Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Configure and test RP controller web service

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Configure and test RP controller web service
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PeterEdvik
    PeterEdvik
  • Mahmoud_Sayed
    Mahmoud_Sayed

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3701 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configure and test RP controller web service

Kirk Mahmoud_Sayed Kirk
‎2022-10-05 03:59 AM

Last Updated: Administrator CraigEl Administrator ‎2024-09-18 05:21 PM

Issue

How to configure and test RP controller web service

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Room Controller (RPC) 24 V
  • Building Operation Room Controller (RPC) 230 V

Cause

In the RP application, a REST (Representational State Transfer) Web Service API is available to facilitate secure HTTPS communications and allow you to obtain BACnet objects and properties from the controller.

Resolution

The following video will illustrate how to:

  • Use the SpaceLogic certificate configuration tool to configure keys and certificates in the RP controller.
  • Configure RP controller Web Service settings.
  • Use SoapUI to test RP controller Web Service.

Things you need:

  • Software

    • EBO 2022 or later server (Enterprise Server, AS-P or AS-B) and WorkStation.

    • SpaceLogic RP controller, RP-C Advanced, RP-C Pro, RP-C Pro Plus and RP-V Advanced, with firmware V4.00.01 or later.

    • SpaceLogic Certificate Configuration Tool, available from Exchange.

  • Tools

    • SoapUI (to be used for testing)

For more information and how to generate certificates, please check RP Controller | Developer Portal.

Note:

  1. Before configuring the Web Services in RP controller, make sure that there no pending IP changes, by checking "Changes pending" property in IP Network Settings Properties – Basic Tab. If "Changes pending" is true, click Activate changes in the IP commands menu, as explained in Configuring BACnet/IP Controller IP Network Settings
  2. For EcoStruxure Building Operation version 4.0.3 or later, a new EBO Workstation command named Export device identifying information is available. It is found in the main context menu of SpaceLogic RP Series controllers and allows the user to save an xml file that can later be imported into the SpaceLogic Certificate Configuration Tool to aid in the efficient configuration of SpaceLogic controllers within the tool. The user may select one or more RP Series controllers when executing the command. Refer to: Exporting Device Information to the SpaceLogic Certificate Configuration Tool

[video]

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • MahmoudSayed22
  • MahmoudSayed23
  • MahmoudSayed24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore