AS goes offline at the ES due to high CPU usage
  • AS goes offline at the ES due to high CPU usage
  • Jonas_Brissman
    Jonas_Brissman
  • sesa139513
    sesa139513
  • sesa125819
    sesa125819
‎2018-09-07 02:14 PM
Last Updated: Janeway Jonas_Brissman Janeway ‎2023-10-23 01:25 AM
Communications with an AS can fail due to high CPU usage and it goes offline in the ES.
  • Building Operation Automation Server Premium(AS-P)
  • Building Operation Automation Server(AS)
A large graphic was being edited and when saved, the AS appeared to crash, but had actually gone offline to the ES.
This issue was due to the AS CPU usage, which was found to be very high and was making the AS appear to be offline to the ES, when the graphic was saved.
The graphic that was being edited was accessing a large number of Universal Inputs, and these input values were changing frequently, this in turn was causing the increased CPU usage.
Changing the threshold setting of a Universal Inputs.
  1. Select the properties of the universal input to be adjusted.
  2. View the configuration section and select the threshold value.
  3. Enter an appropriate value for the input being modified.