Extended Trend Log comparison, EcoStruxure Building Operation versus Continuum

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Extended Trend Log comparison, EcoStruxure Building Operation versus Continuum
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AbeMeran
    AbeMeran

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
896 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Extended Trend Log comparison, EcoStruxure Building Operation versus Continuum

Captain AbeMeran Captain
‎2025-03-23 06:41 PM

on ‎2025-03-23 06:41 PM

Issue

Why do the Architectural Guidelines specify a maximum of 1500 Extended Trend Logs in Automation Servers, whereas such a limitation did not exist with the Continuum Net Controllers, like the NetController II.

 

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Automation Server Premium
  • Building Operation Automation Server Bundled

Cause

EcoStruxure Building Operation's architectural guidelines specify a limit of 1500 Extended Trend Logs for the Automation Servers (AS-P/AS-B). Sites transitioning from Andover Continuum to EcoStruxure Building Operation need to understand the architectural differences that necessitate this limit.

ETLEBOServerGuidelines.jpg

Resolution

The architectural differences between Continuum and EcoStruxure Building Operation means that it is crucial that Extended Trend Logs are managed effectively to ensure ensuring optimal system performance.

 

In Continuum:

  • Controller Role: Controllers do not participate in Extended Trend Log functionality beyond sending data from intrinsic logs upon request from Cyberstations.
  • Log Management: Extended Trend Logs reside at and are managed by Cyberstations.
  • Load Distribution: Multiple Cyberstations, configured to collaborate, maintain the Extended Trend Logs, minimizing the load on controllers.

CyberPreferences.jpg

 

ExtLogPreferences.png

 

ContinuumTransferInterval.jpg

This design puts very little load on the controllers when it comes to Extended Trend Log functionality.

 

In EcoStruxure Building Operation:

  • Distributed Database Architecture: Extended Trend Logs are managed by the AS-P/AS-B servers.
  • Server Load: The server performs tasks typically handled by multiple Cyberstations in Continuum, which often run on more powerful PC hardware.
  • Performance Management: To prevent Extended Trend Log servicing from overwhelming the Automation Server's resources (CPU, memory), a limit of 1500 logs is enforced. Exceeding this limit can degrade server performance and potentially cause reboots due to critical memory usage.  This can be seen in the following example trace log entry: Nov 30 15:39:58 PSS-AS02 memcritsv[1011]: Memory usage critical!

 

 

Labels (2)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • AbeMeran25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore