Can TAC BACnet (Viconics) thermostats have identical names and deviceids within sub networks using their default names?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Can TAC BACnet (Viconics) thermostats have identical names and deviceids within sub networks using their default names?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1796 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Can TAC BACnet (Viconics) thermostats have identical names and deviceids within sub networks using their default names?

Picard Product_Support
‎2018-09-07 12:48 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:09 AM

Issue

Can TAC BACnet (Viconics) thermostats have identical names or device ids within sub networks using their default names?

Product Line

Andover Continuum, EcoStruxure Building Operation

Environment

  • Viconic BACnet Thermostats
  • BACnet
  • BCX
  • B4
  • MSTP

Cause

Viconic stats need a unique address and unique name across the entire BACnet network.

Resolution

  • BACnet Viconics thermostats must have a unique name and device id across the entire BACnet network.
  • The BACnet data link layer has two key parameters: the device object name and the device object ID.
  • The device object name must be unique from any other BACnet device object name on the BACnet network (i.e. not just the MS/TP sub-network).
  • Typically this question comes up because a thermostat will not come online.
  • Run an acctrace during the Find and you will probably see a duplicate MAC address.
  • Once you have given unique names and comm addresses to each of the thermostats on the entire BACnet network, these devices should communicate and come online properly.
  • Each of the Viconic stats are given a unique name that includes the address (once it has been made unique)

To change the communication address:

  1. Hold down the menu button until the option for menu comes up
  2. Answer the questions for the various options and eventually you will be brought to change comm address.
  3. Change Comm address, select Yes and then use the up or down arrows to give this MSTP Viconic stat a unique address.

There is a Configuration Tool to access and edit the name and device id unique naming scheme. Click here for ViconicsConfigurationTool.zip.

Installing and using the Viconics Configuration Tool on a Windows Laptop 

  1. You will need a serial adapter connection to tie into the MSTP bus that the thermostat(s) are connected to
  2. Select the Viconics folder > ViconicsConfigurationTool.zip
  3. You can install this ZIP file in any directory you wish, but the bacdocm.ini file must be installed on your C:\Windows directory.
  4. Use the bacdocm.ini file to configure your network settings at the Configurator Tool level.
  5. You can set the MAC address of your tool, the baud rate of your connection (max 38400 - limited by the RS-232 to RS485 port and Windows) etc.
  6. The "Our Device Instance" value represents the MAC address of the tool which must be unique on the MSTP network.
  7. Also the "MaxMaster" value must be set to a higher value than the highest MAC value on the MSTP network.
  8. You can edit this INI file to modify your settings OR you can modify the settings by going though the BACdoor Configuration Tool.
  9. Once you launch the Configuration Tool, you'll notice a white applet appearing at the right bottom of your screen. That is the BACdoor MSTP sniffer that actually looks for devices and objects.
  10. If you click on that icon, and select the "Configure" tab, a configuration window will be displayed. Select the baud rate at which you want to communicate with your device. This BACdoor configuration does the same thing as changing the BACDOCM.ini file (if properly located in C\Windows).
  11. Launch the Configurator Tool application. It automatically looks for devices on that network (at the baud rate set in the bacdocm.ini file or in the BACdoor Configuration window). If no device is detected an error message will pop-up after 1-2 minutes. All discovered devices will show up in the "Device List" you have to "Connect to device" in order to list all the objects of that device. After you changed the Baud Rate, you have to click on the "Apply changes" button.
  12. Don't forget that the max speed of this tool is 38400. For the first connection, you need to power cycle the thermostat (if it was running at 76800 previously) so that it auto-detects the 38.4 network.
  13. Once you set it to 76.8, you can not connect to that thermostat with the tool because of that 38.4 limitation. Also this tool does not support Read Multiple Property so it reads every property of every object one at a time.
  14. In its default mode of operation, the device will automatically match its baud rate to the baud rate of the network. Automatic baud rate detection will occur when the MS/TP communication port is initialized (on power up). If the network speed is changed, the device will keep listening at the previously detected speed for 10 minutes before resuming auto-bauding. Re-powering the devices will force right away auto-bauding.
  15. SE7xxx series requires the tool. The SE8xxx series does not as access is available through the menu on the device.
Labels (2)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
Attachments
ViconicsConfigurationTool.zip
Tags (1)
  • Find more articles tagged with:
  • 2641
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore