Getting data from Rayleigh Instruments RI-78-80-C kWh Meter

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Getting data from Rayleigh Instruments RI-78-80-C kWh Meter
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3732 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Getting data from Rayleigh Instruments RI-78-80-C kWh Meter

Picard Product_Support
‎2018-09-11 07:08 AM

Last Updated: Crewman ContentModerator ‎2025-10-10 02:54 AM

Issue

How to get data from Rayleigh Instruments RI-78-80-C kWh power meters

Product Line

EcoStruxure Building Operation

Environment

  • EcoStruxure Building Operation Automation Server (ASP/ASB)
  • Modbus RTU Interface

Cause

The RI-78-80-C meter provides a single 48-bit Modbus RTU word representing energy in kWh. This word spans three 16-bit registers (registers 0, 1, and 2). The meter:

  • Only responds to a valid 48-bit read
  • Does not return exceptions for invalid or partial register reads

Resolution

To successfully read the 48-bit value:

Step-by-Step Instructions

  1. Create a Modbus Group
    • Set an appropriate polling interval.
  2. Add Registers
    • Add three 16-bit unsigned registers to the group:
      • ModReg0 (Register 0)
      • ModReg1 (Register 1)
      • ModReg2 (Register 2)
  3. Create an Analog Value
    • Example name: kWReading
  4. Script Program
    • Use the following calculation:
      kWReading = ((256 * 256 * ModReg0) + (256 * ModReg1) + ModReg2) / 100
      ​
    • This formula accounts for the fact that each register only uses half of its 16-bit range (values from 0 to 255).
    • The register values represent 1/100 of a kWh, so a scaling factor of /100 is applied.
  5. Bind Points

    • Bind the Modbus registers and analog value to the script program.

Example Calculation

If:

  • ModReg0 = 3
  • ModReg1 = 167
  • ModReg2 = 59
    Then:
    kWReading = ((3 × 256 × 256) + (167 × 256) + 59) / 100
              = 239419 / 100
              = 2394.19 kWh
    ​
    GavinHe_0-1755098122200.png

 

Additional Notes

  • The device may appear online in EcoStruxure even if it’s not responding correctly.
    • This is because the online poll interval mechanism expects a response from a 16-bit register.
    • Since the RI-78-80-C doesn’t respond to invalid reads, it may falsely appear online.
    • To avoid this, set the online poll interval mechanism to “Inhibit”. GavinHe_0-1755100617955.png

Compatibility Warning:

  • This device may not function correctly in v2.0 and v3.0 due to changes in offline detection.
  • This issue is resolved in v3.1.

Resources

  • Example Modbus Objects and Script
  • RI-78-80-C Exports.zip
Numeric Output kWReading
 
Line Calc1
kWReading = ((256*256*ModReg0) + (256*ModReg1) + ModReg2)/100
Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
RI-78-80-C Exports.zip
Tags (3)
  • Find more articles tagged with:
  • 18261
  • DavidShore20
  • GavinHeward25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore