Active Event View comes up blank.
  • Active Event View comes up blank.
‎2018-09-10 11:50 PM
Last Updated: Crewman ContentModerator ‎2025-09-01 03:37 AM
Active Event Viewer contents and column headers are blank.
Andover Continuum
CyberStation
Warning
Windows registry corruption.
Method #1
Close Continuum and use Windows System Restore to put the system back at a point where the Event Viewer were fine.
Method #2
NOTE: Any customization previously done to the event viewers such as column name changes etc  will be lost when this method is used
  1. Shut down CyberStation then backup the Windows registry as a precaution
  2. Edit the Windows registry and delete HKEY_CURRENT_USER\Software\Andover Controls\Continuum\Access Event View
  3. Start CyberStation and open the event viewer which recreates the entry in the registry using default values.
Tags (2)