Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Operation
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,840
  • TAC IA Series 1,823
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 329
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building operation"

View in: "Building Automation Knowledge Base" | Community

1838 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 31
    • 32
    • 33
    • …
    • 92
  • Next »
Label: "EcoStruxure Building Operation" Show all articles

Recovering from a Failed 1.4 upgrade

Issue Recovering from a Failed 1.4 upgrade. Product Line EcoStruxure Building Operation Environment StruxureWare Device Administrator Cause The upgrade to 1.4 requires special planning and site specific preparation. Before Upgrading you should always review the release notes with an eye for site specific implications. Please read these articles when performing an upgrade to 1.4: Reference Guide and References beginning with 1.4.x Contains detailed information about the changes to Reference Management in 1.4. Upgrading Automation Servers from 1.3 to 1.4 Contains the process for upgrading an Automation Server to 1.4 Resolution The following offers 2 scenarios for correcting issues post upgrade. Scenario 1 In this Scenario, the user will use the built in repair tools added in 1.4. These tools help the user fix issues that are typically fixed prior to upgrading. Please see Reference Guide and References beginning with 1.4.x for a complete description of the changes to the Reference Management in 1.4 In StruxureWare Workstation, browse to the Control Panel and click on "Reference Manager" Note the list of References with errors. Right Click on each item and click "Edit Bindings". Re-Bind any questionable item using the new rules for Reference management. Scenario 2 In this Scenario, the user will downgrade the system to 1.3. This is not a preferable solution, but may be required in specific instances. Please note, that in order to downgrade, you must have a valid backup of the ES and every AS from prior to the 1.4 upgrade. If you do not have a valid 1.3 backup, you will need to use Scenario 1. You will also need to be able to apply any service packs or hotfixes previously used. Validate that you have a 1.3 backup of the AS and every ES by going to C:/ProgramData/Schneider Electric StruxureWare/Building Operation 1.3/Enterprise Server/db_backup. If the Backups are present and the date and time stamps are acceptable, then copy these to another location, to ensure they are not lost. You can either install 1.3 on a second PC or install on the same PC. For this example, we are installing 1.3 parallel to the 1.4 upgrade. Stop the 1.4 enterprise server before proceeding. As you install each piece of software you will be informed that the installation will be done parallel to the current version. The exception to this is the License Server. You can have only one license server installation of any build on the same PC. After you have installed all of the 1.3 Software, Install any Service Packs or Hotfixes that had previously been installed on site. When you are finished, the Start Menu will show the parallel installations of StruxureWare. Open Device Administrator Connect to the AS or all AS Click Upgrade and select "New database" Click OK There is no point to attempt to upgrade the database to 1.3 as any problems will be converted back as well. Log into each Automation Server separately, right click on the server in the system tree, and click Restore. Import the backup set you have from prior to the 1.4 upgrade. Note that Red text indicates that your current build does not match the build used for that backup. At this point, you system will be back at 1.3, and should be running as it was before the upgrade, or at the very least, it will be at a manageable level. Use the links above to correct any Reference issues before proceeding with the 1.4 upgrade.
View full article
Picard Product_Support
‎2018-09-11 05:54 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 01:14 AM

Labels:
  • EcoStruxure Building Operation
1232 Views

Trend Logging in an AS - Storing multiple years of logged data

Issue How can many years worth of logged data be stored in an Automation Server? Product Line EcoStruxure Building Operation Environment Trend Logging Extended Trend Logging AS Cause Site requirements may dictate that longer-than-usual histories of data be kept on file. For example, to log a value every 5 minutes for 2 years equates to approximately 105120 records per year. A Trend log in an AS will store 1000 records. An Extended Trend Log will store 100,000 records. Therefore a single log will start to overwrite in about a year. For the latest up to date values please review  Maximum number using StruxureWare Building Operation (Scalability and Capacity). Resolution To overcome this issue, two Trend Logs and Extended Trend Logs are required. Create a Trend Log and Extended Trend Log for Year 1 (Odd Years). Create a second Trend Log and Extended Trend Log for Year 2 (Even Years). Both of the above Trend Logs with be set to log the same variable. Create a program to select if the year is "odd" or "even", a possible Script might be. In each trend log select the "Activation Method" as "Variable Controlled", and in the "Activation variable" field, "Browse" to the "Script Program" output that is appropriate. Logging will now take place in the Trend Log appropriate for that year.
View full article
Picard Product_Support
‎2018-09-11 09:48 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 11:23 PM

Labels:
  • EcoStruxure Building Operation
1494 Views

Sigma alarms are not received at the Enterprise Server

Issue Alarms are produced by Sigma controllers, but these alarms are not received at the Enterprise Server Product Line EcoStruxure Building Operation, Satchwell Sigma Environment Enterprise Server Sigma 4.08 Alarms Delayed alarms Transition Cause When Sigma alarms are manually tested from the Enterprise Server, the alarms are received normally, but alarms occurring during normal operation on the Sigma system, can be delayed, or not displayed at all at the Enterprise server. This issue is caused by the firewall. If the Enterprise Server is initiating the communication with the Sigma controllers, then the firewall will normally allow any alarm messages from the Sigma controllers to pass through the firewall, and the alarms be displayed normally. When the Enterprise Server is not initiating the communication the Sigma controllers, then the firewall will normally prevent any Sigma alarm messages from passing through, and therefore the Sigma alarms will not be displayed. Resolution The solution is to allow inbound communication to the Enterprise Server PC on port UDP 49152 Depending on the firewall used, the configuration steps can vary. If Windows Firewall is not used: Consult your vendor manual. Example of Windows Firewall not being used If Windows Firewall is used but managed by the IT department: Consult with your IT department. Example of Windows Firewall being managed by IT If Windows Firewall is used and you can manage it: See below Windows Firewall A quick solution is to use "SBO Firewall Config". While the tool is not officially supported, it has been used by various sites. To manually add the exception to Windows Firewall, refer to Using Sigma on Windows 7 with firewall.
View full article
Picard Product_Support
‎2018-09-11 12:53 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 11:14 PM

Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
1406 Views

Problem communicating across the LAN on Windows 7 and above PCs

Issue Continuum / Vista / I/NET / StruxureWare etc will not connect to any of the controllers on the LAN when using a Windows 7 and above PC. Product Line Andover Continuum, EcoStruxure Building Operation, TAC INET, TAC Vista Environment I/NET 2.4x Continuum Vista StruxureWare Windows 7 8 8.1 10 Cause This is due to Microsoft improving their security in Windows 7 and above that will now block many types of connections across a network. Resolution To enable communications across the network; Disable all firewalls and any Anti-Virus software on the PC. (SE laptops, right click on McAfee shield, Quick settings and un-tick everything, this will temporarily disable the AV and firewall) Disable User Administrator Control (UAC) (As per Disabling administrator rights messages in Windows 7 OS and above) Re-install I/NET Seven / Continuum / Vista etc
View full article
Picard Product_Support
‎2018-09-07 07:02 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 11:13 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • TAC INET
  • TAC Vista
1386 Views

Unable to setup alarm enrollments for AS, functionality is grayed out

Issue Event notification is grayed out in the AS and will not allow configuration.  Cannot add a category within the AS. Product Line EcoStruxure Building Operation Environment SmartStruxure Shadow AS Event Notification Cause The Event Notification in the AS can be locked due to a shadow relationship with an Event Notification in the ES. Resolution Note the IP address of the AS, as the shadow relationship can be re-established after necessary changes are made. Remove the shadow relationship to the ES to allow configuration of the AS. Detailed instructions can be found in Unable to add an Automation Server underneath an Enterprise Server. Re-established the shadow relationship if needed.
View full article
Picard Product_Support
‎2018-09-10 10:35 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 11:06 PM

Labels:
  • EcoStruxure Building Operation
1516 Views

XBuilder will not allow a connection between a third party LON device and a graphic

Issue Cannot connect network variable point from a third party LON device to a graphic within an XBuilder project.  XBuilder will not allow the drag and drop of LON network variable between the network pain and the system pain when you attempt to create connections. Product Line EcoStruxure Building Operation, TAC Vista Environment XBuilder Vista Lon Device .xif Cause XBuilder is very particular about the format of an .xif file and it will not allow certain characters in the function block name. Vista and LonMaker have far less limitations and these programs are able to parse these characters without causing problems. This explains why your values may show up in the LNS management tool and Vista Workstation. However, once you import the network into XBuilder you are unable to connect the SNVTs to your graphic. Resolution Replace the incorrect characters in the function block line of the .xif and reload the new .xif into your LonWorks Network.  Please see LON device can communicate in Vista, but fails in a Xenta Server / XBuilder for more information about incorrect characters in an xif file. INCORRECT FUNCTION BLOCK EXAMPLE: File: MP580.XIF generated by NODEUTIL Revision 1.46, XIF Version 4.0 Copyright (c) 1997 by Echelon Corporation All Rights Reserved. Run on Fri Oct 31 16:30:28 2003 80:00:2A:52:00:03:04:03 2 15 1 618 0 8 8 4 4 11 11 0 0 0 0 3 0 16 0 0 1 65536 618 0 0 0 0 0 0 0 0 0 0 0 0 10000000 1 7 1 0 4 4 4 15 200 0 78125 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 1 5 8 5 12 14 15 * "&3.4@0,20000-MP580,8500-SCC,8610-DAC The problem is the three dashes  between the object numbers and the object names in the self doc string.  This is "allowed" in Vista and LonMaker in some sense.  For  example, Vista "replaces this "-" to a "/" but then XBuilder can't handle this situation properly. CORRECTED EXAMPLE: File: MP580.XIF generated by NODEUTIL Revision 1.46, XIF Version 4.0 Copyright (c) 1997 by Echelon Corporation All Rights Reserved.  Run on Fri Oct 31 16:30:28 2003 80:00:2A:52:00:03:04:03 2 15 1 618 0 8 8 4 4 11 11 0 0 0 0 3 0 16 0 0 1 65536 618 0 0 0 0 0 0 0 0 0 0 0 0 10000000 1 7 1 0 4 4 4 15 200 0 78125 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 1 5 8 5 12 14 15 * "&3.4@0,20000MP580,8500SCC,8610DAC;Tracer MP580 The dashes 3 x (-)s have been removed from the function block name
View full article
Picard Product_Support
‎2018-09-10 12:53 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 10:41 PM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1652 Views

Editing an exported XML file is not supported

Issue Is editing an exported XML file supported? Receive errors when attempting to import (a modified) exported XML file. Product Line EcoStruxure Building Operation Environment StruxureWare Building Operation Export / Import  Cause There is minimal error checking on the import so errors could get through and cause problems further down the line and corrupt the database. Resolution Edited exported XML files is not supported and there is no documentation on how to properly edit exported files. This practice should not be attempted.   With 1.5 will comes Project Configuration Server (PCS) and the ability for the businesses to create their own country specific applications and mass create engineering tools. In a future release (currently indicated in 1.6) support for using the Backup and Restore feature to duplicate entire Automation Server databases will be available.  For now both these functions are not supported.  Refer to Do NOT use Backup and Restore to duplicate Automation Server databases! (1.5 and below).
View full article
Picard Product_Support
‎2018-09-11 06:34 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 10:36 PM

Labels:
  • EcoStruxure Building Operation
1584 Views

Shadow Schedule in the Automation Server is not syncing to the Lead Schedule in the Enterprise Server

Issue Shadow Schedule in the Automation Server is not syncing to the Lead Schedule in the Enterprise Server Shadow Schedule in the ES syncs successfully to Lead Schedule in the AS Lead and Shadow Schedules in different AS are syncing successfully Product Line EcoStruxure Building Operation Environment SmartStruxure 1.x Cause Traffic is blocked by Windows Firewall.  Resolution Disable Windows Firewall. Disabling the firewall may not be possible due to security concerns, Exceptions can be added to Windows Firewall for ports that are used by SmartStruxure. Refer to Creating Windows Firewall rules to allow StruxureWare Building Operation to communicate on the TCP port for details. If this doesn't work, please refer to Shadow Schedule in AS isn't synchronized with the Lead Schedule in ES.
View full article
Picard Product_Support
‎2018-09-11 06:09 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:58 PM

Labels:
  • EcoStruxure Building Operation
1639 Views

Not all traffic on a segment is captured when using the LPA through an Automation Server

Issue When using the LPA through an Automation Server (AS) as described in Using Loytec LPA with SmartStruxure AS, only traffic to and from the AS is captured. Product Line EcoStruxure Building Operation Environment LPA Automation Server Cause Due to a hardware limitation in the AS, it's not possible to capture all traffic on the segment Resolution Connect the LPA to the segment using a NIC-USB100 or similar
View full article
Picard Product_Support
‎2018-09-11 08:45 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:55 PM

Labels:
  • EcoStruxure Building Operation
1674 Views

Unable to Upload or display point data on an I/NET Controller in StruxureWare Workstation

Issue Unable to Upload or display point data on an I/NET Controller in StruxureWare Workstation Environment I/NET to StruxureWare Integration Cause The most common cause for I/NET controllers to not integrate with StruxureWare are duplicate point names or illegal characters in use Resolution In Building Operation Workstation, right click on the errant I/NET controller and select "Upload" This is expected to fail at this point Browse to the Enterprise Server Directory as displayed in Building Operation Software Administrator Look in the db/Logs folder Locate the trace log and open it using a text editor scroll to the last line of the log and look for an entry that contains inet information. If the error is caused by duplicate point names, this will be the trace log entry: 2014-01-30 20:00:25.587 [6220] nsp.pin.inet.GetAllPoints InetPlugIn::ProcessChangeSetList failed RecoverableException: d:\dev\rb-int-v140-sp1-system\source\packages\commons\components\C3Po\nsp_servers\csc\changesetmanager\source\ChangeSetTransaction.cpp(987) Error: Object_Already_Exists (0x40006), module Runtime_Db_Manager(41), moduleCode 0, dispString "~/INET Interface/0321 - SBOtester/Point1", techString "" Note the text dispString "~/INET Interface/0321 - SBOtester/Point1", techString "" This indicates that there is a point on the controller named "Point1" which is causing the error Option 1: In I/NET workstation, connect to the controller Rename the point indicated above Perform a station save and attempt to upload the controller again. If it fails a second time, repeat steps 3-10 until you have removed all illegal entries Option 2: Use RdInet to view the Save file. Click on Save Page Open the .csv file in Excel and sort the data by Name Locate the Point indicated above and notice that there will be 2 objects of the same name. In I/NET identify these 2 points. Very likely, one will not actually exist. Copy the Point that exists to the address that was indicated as a duplicate in Excel Delete the newly created point to permanently remove the object from the .sav file. Perform a station save and attempt to upload the controller again. Repeat this process if necessary.
View full article
Picard Product_Support
‎2018-09-11 02:29 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:55 PM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
1604 Views

Troubleshooting I/NET .gpg to TGML Graphics conversion

Issue Various problems with converted TGML graphics Bindings of the I/NET objects within Building Operations have wrong and / or illegal point address. Environment I/NET integration with SmartStruxure Cause Improper preparation before converting graphics may cause nuisance issues. Resolution Ensure the following is done when converting a sites I/NET graphics to TGML Before converting the graphics to TGML Ensure all save files are current Ensure the I/NET network configuration is current Before importing the graphics to StruxureWare Ensure that all affected controllers are imported.  Do not change any names or descriptions before importing graphics Upload any controller which indicates it is required. This will ensure that point names for graphic bindings are correct. In the INET Interface path box, enter the path to where the INET interface is located in WorkStation. This setting affects the bindings that get defined for objects in the resulting TGML file(s). If you accepted the default name when you created the I/NET interface in WorkStation, this path is typically /Server 1/INET Interface/.  Make sure this matches the installed system details.   Click Here to get more detail from the Online Web Help. Check out the I/Net Transition: Graphics Conversion video on the Community website.
View full article
Picard Product_Support
‎2018-09-11 01:51 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:49 PM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
1549 Views

International standards and approvals SmartStruxure been tested against

Issue What are the product certifications? Product Line EcoStruxure Building Operation Environment SmartStruxure for Buildings AS ES Cause Standards documentation required. Resolution Click here for the CE Declaration of Conformity Click Here for the WSPCert For  BACnet BTL Testing see the PICs statements or the BTL Website: http://www.bacnetinternational.net/btl/ For UL and Country of Origin certification, please refer to PSS for this.
View full article
Picard Product_Support
‎2018-09-11 11:54 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:44 PM

