Issue
Copying objects from one MP-X device to another results in a validation error. "Property value '<object type>' already assigned"
Product Line
- MPx series
- EcoStruxure Building Operation
Environment
- Building Operation Workstation
- Building Operation Multi-purpose Controller
- Building Operation Multi-purpose VAV
Cause
The Object ID is already used within the destination device
Resolution
This functions as design. To resolve this:
- Manually enter the Object ID when creating files that may be copied to other MP-X devices. One may choose to use blocks of IDs up to 64,999.