Screen Brightness Issue on White TRCs

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Screen Brightness Issue on White TRCs
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • StephenYang
    StephenYang

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1168 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Screen Brightness Issue on White TRCs

Admiral StephenYang Admiral
‎2024-09-10 11:23 AM

Last Updated: Administrator CraigEl Administrator ‎2024-09-10 07:04 PM

Issue

The first batch of White TRCs (produced in 24H1) could appear too bright in some low-light level situations. All future batches (post 24H1) do not have the issue. See the precise list of affected serial numbers in the appendix section below.

Product Line

EcoStruxure Building Operation

Environment

SpaceLogic Touchscreen Room Controller

Cause

The housing color is set in the device’s manufacturing configuration to tell it what color the screen bezel is (black or white). White TRCs produced with an incorrect housing color will read a higher value for light level. This has a direct impact on the backlight dimming levels, and the only effect will be the screen staying brighter in dark rooms.

Resolution

Customers experiencing brightness issues may simply adjust the backlight brightness parameters to a lower value, which are configurable in the TRC configuration screens and via BACnet/Modbus. This would reduce the overall brightness of the devices immediately, without fixing the housing color. We recommend going with a permanent fix, by setting the housing color via the USB port. The steps to fix this permanently would be:

  • Connect USB-C cable to TRC
  • Log in as an administrator into the TRC’s configuration screens (to enable USB connection)
  • Open a terminal app like hyperterm or putty, with settings:
    • Speed (baud): 115200bps
    • Data bits: 8
    • Stop bits: 1
    • Parity: None
  • Paste in the command: #001000061009FE00009C!
    • Device responds: #000E00071009FE0051!
  • To confirm or test, paste in the command: #000C00001009FEE8!
    • Device responds:
      • White housing: #001200011009FE000000F9!
      • Black housing: #001200011009FE000001FA!

Examples

Below is an example of 4 white TRCs:

  • The two (2) outermost devices are too bright (leftmost and rightmost white TRCs).
  • The two (2) devices in the middle have been corrected to show adequate brightness.
StephenYang_0-1725992144642.png

Appendix

Since the Touch Room Controller’s serial number includes the date code, knowing whether a unit is impacted is very straightforward.
  1. Follow these instructions to determine if the unit of interest is impacted:
    Retrieve the serial number from the unit you suspect has the incorrect housing color.
    1. Example: FL24075TRC00002
  2. Examine the serial number date code, wrapped between the “FL” and “TRC” substrings.
    1. Example: 24075
  3. Decrypt the date code, using this logic:
    1. 24: year 2024
    2. 07: week 07 of 2024
    3. 5: day 5 of week 7 of 2024
  4. If the date code is between the values 24074 and 24285, the product is impacted. Products outside of this date code range are not impacted, and no fix to housing color will be needed.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • StephenYang24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.