Labels:
  • EcoStruxure Building Operation
1568 Views

Type does not exist

Issue When trying to add an automation server underneath an enterprise server the following error is given. Product Line EcoStruxure Building Operation Environment Workstation  Automation Server Cause Something has been left behind in the automation server that causes a conflict. Resolution Reformat the automation server by performing a New database download. Create a backup of the automation server. See Backup of StruxureWare/EcoStruxure Building Operation AS and ES. Launch Device Administrator and add the automation server. Select the automation server and click on the Upgrade Device button in the top left corner.  In the Upgrade device window, choose "New database" in the Type of upgrade field. Click OK. Once the download is complete, log into the automation server and restore the database. See How to restore a StruxureWare Building Operation server backup set. Now add the automation server underneath the enterprise server.
View full article
Picard Product_Support
‎2018-09-11 05:14 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:42 PM

Labels:
  • EcoStruxure Building Operation
1774 Views

Best practice on adding reference host and creating routing table

Issue Host conflict window always pops up, and cleaning routing table doesn't help. Product Line EcoStruxure Building Operation, TAC INET Environment I/NET Cause Host conflict is a normal issue happening in I/NET. It is usually caused by the duplicated host ID setting on different servers, or an engineer laptop is inserted into the network with the same host ID setting with some server. And the routing table will be messed up since all the IP related information will be recorded in the routing table and it will be distributed to all the network devices, including all the servers and NPRs. The usual solution is to clear all the routing tables on all the network devices, . Refer to How to Remove the Routing Tables in a Device or PC about how to clear the routing tables. But if the routing table is cross referred, like Server 1 adding NPR 1 and NPR 2 as reference hosts, while NPR1 adding Server 1 and NPR 2 as reference host, the routing table will never be cleaned out since when you clean the routing table for Server 1, NPR1 and NPR 2 will still try to send their wrong routing table to Server 1. Unless all the network devices are disconnected and the routing tables are cleaned one by one, or disable the 50069 port for the whole network, which is used by the communication between network devices, there is no other way to clean them out. And these two method are not applicable sometimes. Resolution If the routing table can be managed well, such kind of issue will never happen. The best practice on adding reference host and creating routing table is: On the servers: Choose one server as the master reference host. All the other servers add this server as reference host. Don't add NPR as reference host. All the NPRs can be added into the master server by clicking on the NPR button in I/NET configuration and added one by one manually. By this way, the master server can build its own routing table without impacted by other devices. And this one is the only routing table in the whole network. On NPRs. If NPR doesn't need to talk to other NPRs, like transferring indirect points, there is no need to add reference host for NPR. If indirect points are needed, just add the master server as the reference host. Then this NPR will be able to see all the other NPRs based on the routing table on the master server. If the master server is not equipped with UPS, or not always promises to be online, another master NPR can be chosen as a secondary reference host. Add this NPR as a reference host to all the servers and other NPRs. Under this scenario. if the routing table needs to be cleaned, only the master server and the secondary reference host need to be cleaned. It will be more easier to clean all the routing table and get rid of the host conflict error.
View full article
Picard Product_Support
‎2018-09-11 01:42 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:36 PM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
1499 Views

Windows Alignment Issue for I/NET display

Issue When I/NET is running under Windows 7, there will be a display issue about alignment. The font size has been changed to smaller - 100%, but still no use.  Product Line EcoStruxure Building Operation, TAC INET Environment Windows 7 Cause Be sure to try I/NET Seven Windows fields not aligning correctly on workstation's display to change the font size first to see whether it can help. If not, continue to the next information. I/NET used the default MS Sans Serif font to display everything. But something has changed in Windows 7 about the font display.  Research showed that many users with high resolution monitors (particularly LCD flat screens) were running the monitors at lower resolutions than the native resolution of the screen. This was usually because at the native resolution, the fonts were becoming too small to read, so the users would decrease the resolution. Windows includes a facility to increase font and window sizes while keeping the screen at the native resolution.  This is a much better method of increasing the font size as it can produce much smoother images by using many more, smaller pixels. The really significant issue is, unlike CRT monitors, flat-panel LCD monitors have a fixed pixel size, or "resolution", and that when users change to a lower resolution (in order to increase text size) the system has to re-sample the lower-resolution display image into its fixed resolution causing a significant degradation in display quality: not just text looks worse, everything looks worse. A change was made for Windows 7, to set the screen resolution to the monitor's native resolution and if the screen is over a certain resolution to default the font size 120 DPI (dots per inch). This is approximately 125% of normal 96 DPI (100%). When the system defaults to 125% DPI it also adjusts the MS Sans Serif font to be bigger.  If the user then decides to set the DPI back to 100%, then TrueType fonts, which are scalable, adjust as expected. But the bitmap MS Sans Serif font does not: it remains at the larger size, hence this issue. This problem does not occur if Windows 7 keeps DPI at 100% when it is first installed. So anyway, when the default font size is Medium - 125% instead of smaller - 100%, probably the solution below is needed to solve it. Resolution Go to the Registry Editor, and find HKEY_LOCAL_MACHINE\SOFTWARE\Microsoft\Windows NT\CurrentVersion\Fonts. Find the entry MS Sans Serif 8,10,12,14,18,24. The original value is set to SSERIFF.FON on a system which started at 125% DPI. Set to SSERIFE.FON on a system which started at 100% DPI.  Notice that one character of the file name changes from F to E. Restart the computer, and make sure the font size is set to smaller - 100%. Refer to I/NET Seven Windows fields not aligning correctly on workstation's display about how to set font size. Then it should go back to work.
View full article
Picard Product_Support
‎2018-09-11 02:54 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:35 PM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
1567 Views

Alarms not coming into ES from I/NET

Issue Alarms being generated in I/Net are not showing up on the Enterprise Server. Product Line EcoStruxure Building Operation, TAC INET Environment SmartStruxure Integration with I/Net Alarms Cause Alarms generated in I/Net are not populating on the Alarms Window on the ES, all masking are set on both the AMT Configuration and Host Masks. When the point goes into Alarm, it populates the Alarm Window type, whether it is Priority or Critical with said point address. However, it does not show up on the Alarms page because the bin files on the controller needs to be updated to the latest version of software and all points need to be saved prior to integrating with SmartStruxure. Resolution When integrating with SmartStruxure, all controllers are supposed to be updated with the latest version of software as well as sav files, per Resetting a 7793 Controller and PCU (Applies to 7793, 7716, 7728, 7756). Once completed, recheck the points by putting them in Test mode so that they can generate the Alarm condition and it should show up in the ES Alarm now.
View full article
Picard Product_Support
‎2018-09-11 06:20 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:33 PM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
1495 Views

Navigating to a TAC Vista TGML Graphic from a SmartStruxure TGML Graphic through TAC Vista Webstation

Issue The TGML page is dynamic but looks static. Product Line EcoStruxure Building Operation, TAC Vista Environment Vista StruxureWare Interface Cause In the Release Note, page 30 says: It is possible to navigate to a TAC Vista Webstation TGML Graphic through a link in a SmartStruxure TGML Graphic. To achieve this connection a link object is created in the SmartStruxure TGML Graphic which is linked to a SmartStruxure hyperlink object that holds the TAC Vista Webstation TGML Graphic page address. Example of a hyperlink objects address in SmartStruxure that is linked to a TGML Graphic in TAC Vista: HTTP://ip_address/webstation/LoginPage.aspx?page=TgmlGraphicsPage.aspx?objectId=3074949137 Note: This will always require a login by a valid TAC Vista user, even if the TAC Vista Webstation auto login feature has been activated. Resolution The example link above is referring to a static page. For example, if the TGML page is dynamic, you will see the following in the copied link (see bold). HTTP://ip_address/webstation/LoginPage.aspx?page=TgmldynamicGraphicsPage.aspx?objectId=3074949137 You can also read the following in the release note: In order to determine the TAC Vista Webstation URL for a TAC Vista Webstation TGML Graphic the following TAC Vista Web Setting configuration must be in place: Optimized TGML Loading is deactivated Folders pane is set to Standard HTML With these settings it is possible to right-click a TGML object in the folders pane and select "Copy Shortcut." This will copy the TAC Vista Webstation URL to the clipboard and it can then be pasted into a SmartStruxure hyperlink object address field. After the shortcut has been pasted, it will have to be modified in order for the TAC Vista TGML Graphic to be displayed properly in SmartStruxure. The modification is marked with bold in the example below: Copied: HTTP://ip_address/webstation/TgmlGraphicsPage.aspx?objectId=3074949137 Modified: HTTP://ip_address/webstation/TgmlGraphicsPage.aspx?objectId=3074949137 If the link you copied was a dynamic TGML the link will look like: HTTP://ip_address/webstation/TgmldynamicGraphicsPage.aspx?objectId=3074949137 and should be modified as this HTTP://ip_address/webstation/LoginPage.aspx?page=TgmldynamicGraphicsPage.aspx?objectId=3074949137 Also reference the TAC Vista Webstation Graphics Links and SmartStruxure Integration tool on the Community.
View full article
Picard Product_Support
‎2018-09-11 11:25 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:31 PM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1581 Views

