working properly. USE SEARCH & EVENTS EBO 2.x MP Device IP and Settings.xml for EBO 2.0 as it only includes MP controllers EBO 3.x SmartX Device IP and Settings.xml for EBO 3.x or higher Import attached search USE RSTP STATUS GRAPHIC IN WEBSTATION MUST BE EBO 3.1 or higher which includes ClientAPI support Frontline Fridays Episode 02 - Rapid Spanning Tree Protocol (RSTP) Date: 2022-11-11 Mike Botens posted the following in the thread: RSTP Status TGML dated 2022-11-09 PDF of the presentation Fusion Fridays - Session 07 ​​​​ Date: 2020-05-28 The start of the video shows the graphics page in use RSTP Status.zip is downloaded via the link below the video. Extract the TGML and drop it on the AS to import. The suggestion is to store TGML directly under the AS to help with navigation in Webstation. bind Network to the BACnet/IP network with the BACnet/IP Controllers. (You may need a second TGML page if BACnet/IP controllers are on Primary and Secondary IP) Run from web browser via WebStation because utilizes ClientAPI KNOWN ISSUES Offline controllers that are scattered are NOT an RSTP issue. Check to see if there is a possible DHCP issue by verifying controllers are still at their AUTO-IP address (IP 169.254.nnn.nnnn Subnet Mask 255.255.0.0). RSTP communications issues affect the entire RSTP loop or one contiguous group of controllers. Factory Reset or controller replacement should leave one ethernet cable unplugged until configured for RSTP per these articles: Replace a BACnet/IP Controller in an RSTP Ring Network Workflow and MP Controller Reset Modes If BACnet/IP Controller Device Report OR RSTP Graphic reports RSTP Status: Changes Pending instead of RSTP Status: Operational, disable RSTP Mode, Warm Start, re-enable RSTP Mode, Warm Start, and check again. SmartX is now SpaceLogic. KNOWN ISSUES with Firmware affecting RSTP: If Firmware 3.02.01 is installed, please upgrade to 3.02.02. RSTP not performing as expected with Static IP addressing RSTP does not work well on RPC HW RPC-16-B HW revision 6
View full article
Picard David_Purser Picard
‎2023-03-23 09:05 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
8479 Views
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 93
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of