Forcing BACnet I/O point using ES on another system causes WS to freeze
  • Forcing BACnet I/O point using ES on another system causes WS to freeze
  • RandyDavis
    RandyDavis
  • JonGreen
    JonGreen
  • MikaelBodereau
    MikaelBodereau
Commander JonGreen Commander
‎2019-04-11 07:59 AM
on ‎2019-04-11 07:59 AM
Connecting to an ES that is on another machine through WorkStation and trying to force a BACnet input or output point located on a b3, connected to an AS-P, causes WorkStation to freeze. The only way to get out of freeze is by ending the system task in Windows.
  • Building Operation Enterprise Server v2.0.2.x
  • Building Operation Automation Server v2.0.2.x
  • Building Operation Workstation v2.0.2.x
  • Continuum b3xxx Controller any version
EBO v2.0.2.x has communication issues when connecting to an ES that is not on the machine you have WorkStation on.
Upgrading to 2.0.3.45 or later will resolve this