Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,845
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 330
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 33
    • 34
    • 35
    • …
    • 508
  • Next »

Enterprise Server or Enterprise Central will not start

Issue After installing or upgrading from EBO 2.0.x to EBO 3.x.x or EBO 4.0.x, the Enterprise Server or Enterprise Central will not start. When the "Start Service" button is pressed in the Building Operation Software Administrator the server status is stopped and does not change and no activity is seen in the system log area. Product Line EcoStruxure Building Operation Environment Enterprise Server Enterprise Central Cause The vcruntime140.dll file is missing from the Window’s system32 folder. Resolution The vcruntime140.dll file is installed as part of the Visual C++ Redistributable for Visual Studio 2015 installation. Visual C++ Redistributable for Visual Studio 2015 can be downloaded from the link below. https://www.microsoft.com/en-in/download/details.aspx?id=48145   If you have later versions Visual C++ Redistributable for example Visual C++ Redistributable for Visual Studio 2017, Visual Studio 2015, 2017, 2019, and 2022 can be used to save uninstalling version 2017. https://learn.microsoft.com/en-us/cpp/windows/latest-supported-vc-redist?view=msvc-170  
View full article
Gary Schneider Alumni (Retired)
‎2022-12-13 01:24 AM

Labels:
  • EcoStruxure Building Operation
2019 Views

Sending a text message (SMS) from an alarm

Issue Sending a text message (SMS) from an alarm Product Line Andover Continuum Environment Continuum CyberStation CX9900 CX9680 CX9640 Netcontroller Netcontroller II bCX4040 Cause There is no simple way of sending a text message (SMS) from Continuum to a mobile phone. Resolution The below are possible options to send an SMS message:-   Single output (Digital Output) to a GMS modem or auto dialer (single alarm). SMS PE Driver (output via RS232) to a 3rd party GSM modem for more complex alert text. Please see instructions and sample PE code. Send alarm email via outlook or exchange server to an email/SMS Gateway service  Send an email from bCX or NC2 to a email/SMS Gateway service.
View full article
Picard Product_Support
‎2018-09-10 04:52 AM

Last Updated: Sisko GavinHe Sisko ‎2023-06-09 06:47 AM

Labels:
  • Andover Continuum
2740 Views

Continuum error after activating a software license.

Issue When starting Continuum the following error is seen after successful activation of a software license (V2C file): “You have a key that has not been programmed for this version of the software. Please contact your Schneider Electric sales representative for an upgrade. Click OK to exit.”   Product Line Andover Continuum Environment Continuum CyberStation Software License Cause After replacing the CyberStation PC hard disk, the “Status information” was collected from the PC using the “RUSKeyUtility.exe”.  The V2C file was updated by the “Andover Update Service” team, and successfully activated on the PC. The V2C file included the finger print of the PC before the hard disk replacement. A check of the Gemalto Sentinel web page shows the “Secure Storage ID Mismatch” message in the Key Type column as below: Resolution The finger print needs to be cleared by applying a special V2C file. Obtain the most recent C2V file from the PC using the RUSKeyUtility.exe or the “Gemalto Sentinel web page”. Send the C2V file to support Support will supply the special V2C file  
View full article
Lieutenant | EcoXpert Master SangKim Lieutenant | EcoXpert Master
‎2023-06-08 06:11 PM

on ‎2023-06-08 06:11 PM

Labels:
  • Andover Continuum
1014 Views

SpaceLogic controllers MPx/RPx do not support 802.1x network authentication

Issue Do the SpaceLogic controllers MPx/RPx support network authentication via Radius Server (IEEE 802.1X)? Product Line EcoStruxure Building Operation Environment Building Operation Multi-purpose Controller Building Operation Room Controller Cause As noted in the AS supports network authentication via Radius Server (IEEE 802.1X) Knowledge Base article the Automation Servers (AS-P, AS-B) support the 802.1x protocol.   The SpaceLogic controllers MPx/RPx do not support it. Resolution Since the  SpaceLogic controllers MPx/RPx do not support 802.1x network authentication, alternative mechanisms must be provided to authenticate MPx/RPx controllers.   The SpaceLogic controllers MPx/RPx send a gratuitous ARP containing the device MAC address on start up and it is possible to use the MAC Authentication Bypass (MAB) option on the network switch. When MAB is configured on a port, that port will first try to check if the connected device is 802.1X compliant, and if no reaction is received from the connected device, it will try to authenticate with the AAA server using the connected device's MAC address as username and password. The network administrator then must make provisions on the RADIUS server to authenticate those MAC-addresses, either by adding them as regular users, or implementing additional logic to resolve them in a network inventory database. Many managed Ethernet switches offer options for this.  
View full article
Captain AbeMeran Captain
‎2023-06-07 07:21 PM

Labels:
  • EcoStruxure Building Operation
1079 Views

Fail to start SBO 1.8.x and 1.9.x servers in PCT v1.3.3.75

  Issue PCT v1.3.3.75 fail to start SmartX server in versions 1.8.x and 1.9.x Product Line EcoStruxure Building Operation Environment Building Operation Project Configuration Tool (PCT) Cause Defect, user can create SmartX server v1.8.x and 1.9.x but the servers can't start properly. Resolution Uninstall PCT v1.3.3.75 Install PCT v1.3.2.110 (Download), (Client Installer) Install server packages 1.8.x and 1.9.x
View full article
Admiral StephenYang Admiral
‎2023-06-08 10:11 AM

on ‎2023-06-08 10:11 AM

Labels:
  • EcoStruxure Building Operation
  • Project Configuration Tool
1833 Views

Mirroring SNVTs from multiple Lon Devices to Local Node

Issue Added multiple Lon devices to Lon Network and need to mirror SNVTs from more than one device to the Local Node Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium Building Operation Enterprise Server Cause Using SNVT bindings between devices and the Local Node of the EBO server allows LON communications bandwidth to be optimized by using the LonWorks protocol Send and Receive Heartbeats configured per device. However, it can be a time-consuming task to mirror SNVTs from multiple identical devices. This time can be reduced by selecting SNVTs in multiple devices using search. Resolution Create a new search Search for one SNVT that is available on multiple devices Use this article to create the mirrored SNVTs in the local node: Creating Network Variables Automatically Search for the next SNVT that is available on multiple devices Repeat until all desired SNVTs are mirrored. RECOMMENDATION: Save the searches for use later when adding more new devices.
View full article
Picard David_Purser Picard
‎2023-06-07 07:59 PM

Last Updated: Guinan RandyDavis Guinan ‎2023-06-08 09:44 AM

Labels:
  • EcoStruxure Building Operation
864 Views

Infinet and MSTP bus troubleshooting

Issue Troubleshooting steps for the Infinet and MSTP bus. Product Line Andover Continuum, EcoStruxure Building Operation Environment Continuum SmartStruxure RS-485 Infinet BACnet MSTP Cause Methods are needed to troubleshoot the Infinet and MSTP bus Resolution This is not a comprehensive list of all methods for troubleshooting, but a starting point. The Infinit-mstp troubleshooting document is available here. NOTE If BACnet MSTP devices do not support COV subscriptions, then care must be taken when reading values (eg EBO trends or alarms) as excessive traffic can be created that overwhelms the communication bus. For example, if 30 non-COV BACnet devices have EBO alarms (or EBO change of value trends) bound to 4 objects in each controller, this will create 240 packets (reads/replies) that will be attempted every "Minimum polling Interval". This is likely to fill the MSTP bus bandwidth  
View full article
Picard Product_Support
‎2018-09-10 12:30 AM

Last Updated: Dave_Shore Schneider Alumni (Retired) ‎2023-06-08 07:27 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
5397 Views

What are the sensor temperature vs resistance values of the TC range of thermostats.

