Error when trying to copy/paste objects from on MP-X device to another
  • Error when trying to copy/paste objects from on MP-X device to another
  • StephenYang
    StephenYang
  • David_Purser
    David_Purser
Admiral StephenYang Admiral
‎2019-01-09 12:34 PM
Last Updated: Picard David_Purser Picard ‎2019-01-09 01:11 PM
Copying objects from one MP-X device to another results in a validation error. "Property value '<object type>' already assigned"
  • MPx series
  • Building Operation Workstation
  • Building Operation Multi-purpose Controller
  • Building Operation Multi-purpose VAV
The Object ID is already used within the destination device
This functions as design. To resolve this:
  1. Manually enter the Object ID when creating files that may be copied to other MP-X devices. One may choose to use blocks of IDs up to 64,999.Manul ID SC.png
    2. Utilize the import/export function within EBO which will import the BACnet objects using the next available Instance IDs.
Tags (8)