Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Operation
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building operation"

View in: "Building Automation Knowledge Base" | Community

1895 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 93
    • 94
    • 95
  • Next »
Label: "EcoStruxure Building Operation" Show all articles

Locked in SmartXKiosk after first-time startup before a password has been set

Issue After starting up the SmartX Advanced Display for the the first time, the operator finds himself stuck in SmartXKiosk mode before having any chance to select a password/PIN code. Product Line EcoStruxure Building Operation Environment Advanced Display v1 Advanced Display v2 Cause SmartXKiosk has been selected as launcher. The first time the SmartX Advanced Display is booted up the operator is presented of a choice to use  SmartXKiosk or TouchWiz as launcher. If SmartXKiosk then is selected instead of TouchWiz the operator will enter SmartXKiosk without having set a password first. Resolution Request an unlock code (PIN) from your local support center, which will enable the operator to exit Kiosk Mode. Press the Home (Hardware) Button at the SmartX Advanced Display. This will enable you to choose launcher again. Make sure that "TouchWiz" is selected. Note: In the next release this will note be an issue, since you are forced to select "TouchWiz" at first use to proceed (if SmartXKiosk is selected, you will be prompted to choose again)
View full article
Picard Product_Support
‎2018-09-06 07:29 AM

Labels:
  • EcoStruxure Building Operation
2436 Views

MPX firmware versions from the controller error log

Issue Converting the entries from an MPX controller error log can be useful when there has been a software revision change. Product Line EcoStruxure Building Operation Environment EBO MPX Cause There may be an entry in an MPX error log that shows as follows: 25 I 2018-07-02 10:07:36.56 0x00006409 0x20000015 0x80018a15 0x10000134 0x18061101 Software revision change Resolution The ability to extract the firmware revision numbers from the controller error log is useful especially if you do not have the device report. Take a look at the last 2 numbers of the following line: 25 I 2018-07-02 10:07:36.56 0x00006409 0x20000015 0x80018a15 0x10000134 0x18061101 Software revision change 0x10000134  == 1.00.01.00134  (please disregard the missing 01) 0x18061101 == 2018 06 11 (ignore the trailing 01 in the hex number)
View full article
Picard Product_Support
‎2018-09-06 07:28 AM

Labels:
  • EcoStruxure Building Operation
2106 Views

Issue creating Lon bindings

Issue Trying to create a Lon binding from two or more nvo's in one Lon device (hub) to two or more nvi's in many Lon devices (targets), a so-called fan-out binding. The binding between the first Lon devices works fine, but when trying to create the binding from the Hub Lon device to the second Lon device (target) it does not work. The binding window for the second Lon device (target) is opened; the Lon device (hub) is chosen in the browser window on the right side; and the nvo in the hub is dragged to the nvi in the second target device. But the binding tool will not accept this binding. It is not possible to release the nvo from the Hub Lon device on the nvi in the second target Lon device. Product Line EcoStruxure Building Operation Environment Building Operation Workstation LON Devices Cause Normally when creating a binding using the EBO binding tool you open the binding window for the target (receiver of the value). But in this particular case you need to do it the other way around and open the binding window for the hub (sender of the value) instead, and then drag the target to the hub. Read more about Fan-out Bindings in the Webhelp. Resolution Go to the Lon device with multiple ins or outs (hub) and open the bindings window In the browser window on the right side find the target Lon device Drag the nvi from the target device to the nvo in the hub Lon device
View full article
Janeway Jonas_Brissman Janeway
‎2019-03-22 07:07 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-05-20 07:22 AM

Labels:
  • EcoStruxure Building Operation
1793 Views

Downloading the MP-V Flow Balance Data Object properties to a controller

Issue Unable to download MP-V Flow Balance Data object to a controller using download all Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Multi-purpose VAV Cause The inability to use download all is a protection added to prevent overwriting any flow balance data inadvertently Resolution All Flow Balance Data Object properties are downloaded by explicitly downloading the Flow Balance Data Object as shown in the video below    
View full article
Commander JonGreen Commander
‎2019-03-27 10:43 AM

Last Updated: Guinan RandyDavis Guinan ‎2019-04-15 07:39 AM

Labels:
  • EcoStruxure Building Operation
2805 Views

Forcing BACnet I/O point using ES on another system causes WS to freeze

Issue Connecting to an ES that is on another machine through WorkStation and trying to force a BACnet input or output point located on a b3, connected to an AS-P, causes WorkStation to freeze. The only way to get out of freeze is by ending the system task in Windows.   Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server v2.0.2.x Building Operation Automation Server v2.0.2.x Building Operation Workstation v2.0.2.x Continuum b3xxx Controller any version Cause EBO v2.0.2.x has communication issues when connecting to an ES that is not on the machine you have WorkStation on.  Resolution Upgrading to 2.0.3.45 or later will resolve this
View full article
Commander JonGreen Commander
‎2019-04-11 07:59 AM

on ‎2019-04-11 07:59 AM

Labels:
  • EcoStruxure Building Operation
1975 Views

BACnet Object binding options using priorities

Issue How to bind BACnet Objects with Priority Levels Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation BACnet MPX, RPC, MPC Cause Servers (ES, AS) and other native devices (MPX, RPC) have slightly differing binding options. EcoStruxure Building Operation BACnet binding offers many options and the information below gives an example of how it can be achieved, it is not the only method. Resolution When binding between BACnet objects in EcoStruxure Building Operation (either external or within the device) it is usually better to utilize the BACnet Priority based control, often this facility is not fully exploited. Object Force and Overrides will use set priorities as in the BACnet Interface setting for the site (see System/Interface Manager/BACnet), the defaults are below. The example below shows a simple bind from a BACnet Schedule-value to a BACnet Binary-value Priority 16 (or other priority as required, as binding at Priority 16 can interfere with simple manual overrides). A BACnet datetime_value has no Priority array, so if you bind, for example, from a "BACnet Schedule Next transition" to "BACnet datetime_value Value" the bind to a Priority cannot be achieved, as below. In addition, the MPX & RPC have some constraints that Servers do not have. If you bind "Transfer Value to" an Object Value Property (rather than a Priority) then further bindings "Transfer Value to" binding to a Priority is inhibited. The screenshot below shows the error that is seen. This promotes using Priorities to control BACnet Objects.
View full article
Dave_Shore Schneider Alumni (Retired)
‎2019-04-04 06:53 AM

on ‎2019-04-04 06:53 AM

Labels:
  • EcoStruxure Building Operation
6128 Views

BACnet trend log properties missing after download to IP Controller

Issue When creating a BACnet trend log in an offline IP controller (e.g. an MP-C), the following properties are visible and can be adjusted: Delta Align intervals Interval offset Before download to the MP-C: After downloading to the MP-C these properties are not visible anymore. After download to the MP-C: Product Line EcoStruxure Building Operation Environment SmartX IP Controller Building Operation Workstation Cause Before downloading a “generic” object to a BACnet device, Workstation doesn’t know what BACnet properties the device supports and which it does not support. Therefore it will display the full super-set of BACnet properties for the given object type to the user. When the object has been downloaded, any property not supported by the device will be removed from the editor. Resolution This is by design.
View full article
Janeway Jonas_Brissman Janeway
‎2019-03-25 07:16 AM

Last Updated: Janeway PeterEdvik Janeway ‎2019-03-28 05:40 AM

Labels:
  • EcoStruxure Building Operation
1799 Views

WebReports displays a blank white screen instead of data

Issue When viewing WebReports within WorkStation or Internet Explorer the report data is not shown. All that is seen is a blank screen even though the menu items are still displayed (as shown in Figure 1 below). Figure 1:: Report viewed through WorkStation (Or Internet Explorer) When viewing the same WebReport through a different browser, Chrome or Firefox the report displays correctly Figure 2:: WebReport viewed using other Browsers (such as Chrome and Firefox) Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation WebReports EcoStruxure Building Operation WorkStation Cause The issue has only been seen with Internet Explorer since the other browsers appear to work. Since Building Operation WorkStation uses Internet Explorer as its internal browser, the problem is seen when displaying WebReports within WorkStation. To confirm that this is the issue you can check the Windows Event Log contents (Application Log Warnings) related to: <Provider Name="ASP.NET x.x.xxxxxxx.x" /> ... <Data>/LM/W3SVC/1/ROOT/SchneiderElectric/WebReports-1-131958191596842252</Data> <Data>Full</Data> <Data>/SchneiderElectric/WebReports</Data> <Data>C:\Program Files (x86)\Schneider Electric EcoStruxure\Building Operation WebReports\WebReports\</Data> <Data>CultureNotFoundException</Data> <Data>Culture is not supported. Parameter name: culture 4096 (0x1000) is an invalid culture identifier. at System.Globalization.CultureInfo.InitializeFromCultureId(Int32 culture, Boolean useUserOverride) at Microsoft.Reporting.WebForms.ReportDataOperation..ctor(IReportServerConnectionProvider connectionProvider, Boolean requiresFullReportLoad) at Microsoft.Reporting.WebForms.HttpHandler.GetHandler(String operationType, IReportServerConnectionProvider connectionProvider) at Microsoft.Reporting.WebForms.HttpHandler.ProcessRequest(HttpContext context) at System.Web.HttpApplication.CallHandlerExecutionStep.System.Web.HttpApplication.IExecutionStep.Execute() at System.Web.HttpApplication.ExecuteStepImpl(IExecutionStep step) at System.Web.HttpApplication.ExecuteStep(IExecutionStep step, Boolean& completedSynchronously)</Data> Resolution To correct this issue ensure that the Windows Regional Language, found in the Windows Control Panel matches between the Workstation PC and the Reports Server.
View full article
Picard RobertAndriolo Picard
‎2019-03-26 11:05 PM

Last Updated: Administrator CraigEl Administrator ‎2019-03-27 12:16 AM

Labels:
  • EcoStruxure Building Operation
1854 Views

TAC Vista Conversion Tool converts TAC Xenta I/O modules from LonWorks units to SlaveSpeak devices

Issue TAC Xenta I/O modules that are added as LonWorks units in TAC Vista, are converted to Xenta I/O modules belonging to a Xenta Base unit (SlaveSpeak devices) in EcoStruxure Building Operation, after conversion using TAC Vista Conversion Tool. Product Line EcoStruxure Building Operation, TAC Vista Environment Vista Server TAC Vista Conversion tool Xenta Xenta I/O-modules Cause In TAC Vista, the Xenta I/O modules are normally located on the same subnet as the Xenta Base unit, and belong to the Xenta Base unit, communicating as SlaveSpeak devices. If a Xenta I/O module is located on another subnet than the Xenta base unit, it could instead be added as a LonWorks Unit in Vista, and therefore communicating via LonWorks bindings to the Xenta base unit using SNVTs. Vista Conversion Tool does not handle this configuration. In the conversion tool, all Xenta I/O modules are expected to be connected directly to a Xenta base unit, located on the same Subnet, and are therefore always treated as SlaveSpeak devices. Resolution After running the Vista Conversion tool, you have to re-build the LonWorks Bindings between the Xenta I/O module and the Xenta Base unit manually in EBO, as the Conversion Tool does not handle the actual configuration setup.
View full article
Guinan MikaelKrantz Guinan
‎2019-03-22 06:21 AM

on ‎2019-03-22 06:21 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
2091 Views

Unwanted 'Pan and Zoom' on TGML Graphics when using Webstation

Issue When editing an EBO graphic in Webstation rather than Workstation, there is an inherent feature which allows a user to zoom in and out of the graphic using the mouse scroll. They can also pan around the page by holding down the left mouse button as they move. In many cases however, this feature is not wanted and makes the graphic more difficult to use. Image Zoomed Out  Image Zoomed In and Panned Right Product Line Building Operation Webstation Environment Graphics Cause Pan and Zoom in Webstation are features that are enabled by default in all TGML Graphics Resolution Edit the graphic object and select the top TGML root of the page properties. There is a 'Disable Pan and Zoom' option which by default is set to False.  Setting this option to True and then saving turns off the Pan and Zoom functions for that graphic
View full article
Admiral David_Kendrick Admiral
‎2019-02-06 02:48 AM

on ‎2019-02-06 02:48 AM

Labels:
  • EcoStruxure Building Operation
2905 Views

Error when trying to copy/paste objects from on MP-X device to another

Issue Copying objects from one MP-X device to another results in a validation error. "Property value '<object type>' already assigned"     Product Line MPx series EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Multi-purpose Controller Building Operation Multi-purpose VAV Cause The Object ID is already used within the destination device Resolution This functions as design. To resolve this:   Manually enter the Object ID when creating files that may be copied to other MP-X devices. One may choose to use blocks of IDs up to 64,999.   2. Utilize the import/export function within EBO which will import the BACnet objects using the next available Instance IDs.
View full article
Admiral StephenYang Admiral
‎2019-01-09 12:34 PM

Last Updated: Picard David_Purser Picard ‎2019-01-09 01:11 PM

Labels:
  • EcoStruxure Building Operation
2500 Views

Datasheet specifies contact rating as “Pilot Duty”

Issue The datasheet for DO-FA-12 says: Contact rating .......................250 VAC/30 VDC, 2 A, Pilot Duty (Power Factor 0.35) What does "Pilot Duty" mean? Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Bundled (AS-B) Building Operation IO-module Cause The datasheet specifies the rating class of the relays.  Understanding what "Pilot Duty" means is needed in order to know what load can be controlled by the relay. Resolution A "Pilot Duty" rating means that this relay is made for a specific highly inductive load, such as controlling the coil of another relay or contactor. Contacts with a "Pilot Duty" rating have passed standardized testing to prove they can reliably control a "Pilot Duty" load. In another example the datasheet of a device may say: Relay contact rating 250 VAC / 30 VDC, 2 A Pilot Duty (C300) In this case C300 indicates the rating of the relay, according to the UL 508 standard. The start current of a motor could damages the relays in case the current is too high. The start current could be up to 8 times the rated current, or more.
View full article
Guinan MikaelKrantz Guinan
‎2018-12-13 02:09 AM

Last Updated: Janeway PeterEdvik Janeway ‎2018-12-13 02:10 AM

Labels:
  • EcoStruxure Building Operation
6687 Views

Linux information on the Automation Server

Issue Information concerning Linux releases used within the Automation Server.   Product Line EcoStruxure Building Operation Environment Linux Operating System (OS) Building Operation Automation Server Building Operation Automation Server Premium Cause Questions concerning Linux releases used within the Automation Server. Resolution AS versions to 1.4.1 run Linux kernel 2.6.25.1 AS versions 1.5 to 2.0.2 run Linux kernel 3.0.101 AS-P versions 1.7 to 2.0.2 run Linux kernel 3.5.0-lsp-3.3.1 For questions concerning what type of Linux...i.e. Red Hat, Ubuntu, openSUSE - There is no linux distribution in the automation server just vanilla linux kernel. For further reading, download some documentation about the kernel from their website www.kernel.org  
View full article
Administrator CraigEl Administrator
‎2018-11-26 06:43 PM

Last Updated: Picard RobertAndriolo Picard ‎2018-11-26 06:57 PM

Labels:
  • EcoStruxure Building Operation
2730 Views

Changing the IP address of Automation Server

Issue How to change the IP address of the Automation Server and ensure proper communication. Product Line EcoStruxure Building Operation Environment Enterprise Server Automation Server Building Operation Device Administrator Building Operation Workstation Cause At times the IP address information for an Automation Server must be changed after being added to an Enterprise Server to accommodate changes in IP network design, correction of incorrect data, or any other reason. Changing the IP address needs to be done in the proper method to avoid artifacts and confusion after the change. Resolution To avoid complications, follow this process to modify the IP address of an Automation Server that is already communicating with an Enterprise Server. In the Building Operation Device Administrator connect the AS controller via USB or IP.  WebHelp Topic Connect to SmartX Servers Right-click on the AS and select Network Settings Modify the IP address settings to the new values Additionally, this can be changed through PuTTY with the "setip" command. Power Cycle the Automation Server (If a power cycle is not completed the AS will still have invalid data for network settings despite the physical network interface running with the new settings) Start Building Operation Workstation and log in to the Enterprise Server Select the Enterprise Server and open the Communication Tab Highlight the Automation Server that needs to be changed and modify the address field for the IP address of the device. (The Communications settings tab is enabled by selecting the Show/Hide tick icon). Click the Save button The Enterprise Server should now automatically establish communication with the AS, but if you want to speed this process you can right-click the Enterprise Server and select the "Advanced\Repair Server Communication" option. IMPORTANT: As of 1.41 if the IP address is changed on a server that is configured with a BACnet interface, the IP address and possibly the broadcast address of the IP Network under the BACnet interface must be updated manually. (see below)
View full article
Picard Product_Support
‎2018-09-10 11:32 PM

Last Updated: Picard RobertAndriolo Picard ‎2021-11-22 06:37 PM

Labels:
  • EcoStruxure Building Operation
7703 Views

Micronet BACnet (MNB) AV and BV objects in G3 are purple indicating they are overridden.

Issue Micronet BACnet (MNB) AV and BV objects in G3 are purple indicating they are overridden. The AV and BV objects are read only, how can they be overridden? Product Line TAC IA Series Environment Niagara G3 Micronet BACnet MNB-300 MNB-VAV MNB-1000 Cause Purple BACnet values (I/A Series R2 and G3 graphic override color) are internal BACnet points that can not be modified (display only). This behavior is normal and began to appear in MNB controller firmware versions 1.2 and higher. Per the BACnet specification, read-only type points must be set to indicate an override condition. The root cause is a design change required by the BACnet specification to bring the controllers into compliance for BTL certification. The ASHRAE BACnet Specification 135-2004 specifies that the "read-only" type objects (e.g. Analog Value, Binary Value, etc.) OVERRIDDEN flag is: Logical TRUE (1) if the point has been overridden by some mechanism local to the BACnet device. In this context "overridden" is taken to mean that the Present Value property is not changeable through BACnet services.In this case, the override is meant to indicate to Niagara that the point is locally overridden (by the controller) and cannot be changed by the Niagara BACnet service (or user).When the ENC learns the device it reads what "Protocol Services" it supports. If it supports COV then the "use COV" flag is set to true in the device object and when the proxy points are brought in they are defined as COV and once subscribed they will send their present value and status flag values to the ENC. In this case the AVM & BVM (being read only) objects will show overridden along with their value and be purple by default. Resolution All MNB devices support COV so the use COV property is set to true when they are discovered in the ENC.If the use COV property of the Device object is changed to false the ENC will use readPropertyMultiple (if supported in the device) to poll for data. If readPropertyMultiple is not supported in the device the ENC will read one property at a time. Now when the points are learned they will be defined as polled and when polled only the present value (PV) is requested (by default). Hence the AVM & BVM objects will show their value but not show overridden because their status flags are not known at the ENC. If the use COV device property is set to true after the AVM and BVM proxy points are defined in the ENC they will show overridden and purple after they are successfully subscribed. Turning the use COV property in the device to false at this point will cause these objects to be polled but their status is already known so they will continue to show overridden along with their present value. The only way to change that is to delete and re-learn them while the device use COV property is sent to false.
View full article
Picard Product_Support
‎2018-09-06 10:01 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-10-02 12:28 PM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
2613 Views
  • « Previous
    • 1
    • …
    • 93
    • 94
    • 95
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore