Host SpaceLogic IP device located in a remote subnet using BBMD

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Host SpaceLogic IP device located in a remote subnet using BBMD
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Mahmoud_Sayed
    Mahmoud_Sayed

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
5 Likes
6370 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Host SpaceLogic IP device located in a remote subnet using BBMD

Kirk Mahmoud_Sayed Kirk
‎2023-11-21 02:33 PM

on ‎2023-11-21 02:33 PM

Issue

SpaceLogic IP device is located in a remote subnet and EcoStruxure BMS server can't discover it.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server
  • Building Operation Automation Server
  • Building Operation Automation Server Premium
  • Building Operation Automation Server Bundled
  • Building Operation Edge Server - Standard
  • Building Operation Multi-purpose Controller
  • Building Operation Multi-purpose VAV
  • Building Operation Room Controller (RPC)
  • Building Operation IP-IO

Cause

BACnet broadcast messages, such as Who is/I am that are used for device discovery, will not be forwarded between the two IP subnets. BACnet Broadcast Management Device (BBMD) is required to allow BACnet to operate through IP routers.

Resolution

Scenario 1:

SpaceLogic BACnet/IP device is located in remote subnet with no EcoStruxure BMS server or BBMD located in same subnet. EcoStruxure BMS server will be configured as BBMD, and SpaceLogic BACnet/IP device will be configured as foreign device and register itself with BBMD (which is the AS-P in our example). 

Scenario 1.png

 

The following video will illustrate how to:

  • Configure SpaceLogic BACnet/IP device located in foreign IP subnet as a foreign device.
  • Configure an EcoStruxure BMS server as BBMD.
  • View foreign device registration on the EcoStruxure BMS Server.
  • Discover and host the SpaceLogic BACnet/IP device.

[video]

 

Scenario 2:

SpaceLogic BACnet/IP device is located in remote subnet with a 3rd party device that can be configured as BBMD. In the other subnet, EcoStruxure BMS server will also be configure as BBMD. SpaceLogic IP device will not be configured as foreign device as there is BBMD device in the same subnet. This BBMD will redistribute the essential broadcast messages to it. Once configured, EcoStruxure BMS server will be able to discover and host the SpaceLogic BACnet/IP device and other BACnet deviced located in the remote subnet.

Presentation1.jpg

 

The following video will illustrate how to:

  • Configure SpaceLogic BACnet/IP device located in a remote IP subnet.
  • Configure an EcoStruxure BMS server as BBMD.
  • Configure Broadcast distribution table (BDT) in EBO.
  • Use BACnet browser to check and verify the BDT configuration of a 3rd party BACnet device.
  • Discover and host the SpaceLogic BACnet/IP device and 3rd party BACnet devices located on remote subnet.

[video]

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • MahmoudSayed23
Was this article helpful? Yes No
100% helpful (5/5)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore