Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Setup External Log Storage using MSSQL

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Setup External Log Storage using MSSQL
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PeterEdvik
    PeterEdvik
  • Jonas_Brissman
    Jonas_Brissman
  • GavinHe
    GavinHe
  • Mahmoud_Sayed
    Mahmoud_Sayed

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
3 Likes
8674 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Setup External Log Storage using MSSQL

Janeway Jonas_Brissman Janeway
‎2023-03-02 05:58 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2024-10-11 05:47 AM

Issue

How to setup and configure External Log Storage in EcoStruxure Building Operation (EBO) when using Microsoft SQL Server as external log storage.

Product Line

EcoStruxure Building Operation

Environment

    Building Operation Automation Server Premium (AS-P)
  • Building Operation Enterprise Server
  • Building Operation Enterprise Central

Cause

You use External Log Storage feature to store historical data from EcoStruxure BMS. The amount of stored data is limited only by the equipment you use, and not by the capacities of the feature.

The External Log Storage feature uses an external database administered by either a combination of TimescaleDB and PostgreSQL software, or Microsoft SQL server.

Resolution

Please see the below video demonstrating how to:

  • Create a database and user account in Microsoft SQL (MSSQL) Server using Microsoft Server Management Studio.
  • Configure the External Log storage connection between EBO and MSSQL server in EBO.

Also please note the following:

  • In the video the "Host address" in EBO is set to the IP address or DNS name\SQLserver instance like this: localhost\SQLEXPRESS. If the SQL server is not located on the same computer as the EBO server only use the IP address or DNS name and no instance on "Host address".
  • The video demonstrates using the version 5 script when configuring the database in the MSSQL server, search External Log Storage - MSSQL Installation Script  to download the appropriate EBO version script.
  • For the example query to manage user permissions download User Rights Script or see attached script.txt.
  • If using MSSQL Express rather than the full MSSQL version it may be necessary to consult External log storage not working with SQL Server Express.

 

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
Tags (3)
  • Find more articles tagged with:
  • GavinHeward24
  • JonasBrissman23
  • MahmoudSayed24
Was this article helpful? Yes No
82% helpful (9/11)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore