Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

SpaceLogic IP devices IP address settings and BACnet hosting

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SpaceLogic IP devices IP address settings and BACnet hosting
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Dave_Shore
    Dave_Shore
  • Mahmoud_Sayed
    Mahmoud_Sayed
  • DavidChild
    DavidChild
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
21244 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SpaceLogic IP devices IP address settings and BACnet hosting

Dave_Shore Schneider Alumni (Retired)
‎2018-10-18 04:16 PM

Last Updated: Spock Mahmoud_Sayed Spock ‎2023-10-27 12:01 AM

Issue

Cannot change the IP address or host a SpaceLogic IP device, MP or RP controllers, or IP-IO modules in a second EBO Server.

Product Line

EcoStruxure Building Operation

Environment

  • IP address BACnet
  • Building Operation Multi-purpose Controller
  • Building Operation Multi-purpose VAV
  • Building Operation Room Controller 
  • Building Operation IP-IO
  • Building Commission Application

Cause

1. IP settings are saved (eg in Building Commission), but the IP address of the Controller does not change. (Option to change most settings is grayed out from Building Commission for hosted SpaceLogic IP devices)

2. The Controller is already hosted by an EBO server and cannot be hosted by a second EBO server, thus data objects cannot be read.

3. Rehosting an SpaceLogic IP device to a different EBO server

Resolution

1. Changing the IP address "settings" can be done with Building Commission application, formely know as eCommission Tool, in some earlier versions but if the SpaceLogic IP device, formely known as SmartX IP device, is already fully hosted by an EBO Server, then a warm start from the Building Commission is inhibited. (Option to change most settings is grayed out from Building Commission for hosted SpaceLogic IP devices)

eCT change IP.jpg

Without the hosting Server initiated warm start the new IP setting will not be used.

IP Commands Activate Changes.jpg

If the SpaceLogic IP device is not hosted then the IP address can be changed from the Building Commission, using the warm start option.

Notes

  • A local warm start initiated at the SpaceLogic IP device(manually with the reset button) will not force the SpaceLogic IP device to use these new settings.
  • See BACnet/IP Controller Commissioning Scenarios
  • The IP address of a Hosted SpaceLogic IP device cannot be modified from eCommission Tool
  • A factory reset will force the SpaceLogic IP device to return to AutoIP and DHCP, the BACnet Id will generally be retained see Automatic Association after a Factory Reset in a BACnet Controller or IO Module

2. When a SpaceLogic IP device is fully hosted by an EBO Server, it can be BACnet hosted by a second EBO Server, but this will only contain the standard BACnet Applications folder. This hosted BACnet Device needs to be manually created using the SpaceLogic IP device instance Id. 

Below, it can be seen that the fully hosted SpaceLogic IP device and the BACnet only hosting under ASP_22Fully Hosted and host.jpg

 

3. When a SpaceLogic IP device is configured or programmed via the hosting EBO Serving using WorkStation, some of the objects (eg. Scripts or Function Block) data is not fully contained within the SpaceLogic IP device. Thus if the hosting EBO server is changed, some of the configuration data will be lost and a simple upload to the new hosting EBO Server will not upload all the data required to recreated these objects.
In such a case, an export from the original hosting EBO Server should be imported into the new hosting EBO Server to ensure no data is lost.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (5)
  • Find more articles tagged with:
  • DavidShore19
  • DavidShore20
  • DavidShore21
  • MahmoudSayed23
  • MPC MPV
Was this article helpful? Yes No
91% helpful (10/11)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of