Compatible SpaceLogic Sensors for TAC Xenta 100 Series Controllers
  • Compatible SpaceLogic Sensors for TAC Xenta 100 Series Controllers
  • RandyDavis
    RandyDavis
  • MikaelKrantz
    MikaelKrantz
Guinan MikaelKrantz Guinan
‎2021-11-08 12:43 PM
Last Updated: Administrator CraigEl Administrator ‎2023-11-08 03:20 PM
Which SpaceLogic Sensors could be used with the TAC Xenta 100 series controllers?
TAC Vista
  • ZBuilder
  • Xenta 122
The STR100-series sensors will be withdrawn, and SpaceLogic Sensors have been identified as suitable replacements.
Only TAC Xenta 122 controllers can be configured to use 10K Type 3 Thermistor.
To integrate SpaceLogic Sensors with the TAC Xenta 122 controllers, follow these steps in ZBuilder:
  1. Access the Configuration tab.
  2. Navigate to the Room unit settings.
  3. Locate the checkbox labeled "Use STR-5xx series" and select it.
Please note that only the SLASXXX, SLABXXX, and SLAWXXX models are compatible with the TAC Xenta 122 controllers. These sensors, however, do not feature buttons for setpoint adjustment or fan control.