Issue Resistance against temperature Product Line Field Devices Environment TC300 thermostat range TC900 thermostat range RS-03 remote sensor Cause Remote sensor compatibility Resolution The TC thermostat range use a 10K type 3 (3950) Negative Temperature Coefficient (NTC) thermistor. Whilst this is similar to the 10K type 3 thermistor used in the other BMS field device sensors such as the SpaceLogic SLA range, it has a different resistance curve and the temperature read will be different.   The table below shows that at typical room temperatures the error is 0.6°C or less. T(°C) RS-03 R(KΩ) SPA R(KΩ) Error % Error °C 0 31.77 29.575 6.91% 1.736 5 24.94 23.504 5.76% 1.366 10 19.68 18.809 4.43% 1.052 15 15.62 15.146 3.03% 0.812 20 12.47 12.271 1.60% 0.63 25 10 10 0.00% 0 30 8.064 8.195 -1.62% 0.3872 35 6.538 6.752 -3.27% 0.3052 40 5.327 5.592 -4.97% 0.2422 45 4.363 4.655 -6.69% 0.1928 50 3.592 3.893 -8.38% 0.1542   Click here to view the TC thermostat's RS-03 remote temperature against resistance chart. Click here to download the chart that provides the temperature against resistance reading for the TC thermostat's RS-03 remote temperature sensors.
View full article
Picard Product_Support
‎2018-09-11 07:51 AM

Last Updated: Administrator CraigEl Administrator ‎2023-06-08 12:06 AM

Labels:
  • Field Devices
2720 Views

Newly enrolled users are not being granted access at Suprema readers

Issue Newly enrolled users biometrics are not working at Suprema readers while existing users are functioning normally. New user updates appear to be working, the Download Server is online, with changes being made to the controller .dat and suprema reader .dat files in the Security Expert Servers ProgramData folder as users are updated. Controller .dat files Product Line EcoStruxure Security Expert Environment Security Expert Suprema Integration Cause The Suprema BioStar services are running on the Security Expert server which conflicts with the operation of the Security Expert Download service. Both the BioStar software and Security Expert Download service use the same port (51211) to communicate with the biometric readers. Resolution The Suprema BioStar software is only used during commissioning and configuration of the biometric readers and does not need to be permanently running. Due to the port conflict, the Suprema services cannot be run on the Security Expert server with the Security Expert Download service active. Stop all of the BioStar services running on the Security Expert server and set the startup type to manual. Suprema services Restart the Security Expert download service. Download service New user updates will now be downloaded to the Security Expert controllers and Suprema readers.
View full article
Kirk AdamSteele Kirk
‎2023-06-07 11:16 PM

on ‎2023-06-07 11:16 PM

Labels:
  • EcoStruxure Security Expert
2196 Views

The RUSKeyUtility displays a “Vendor lib cannot be found” error message.

Issue The RUSKeyUtility.exe displays a “Vendor lib cannot be found” error when applying license a V2C file to Cyberstation. Product Line Andover Continuum Environment Andover Continuum Cyberstation Software License Cause There are three main reasons for the error : The “C:\Program Files (x86)\Common Files\Aladdin Shared\HASP” folder path is not added to the Windows Path system variable. The folder path is added to the Windows Path system variable, but the “haspvlib_84344.dll” file does not exist in the “C:\Program Files (x86)\Common Files\Aladdin Shared\HASP” folder. The folder path is added to the Windows Path system variable, and the “haspvlib_84344.dll” file exists in the “C:\Program Files (x86)\Common Files\Aladdin Shared\HASP” folder, but the “haspvlib_84344.dll” file is damaged. Resolution Add the path to the  Windows Path system variable. Select the Advanced tab from Control Panel -> System -> Advanced system settings Click the Environment Variables button Highlight the Path Click the Edit button and add the C:\Program Files (x86)\Common Files\Aladdin Shared\HASP path Request the latest “haspvlib_84344.dll” file from Product Support and copy it to the folder. Request the latest “haspvlib_84344.dll” file from Product Support and copy it to the folder to replace the damaged one.  
View full article
Lieutenant | EcoXpert Master SangKim Lieutenant | EcoXpert Master
‎2023-06-07 07:40 PM

Last Updated: Administrator CraigEl Administrator ‎2023-06-07 07:42 PM

Labels:
  • Andover Continuum
1353 Views

AS supports network authentication via Radius Server (IEEE 802.1X)

Issue Does the Automation Server support network authentication via Radius Server (IEEE 802.1X)? Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Cause AS supports network authentication via Radius Server (IEEE 802.1X)? Resolution RADIUS and IEEE 802.1X are not the same thing, although they can be used together. Remote Authentication Dial In User Service (RADIUS) is a networking protocol that provides centralized Authentication, Authorization, and Accounting (AAA) management for computers to connect and use a network service. RADIUS is a client/server protocol that runs in the application layer, using UDP as transport.   The RADIUS server is usually a background process running on a UNIX or Microsoft Windows server. RADIUS serves three functions: to authenticate users or devices before granting them access to a network, to authorize those users or devices for certain network services and to account for usage of those services.  IEEE 802.1X is an IEEE Standard for port-based Network Access Control (PNAC). It is part of the IEEE 802.1 group of networking protocols. It provides an authentication mechanism to devices wishing to attach to a LAN or WLAN. It is a mechanism used in (mostly) switches and wireless access-points to allow or block devices to access the network (or granularly allow access to parts of it).   For example, if you have a network port in a meeting room, you can enable 802.1x on the switch port and configure it in such a way that when an employee connects they have access to the entire network, but if a guest connects (with a temporary password) they can only reach the Internet and if a passer-by is tempted to try his luck, they cannot access anything at all. Does IEEE 802.1X also use RADIUS as it's underlying authentication mechanism? Yes and no. IEEE 802.1x uses Extensible Authentication Protocol (EAP), the drawing below shows that for wired 802.1x: EAP over LAN (EAPoL) is used between the Supplicant (software on a computer) and the Authenticator (switch). EAP is then usually tunneled over Radius between the Authenticator and the Authentication Server, but it can also be done over Diameter (the successor to Radius). For wireless, it is similar in the sense that there is also no Radius between the supplicant and the authenticator, only between the authenticator and the Authentication Server (to tunnel the EAP). From EBO 2022 the AS-P and AS-B can be configured as supplicants on a network protected by IEEE 802.1X security. See the IEEE 802.1X Security Webhelp topic for further details.   Note: MPx/RPx do not support 802.1x network authentication, see the SpaceLogic controllers MPx/RPx do not support 802.1x network authentication Knowledge Base article  for further details.    
View full article
Picard Product_Support
‎2018-09-06 10:26 AM

Last Updated: Administrator CraigEl Administrator ‎2023-06-07 07:29 PM

Labels:
  • EcoStruxure Building Operation
2678 Views

Connection error between MSSQL and EBO using External log Storage

Issue Getting the connection error below when using Microsoft SQL server as External Log Storage for EBO. Error: [Microsoft][ODBC SQL Server Driver][TCP/IP Sockets] SSL Security error [Microsoft][ODBC SQL Server Driver][TCP/IP Sockets] ConnectionOpen (SECDoClientHandshake()). [Microsoft][ODBC Driver Manage     Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server (ES) Building Operation Enterprise Central (EC)   Cause When EBO connects to the Microsoft SQL server it uses the ODBC installed on the computer. It will use the ODBC version which comes with the OS and not the newest one installed on the computer. In this case that was too old to work with the Microsoft SQL server Resolution It is possible to specify what ODBC version EBO should use. First check what ODBC version is installed on the computer. Enter ODBC in the search bar on the computer Open ODBC Data sources and select the Drivers tab. Open EBO and navigate to the properties /External Log Storage/Microsoft SQL Server in the system tree. In the Database name field it is possible to specify which ODBC version EBO should use, see picture below
View full article
Janeway Jonas_Brissman Janeway
‎2023-06-07 07:04 PM

on ‎2023-06-07 07:04 PM

Labels:
  • EcoStruxure Building Operation
2235 Views

Ensuring Windows features are installed for Security Expert SOAP service

Issue SOAP service can't be reached at http://localhost:8030/SecurityExpertSOAPService/service.svc.  HTTP Error 404 error seen when attempting to browse. Product Line EcoStruxure Security Expert Environment Security Expert Server Cause Confusion related to the indicator Windows uses to denote when features have been enabled. Instructions in the Security Expert SOAP service installation manual not sufficiently clear. For instance, the documentation shows a checkmark in the .NET framework feature but it does not show the sub-items, a checkmark here means all of the sub-items are also enabled but this is not necessarily intuitive.  When not all of the sub-items are enabled, Windows shows the check box filled with a black square but many users are interpreting this as meaning the same as a checkmark. Resolution When a feature check box shows a checkmark in the documentation, make sure to expand the feature and enable ALL of its sub-items. 
View full article
Captain AbeMeran Captain
‎2021-02-04 06:36 AM

Last Updated: Kirk AdamSteele Kirk ‎2023-06-07 06:06 PM

Labels:
  • EcoStruxure Security Expert
2186 Views

MQTT - Mosquitto Broker Insecure Configuration

Issue MQTT client from an AS-P cannot establish communication with the Mosquitto broker installed on the machine that hosts the Enterprise Server (ES). At the same time, the MQTT client from the ES was online with the Mosquitto broker. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server IoT messaging MQTT (Messaging Queuing Telemetry Transport) Cause In version 1.6.x and earlier from the Mosquitto broker, the option - allow_anonymous [ true | false ] from the configuration setup (e.g. mosquitto.conf — the configuration file for mosquitto) of the broker was defaulted to  true  unless there were other security options set.   In recent versions of the broker, the option allow_anonymous defaults to  false - Unless no listeners are defined in the configuration file, in which case it set to  true  - but connections are only allowed from the local machine if external connections are required; specific port listeners need to be set. Resolution To configure the MQTT Mosquitto broker for insecure communication with an EBO server, follow these steps.  Download the Mosquitto broker latest version from the Eclipse website and install it on the host machine. Locate the mosquitto.conf file in the  Mosquitto installation folder (Default: C:\Program Files\mosquitto). Edit the mosquitto.conf file with a text editor application (e.g. Notepad, Notepad++). Setting up the  allow_anonymous configuration as true and the listeners to the desired communication ports (e.g. 1883: This is the default MQTT port. 1883 is defined at IANA as MQTT over TCP. 8883: This is the default MQTT port for MQTT over TLS.)   Check the Video attached, which includes the basic configuration of the mosquitto.conf file.   
View full article
Commander Hernan_Urueña Commander
‎2022-09-28 08:42 PM

Labels:
  • EcoStruxure Building Operation
2749 Views

Number of wires in a RP-C terminal

Warning Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source. Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices. Issue Page 1031 of the hardware reference guide only states wire cross-sectional area: 0.34 to 2.5 mm 2 (22 to 14 AWG) and not the number of wires allowed to terminate. Product Line EcoStruxure Building Operation Environment Building Operation Room Controller (RPC) 24V Building Operation Room Controller (RPC) 230V Cause Documentation clarification. Resolution It is OK to terminate up to 2 wires into each terminal as long as the total area of the wires does not exceed 2.5mm 2 .  
View full article
Gary Schneider Alumni (Retired)
‎2023-06-06 02:44 AM

on ‎2023-06-06 02:44 AM

Labels:
  • EcoStruxure Building Operation
967 Views

Model and Device Name from SLP sensor via Modbus RTU

Issue Model and Device Name from SLP sensor via Modbus RTU Product Line EcoStruxure Building Operation Environment Automation Server AS, ASP, ASB SpaceLogic Sensor SLP Cause The Model, Device Name and Serial number are 64bit values and need to be collected with a single query to get the correct data. Script and Function Block programs can not manipulate 64 bit values - Model Register 9, 64bit, read only, Read Function Code 4 - Serial number Register 42, 64bit, read only, Read Function Code 4 - Device Name Register 7, 64bit, read/write, Read Function Code 3 (currently the documentation shows these as 32bit) Resolution A simple way to collect the Model and Serial Number is shown below This involves creating a Modbus Poll Group for the 4x 16bit parts of the 64bit Modbus Register. This will effectively query the 4 registers in a single packet, ensuring the correct data is collected. The same method can be used to collect the Device Name, but this value cannot be written using the same Group, as block/group write is not supported in EBO Create a Modbus Poll group containing the four 16bit registers, then create a String variable Then create a script to convert to ASCII characters
View full article
Dave_Shore Schneider Alumni (Retired)
‎2023-03-02 07:06 AM

Labels:
  • EcoStruxure Building Operation
1256 Views

Upgrading SQL Express to a paid Edition of SQL for EcoStruxure Reports Server

Issue Upgrading SQL Express to a paid Edition of SQL for EcoStruxure Reports Server Product Line EcoStruxure Building Operation Environment WebReports Reports Server SQL Express Cause SQL Express 2008 R2 (for example) is limited to 10 Gb of Storage and 1 Gb of Ram usage. Many sites need a larger, more robust database than this allows. Resolution NOTICE: Before beginning, it is important to understand the difference between the Instance name and the version of SQL running.  The default instance name used in the the SQL Express version of SQL is SQLEXPRESS. This can be changed to anything during installation, but cannot be changed later.  This means that when upgrading to SQL Enterprise edition, the SQL instance name will still need to be SQLEXPRESS. The instruction below assumes the instance name is SQLEXPRESS and will be typed in that manner.   Perform a full backup of the Enterprise Server and Reports Server before beginning any upgrade process. Save these files to an external drive. Purchase a supported edition of SQL for the revision of EcoStruxure Building Operation WebReports being used. Please check the data sheet for the release to obtain this information. Open the Command Prompt and Browse to the location of the installation files for SQL. This should be the folder containing the setup.exe file for the new version of SQL Enter the Command "setup /ACTION=editionupgrade /INSTANCENAME=SQLEXPRESS /PID=XXXXX-XXXXX-XXXXX-XXXXX" NOTE:If  not using the default instance name, enter the correct instance name in place of SQLEXPRESS. PID is the product ID that came with the installation media. In some cases, this will be left out of the command string and entered later. (setup /ACTION=editionupgrade /INSTANCENAME=SQLEXPRESS) The SQL Installer will open. After the Setup Support Rules operation runs, click OK Click Next Verify the Product Key and click Next. Accept the License Agreement and click Next Ensure that the correct instance of SQL is selected and click Next. After the Edition Upgrade Rules runs, click Next Review the Upgrade Summary and click Upgrade When Complete click Close Open the SQL Server Configuration Manager using the start menu and verify that the SQL Server (SQLEXPRESS) service is running and that the SQL Server Reporting Services service is running. If either are stopped, right click and select the start option. Verify the upgrade is successful by opening a Web Browser and entering the URL "http://localhost/Reports_SQLEXPRESS" It should now be possible to see the option to directly edit reports in Report Builder. Log into the WebReports Interface. Notice that the initial report showing Database usage no longer runs.
View full article
Picard Product_Support
‎2018-09-11 01:35 PM

Last Updated: Sisko GavinHe Sisko ‎2023-06-06 12:11 AM

Labels:
  • EcoStruxure Building Operation
2859 Views

Suprema integration using CARD + BIOMETRIC credentials at the Suprema reader

Issue Using CARD + BIOMETRIC credentials at an integrated Suprema reader for user access. Product Line EcoStruxure Security Expert Environment Security Expert Suprema Biometric Reader Cause Security Expert does not support CARD + BIOMETRIC credentials being read at the integrated Suprema reader. Only BIOMETRIC credentials are supported to be read at the Suprema reader. Resolution For situations where CARD and BIOMETRIC credentials are required to authenticate users a supported solution is to install a Security Expert reader in conjunction with a Suprema reader at the door. The Security Expert reader will read the Security Expert Mifare/DESFire tags, compare this to the credentials configured in Security Expert user and then wait for the proper biometric to be provided before allowing access through the door.
View full article
Kirk AdamSteele Kirk
‎2023-06-05 10:39 PM

on ‎2023-06-05 10:39 PM

Labels:
  • EcoStruxure Security Expert
1762 Views

Continuum BACNet MSTP devices (b3 controllers) not showing up in BACNet View.

Issue The Continuum BACNet MSTP devices (b3 controllers) are created and do not appear in the BACNet View of the Continuum Explorer when the "Find New BACNet Devices" is performed.  In rare cases, they are all showing online in Infinity View and stay stable but some of them are not showing in BACNet View at all.  Product Line Andover Continuum Environment Continuum Explorer BACNet MSTP devices (b3 controllers) Cause Most of this issue happens when these BACNet objects are left over in the Continuum database due to an incomplete/unsuccessful delete operation on the BACnet devices that previously existed in the database.  Resolution When this happens, deleting all the objects from BACNet view from Continuum Explorer and redo the "Find New BACNet Devices" will fix it most of the time.  If the issue persists, it is necessary to run the "ACCTrace.exe" utility located in the Continuum directory of the workstation to start a capture.  Wireshark will also need to be run at the same time whilst completing a  "Find New BACNet Devices" again.  Wait for about 5 minutes then stop the ACCTrace and Wireshark captures and save the log files.  Send the log files to Product Support with a Continuum Analyzer log file and the names of the issued MSTP devices which are not showing in the BACNet View. SQL Enterprise Manager will need to be available to fix the issue in the database.
View full article
Picard Product_Support
‎2018-09-06 02:59 PM

Last Updated: Sisko GavinHe Sisko ‎2023-06-05 03:27 AM

Labels:
  • Andover Continuum
2568 Views

Configuring controllers for Access Control using SystemStatus and AccessServer system variables.

Issue Understanding and configuring controllers for Access Control using SystemStatus and AccessServer system variables. Product Line Andover Continuum Environment Access Control CX9702 ACX57xx Netcontroller Netcontroller II Cause Operators can be unsure what the various values for SystemStatus and AccessServer are and what they need to be set to for successful access control. Resolution 1. SystemStatus The first thing to realize is that there are four different modes that an Access controller can be set to, the SystemStatus indicates the mode controller is currently in. This is an Access-only system variable and will default to NoDatabase if left unconfigured. These four values are as follows: Normal — The controller is working normally. NoComm — Local controller has lost communications to the Workstations configured as Primary and Secondary Access Servers. NoDatabase — The Access server and the local controller have been reset or have otherwise lost connection to the database to check access card numbers and personal identification numbers (PINs). Can also indicate that the local controller has lost comms to the Access Server and has no local personnel database to authenticate to. ColdStart — Indicates the Access Controller SystemStatus initial value, before any door has been configured. The sequence for how SystemStatus gets set is as follows: On a ColdStart if the AccessServer = 1-190 it is set to NoDatabase when the first door is configured. When CyberStation finishes the personnel distribution, it explicitly sets the value to Normal.  On a ColdStart if the AccessServer  > 190 it is set to Normal when the first door is configured and the controller is communicating with the Primary and/or Secondary Access Server workstations. Note: Upon initial configuration, or a restart, the CyberStation can fail to set the SystemStatus to Normal; leaving the controller in NoDatabase mode. If this occurs, the value can be manually set to Normal to "kick start" the controller. 2. AccessServer The second thing to look at is that the value of the AccessServer SystemVariable has been set. This should be set to the ACC Net Id of the Workstation configured as the Primary Access Server (> 190) for local then remote validation or set to the controllers ACC Net Id for local validation only. 3. Door Object Additionally Door objects need to be configured to handle the above conditions, there are a number of ways they can require authentication when a card is presented, these are listed in the Entry Reader and Exit Reader tabs of the Door object in the form of check boxes. The main ones being validate site, validate card, valid pin, and Door Forced Lock Schedule. Tick whatever options are required.
View full article
Picard Product_Support
‎2018-09-10 11:27 PM

Last Updated: Sisko GavinHe Sisko ‎2023-06-05 03:12 AM

Labels:
  • Andover Continuum
2450 Views
  • « Previous
    • 1
    • …
    • 33
    • 34
    • 35
    • …
    • 508
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of