Issue
When creating a BACnet trend log in an offline IP controller (e.g. an MP-C), the following properties are visible and can be adjusted:
- Delta
- Align intervals
- Interval offset
Before download to the MP-C:
After downloading to the MP-C these properties are not visible anymore.
After download to the MP-C:
Product Line
EcoStruxure Building Operation
Environment
- SmartX IP Controller
- Building Operation Workstation
Cause
Before downloading a “generic” object to a BACnet device, Workstation doesn’t know what BACnet properties the device supports and which it does not support. Therefore it will display the full super-set of BACnet properties for the given object type to the user.
When the object has been downloaded, any property not supported by the device will be removed from the editor.
Resolution
This is by design.