Collect logs from the Enterprise Server and Enterprise Central

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Collect logs from the Enterprise Server and Enterprise Central
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Katha
    Katha

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
5501 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Collect logs from the Enterprise Server and Enterprise Central

Picard Product_Support
‎2018-09-06 03:56 PM

Last Updated: Lt. Commander Katha Lt. Commander ‎2025-10-10 05:34 AM

Issue

When troubleshooting server issues, it can be helpful to look at the logs that are recorded within the Enterprise Server or Enterprise Central

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server
  • Building Operation Enterprise Central

Cause

Within the Enterprise Server and Enterprise Central logs are many records that are logged as a part of normal operations and unexpected events.

Resolution

Collect ES and EC Logs via EBO Workstation:

  1. Refer to the Workstation section of KB article: Collect logs from an Automation Server

Collect ES and EC Logs via Windows Explorer, especially if ES or EC will not run as a service or keep crashing:

  1. The ES or EC database path is listed in Software Administrator. 
    1.  For Windows 10, Windows 11, Windows Server 2016, 2019, 2022 the default paths for the logs folder are:
      1. Enterprise Server: C:\ProgramData\Schneider Electric [EcoStruxure|StruxureWare]\Building Operation [n.n]\Enterprise Server\db\logs
      2. Enterprise Central: C:\ProgramData\Schneider Electric EcoStruxure\Building Operation [n.n]\Enterprise Central\db\logs
    2. In EBO V3.2 or higher, shortcut buttons can be found in Software Administrator to go to the folder for logs and database directly. Software Administrator Logs.png

       

    3. By default, the "Program Data" folder is hidden, so Windows needs to be configured to view hidden files and folders. For Windows 10 or 11, open Windows Explorer and select View > Show > Hidden items. For other Windows versions, please refer to this Microsoft help article: Show hidden files (microsoft.com).View hidden items.png
    4. Using Windows Explorer, Navigate to the ES or EC logs folder to find System and Trace logs.Logs folder.png
    5. Copy the Logs folder contents and send them to Product Support as a compressed file if required.
    6. To open a log file, Right-click on one of the logs and select Open with...
      Open With.png
    7. Expand the window and select WordPad.
      Open With Wordpad.png
  •  

Other ways to review site-specific issues:

  1. Is the issue site-specific regarding workstation being used or applications/programs running on these machines? Always try to keep the programs on a workstation to a minimum.
  2. Review the Windows Event Logs. What specifically happens when an error occurs?
    Follow this KB article to view and save the Windows Events: Viewing, Saving, Sharing Windows Event Logs for Troubleshooting Purposes - Communities
  3. Make sure that PCs and Windows OS used for WorkStation, ES or EC meet the requirements mentioned in Information Technology System Planning Guide (se.com)
  4. Make sure that the firewall and antivirus are correctly configured, and required ports are open for EBO, as explained in Information Technology System Planning Guide (se.com)
  5. Make sure that the current installed EBO version is supported, as per the Software Support Policy for EcoStruxure Building Operation - PA-00300.
  6. Check if Microsoft currently supports the installed Windows OS: Lifecycle FAQ - Windows | Microsoft Docs
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (4)
  • Find more articles tagged with:
  • 7471
  • DavidPurser22
  • KatharineVasquez25
  • MahmoudSayed22
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore