Getting data from Rayleigh Instruments RI-78-80-C kWh Meter

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Getting data from Rayleigh Instruments RI-78-80-C kWh Meter
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Dave_Shore
    Dave_Shore
  • PaulFr
    PaulFr
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2997 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Getting data from Rayleigh Instruments RI-78-80-C kWh Meter

Picard Product_Support
‎2018-09-11 07:08 AM

Issue

How to get data from Rayleigh Instruments RI-78-80-C kWh power meters

Product Line

EcoStruxure Building Operation

Environment

Modbus RTU Interface

Automation Server

Continuum X-driver

Cause

The Rayleigh Instruments RI-78-80-C has a single 48bit Modbus RTU word available to be read (kWh)

It does not respond with an exception when an incorrect register is requested (or a single 16bit part of the 48bit word requested)

Only half of each 16bit registers within the 48bit word is used
Thus Register address 0, 1 and 2 can have a value 0-255 (00 00 to 00 FF) only

The value are actually in 1/100 kWh
Reg2 0 to 255 (255 = 255/100 kWh)Reg1 0 to 255 (255 = 255 x 256/100 kWh)Reg0 0 to 255 (255 = 255 x 256 x 256/100 kWh)
So if Reg0 = 3, Reg1 =167 and Reg2 = 59Then the reading would be(3 x 256 x 256 / 100) + (167 x 256 / 100) + (59/100)= 2394.19 kWh
The value is in 1/100 kWh
Reg2 0 to 255 (255 = 255/100 kWh)
Reg1 0 to 255 (255 = 255 x 256/100 kWh)
Reg0 0 to 255 (255 = 255 x 256 x 256/100 kWh)

Example
So if Reg0 = 3, Reg1 =167 and Reg2 = 59
Then the reading would be(3 x 256 x 256 / 100) + (167 x 256 / 100) + (59/100)
= 2394.19 kWh
 

Resolution

To read the three registers, Modbus Register Groups must be used within SmartStruxure, this ensure a single read is done for the 3 registers comprising the 48bit value.

Then a program can be used to calculate the actual meter value.

This device will not appear as online in SmartStruxure as the Device Online mechanism requires a response from a 16bit register read
(this device does not respond with an exception when an incorrect register is requested and has no 16bit registers to read)

 

Download an example of Modbus Objects and Script.

The below example script could also be atapted for Continuum Plain English Program

Numeric Input ModReg0, ModReg1, ModReg2
Numeric Output kWReading

Line Calc1
kWReading = ((256*256*ModReg0) + (256*ModReg1) + ModReg2)/100

Note

This device may not operate correctly in v2.0 and v3.0 due to a change in the method of offline detection, but this is fixed in v3.1

Numeric Output kWReading
 
Line Calc1
kWReading = ((256*256*ModReg0) + (256*ModReg1) + ModReg2)/100
Labels (2)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
Attachments
RI-78-80-C Exports.zip
Tags (2)
  • Find more articles tagged with:
  • 18261
  • DavidShore20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of