Memory Usage in TAC Menta/TAC Xenta

Issue How to check the amount of used memory in a TAC Menta/TAC Xenta application. Product Line TAC Vista Environment TAC Menta Xenta 281 Xenta 301 Xenta 401 Cause When programming applications for TAC Xenta, you may want to be able to check the size of your application, to verify that it can be downloaded to the device. Resolution To be able to check how much memory an application is using, the application needs to generated. In TAC Menta, edit mode: Select Option, Simulate to enter Simulate mode. In Simulate Mode, select Commands, Generate, to generate the application. To be able to check the Memory usage, you have to return to Edit mode, Select Options, Edit. Now you can check the Memory usage by selecting Options, Memory Usage... As this calculation is done on your PC, and not in the device, and that the memory in the TAC Xenta device is dynamic allocated, it is a recommendation to have at least 10% free memory in each category to avoid future problems. For more information about the Advanced button, please see TAC Menta Advanced Memory Usage: BPR Size Calculator.
View full article
Kirk MikaelKrantz Kirk
‎2019-05-15 03:30 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:23 PM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1384 Views

Import all converted I/NET graphic folders into EcoStruxure at one time

Issue In order to make page links between different I/NET graphic folders work fine, the same folder structure needs to be created manually in EcoStruxure / SmartStruxure. Refer to Converting I/NET graphics to TGML using the "Create Source Tree" option to realize this. Product Line EcoStruxure Building Operation, TAC INET Environment EcoStruxure / SmartStruxure 1.4 or higher I/NET Cause The I/NET graphic folder structure will not be created automatically before SmartStruxure 1.4.0. Resolution Starting in version 1.4.0, there was a new feature called Data import for I/NET graphic. Using this feature, all the converted I/NET graphic folders structure can be imported at one time without any need for manual work. Here are the steps to make it work: Convert the I/NET graphics according to Converting I/NET graphics to TGML using the "Create Source Tree" option, but do not create the folder structure manually in EcoStruxure / SmartStruxure. Create the default Inet Graphics folder by right clicking on I/NET Interface-->New. Right click on Data Import and choose the root folder of all of the I/NET graphics. Click OK. Data importer will check all the file names and bindings. If any error happens, check and fix it before importing again. (Currently apostrophe is not supported in SmartStruxure. Change the name and relative link and do it again. It may be fixed in later version) Check whether all the bindings and links work fine. Important: Currently this feature doesn't support export/import in SmartStruxure. It will fail to import if any sub folders are contained under INET interface. This may be fixed in later version. The workaround is to still create the whole structure according to Converting I/NET graphics to TGML using the "Create Source Tree" option.
View full article
Picard Product_Support
‎2018-09-11 10:10 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:13 PM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
1493 Views

Xenta Operator Panel will not recognize Xenta controllers in a SmartStruxure network

Issue The TAC Xenta operator panel will not display controllers on the network even though it has the correct StruxureWare Domain ID entered and is set to manual mode. Product Line EcoStruxure Building Operation Environment TAC Xenta Operator Panel StruxureWare Cause StruxureWare Building Operation sets its LonWorks Domain ID to a decimal value. The TAC Xenta Operator Panel needs the hexadecimal value in order to operate properly. The decimal value must be converted to hexadecimal. Resolution In order to locate the domain ID of a LonWorks Network, see How to locate and change the LonWorks domain ID. Converting a decimal value to hexadecimal using a calculator Open the calculator on your computer. If Windows go to Start > All Programs > Accessories > Calculator. In the View menu, select Programmer. Enter in the decimal value of the domain ID. Select the Hex button on the left side of the calculator. The domain ID has been converted to hexadecimal. In the example, the domain ID 0B should be entered into the operator panel and set to manual mode.
View full article
Picard Product_Support
‎2018-09-10 10:36 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 09:00 PM

Labels:
  • EcoStruxure Building Operation
1424 Views
  • « Previous
    • 1
    • …
    • 31
    • 32
    • 33
    • …
    • 92
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of