SmartXKiosk PIN Reset

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SmartXKiosk PIN Reset
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • GavinHe
    GavinHe
  • David_Kendrick
    David_Kendrick
  • StephenYang
    StephenYang
  • Robert_Davis
    Robert_Davis
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
4694 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SmartXKiosk PIN Reset

Picard Product_Support
‎2018-09-06 08:45 AM

Last Updated: Sisko GavinHe Sisko ‎2023-10-25 07:48 AM

Issue

The 6 character PIN for the SmartXKiosk has been forgotten so the user cannot exit Kiosk mode

Note the PIN is case sensitive

Product Line

EcoStruxure Building Operation

Environment

  • SmartXKiosk
  • Advanced Display v1
  • Advanced Display v2
  • SmartX Controller

Cause

The 6 characters PIN for the SmartXKiosk has been forgotten or lost and the user cannot locate it.

Resolution

In order to reset your SmartXKiosk PIN, follow the steps below:

 

  1. In the SmartXKiosk application, click on Exit Kiosk Mode in the bottom right corner of the screen.
  2. In the Exit Kiosk Mode window, click on Forgot PIN?. An 8 characters or 15 characters Session ID will be generated.  Take note of this Session ID. 
    StephenYang_0-1685560587502.png

     

  3. Open a ticket with Support to request a SmartXKiosk PIN reset and provide them with the Session ID.
  4. Once Support sends you back the Recovery PIN, click Continue on the Session ID window.
  5. In the next window fill in the Session ID from step 2. and the Recovery PIN that Support has provided. Click Continue.
  6. You can now reset your PIN. Enter your new 6-digit PIN number and confirm it before clicking Submit. The PIN is case sensitive. It must be exactly 6 characters, otherwise an error will occur. 
  • Important Note: The Session ID generated and the Recovery PIN provided to you by Support will expire at midnight on the day that the Session ID was generated.  

Note: For Advanced Display v3 please see How to recover the password for Advanced Display version 3

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (13)
  • Find more articles tagged with:
  • 18140
  • advanced
  • android
  • code
  • DavidKendrick22
  • display
  • GavinHeward23
  • lock
  • lockout
  • out
  • password
  • StephenYang23
  • tablet
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore