MPX firmware versions from the controller error log
  • MPX firmware versions from the controller error log
  • Alan_Wood
    Alan_Wood
‎2018-09-06 07:28 AM
Converting the entries from an MPX controller error log can be useful when there has been a software revision change.
  • EBO
  • MPX
There may be an entry in an MPX error log that shows as follows:
25  I  2018-07-02 10:07:36.56  0x00006409  0x20000015  0x80018a15
0x10000134 0x18061101 Software revision change
The ability to extract the firmware revision numbers from the controller error log is useful especially if you do not have the device report.
Take a look at the last 2 numbers of the following line:
  • 0x10000134  == 1.00.01.00134  (please disregard the missing 01)
  • 0x18061101 == 2018 06 11 (ignore the trailing 01 in the hex number)
Tags (3)
  • 19913
  • DavidShore19
  • MPV MPC