When Continuum Explorer is launched it takes a very long time to update.
Andover Continuum
  • CyberStation
  • WebClient
When Continuum Explorer is launched it must populate all objects that reside at the root.  When there are a very large number of Personnel objects or other object types in the root, Continuum Explorer will be slow or unresponsive until this population process is complete.
  • Create a Folder under the Root of Continuum Explorer and move personnel objects to this folder.
  • Consider doing this to other objects that exist in large numbers.