Graphics update slow and open objects slow even failed
  • Graphics update slow and open objects slow even failed
  • GavinHe
    GavinHe
  • YangboLIU
    YangboLIU
‎2018-09-06 09:14 AM
Last Updated: Sisko GavinHe Sisko ‎2024-09-26 03:27 AM
  1. Graphics updates are very slow, it takes over 1 minutes to load a graphic,
  2. Opening objects from Continuum Explorer is slow, sometimes it will failed to open an object if clicked too frequently.
  3. When using the BACnet path for objects on graphics it is fast.
Andover Continuum
  • b4920 version 4.2000026
  • b3s version 4.5000035
  • Cyberstation 1.81 or above
  1. For the old BACnet IP controller b4920, versions prior to 4.200029 could have some communication issue with b3s
  2. MSTP enhance mode not enabled on b4920,
  1. Upgrade b4920 to version 4.2000029 or above, preferably the latest version
  2. Go to the webpage of b4920, check "MSTP Enhance Mode" and then click submit
  3. Wait for b4920 to go back online and test graphics operation