BACnet trend log properties missing after download to IP Controller
  • BACnet trend log properties missing after download to IP Controller
  • Jonas_Brissman
    Jonas_Brissman
Janeway Jonas_Brissman Janeway
‎2019-03-25 07:16 AM
Last Updated: Janeway PeterEdvik Janeway ‎2019-03-28 05:40 AM
When creating a BACnet trend log in an offline IP controller (e.g. an MP-C), the following properties are visible and can be adjusted:
  • Delta
  • Align intervals
  • Interval offset
Before download to the MP-C:
After downloading to the MP-C these properties are not visible anymore.
After download to the MP-C:
  • SmartX IP Controller
  • Building Operation Workstation
Before downloading a “generic” object to a BACnet device, Workstation doesn’t know what BACnet properties the device supports and which it does not support. Therefore it will display the full super-set of BACnet properties for the given object type to the user.
When the object has been downloaded, any property not supported by the device will be removed from the editor.
This is by design.
  • JonasBrissman19
80% helpful (4/5)