Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,854
  • TAC IA Series 1,826
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 48
    • 49
    • 50
    • …
    • 509
  • Next »

Advanced Display v3 (AD v3) displays Website Not Available

  Issue Cannot communicate to an ADV3 connected to the USB port of an AS-P or AS-B. The error message “Website not available” is displayed. Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Advanced Display v3 (AD v3) Cause The AS-P or AS-B’s USB port uses a IP network connection to the ADV3 that defaults to 192.168.42.116. If the AS-P’s primary port is in the same range, for example the main LAN network range is 192.168.42.* there is a conflict with the USB IP network. Resolution Change the sites main LAN, which the AS-P or AS-B primary port connects too, to another network range.
View full article
Gary Schneider Alumni (Retired)
‎2023-09-08 03:36 AM

on ‎2023-09-08 03:36 AM

Labels:
  • EcoStruxure Building Operation
2942 Views

Cannot clear Semantic DB default admin password alarm when Enterprise Server added to Enterprise Central

Issue On a system requiring Semantics after adding Enterprise Servers to an Enterprise Central alarms are generated that cannot be cleared.  Changing the password for the Servers does not fix the issue. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Central Building Operation Enterprise Server Building Operation Workstation Cause Incorrect method used when setting up Semantics during installation, Semantics were enabled on the Enterprise Server as well as the Enterprise Central.  After adding to the Enterprise Central the Enterprise Server points to a different address where the alarm is for the original Enterprise Server address.   Resolution On the Enterprise Server the alarm needs to be verified against the original connection, this involves removing the lead object link and changing the settings to look at the original Semantic Database.   On the Enterprise Server Semantic Settings remove the lead object entry pointing to the Enterprise Central.  Open the Services Manager and Stop and Re-Start the GraphDB service, if stopped start it. Additionally, Stop and Start the Enterprise Server service, this can also be done in the Services manager using Software Administrator to stop and start will show any errors if evident. Log back into the Enterprise Server and the password alarm should be cleared, this may take a minute or so but not any longer.  This is only if the password has been changed, please see Semantic DB authentication failure" alarm. Also, in the EC the password alarm should have cleared. Once the alarm is cleared the GraphDB service can be disabled from within services as it is not required. Re-instate the lead object entry pointing to the Enterprise Central that was initially removed. For more information on Semantics please see Semantic Overview
View full article
Sisko GavinHe Sisko
‎2023-09-07 07:57 PM

on ‎2023-09-07 07:57 PM

Labels:
  • EcoStruxure Building Operation
3404 Views

Access Expert User Group Permissions 'Password is incorrect' Error

  Issue After adding a new group with limited permissions to a User, the User cannot change their password or Login to the Instance. The Error 'Password is incorrect' is displayed When trying to change the password the dialog box may flash, but not continue. If you click the Ok button again, it will show the 'Password is incorrect' box. Product Line EcoStruxure Access Expert Environment Access Expert Hosted V3 Cause A User Group with restricted access to specific objects didn't have permissions to the Instance object Resolution Add permissions to the User Group If 'All Types' are a part of a UserGroup then the 'Instance' object is included. However, if specific object permissions are selected for the User Group then the 'Instance' Read permission must be added at a minimum for the User to have access to the Instance. If the User is required to change their password then they will also need Publish permissions. Original Changed
View full article
Admiral Alan_Wood Admiral
‎2023-09-07 07:54 PM

on ‎2023-09-07 07:54 PM

Labels:
  • EcoStruxure Access Expert
1397 Views

I/A Series Niagara 4 Hardening Guide - Tips to Secure an I/A Series Niagara 4 System

Issue Procedures and processes to secure I/A Series Niagara 4 Systems Product Line TAC IA Series Environment  I/A Series Niagara 4 Systems Cause Users accessing system without permission Potential damage done by malicious entry to the system Resolution The attached document describes how to implement security best practices in an I/A Series Niagara 4 system.  While it is impossible to make any system completely impenetrable, there are many ways to build up a system that is more resistant to attacks. In particular, this document describes how you can help make an I/A Series Niagara 4 system more secure by carefully configuring and using: Passwords System Passphrase Platform Account Management Station Account Management Role and Permission Management Authentication TLS and Certificate Management Module Installation Additional Settings External Factors Please note that while all of these steps should be taken to protect your I/A Series Niagara 4 system, they do not constitute a magic formula. Many factors affecting security and vulnerabilities in one area can affect security in another; it doesn’t mean much to configure a system expertly if your JACE is left physically unsecured where anyone can access it. Note: Schneider Electric strongly recommends upgrading to the latest I/A Series N4 version maintenance build that implements numerous security updates.  Before updating any system, make sure to review the build-included documentation to understand the behavioral impacts of the security enhancements and JACE hardware platforms supported. Download the Niagara 4 Hardening Guide_2023 for more details.
View full article
Lt. Commander WaynePeters Lt. Commander
‎2019-01-31 01:19 PM

Last Updated: Guinan RandyDavis Guinan ‎2023-09-07 12:14 PM

Labels:
  • TAC IA Series
6069 Views

MNB-1000 BACnet MS/TP communications does not auto-baud

Issue MNB-1000 BACnet MS/TP communications do not auto-baud (synchronize). Product Line TAC IA Series Environment I/A Series MNB-1000 Firmware 1.2 and above Cause I/A Series MNB controllers with firmware 1.2 and above support baud rate synchronization (auto-baud) for BACnet MS/TP communications. This auto-baud feature is available if the device is configured for BACnet MS/TP communications only.  If the MNB-1000 BACnet Ethernet (or BACnet IP) communications are enabled, even though this is not being used in normal operation, it will cause the auto-baud to be disabled. Resolution 1. Disable the BACnet Ethernet (or BACnet IP) communications on the MNB-1000. Use a compatible RS-232 to RS-485 converter or the Roam IA to access the MNB-1000 via BACnet MS/TP communications. 2. Set the baud rate of the MNB-1000 MS/TP port to a fixed speed that matches the configured baud rate of the RS-485 port of the Jace. - Connect to the MNB-1000 using the WorkPlace Commissioning Tool. - Go to the MNB-1000 device properties, MS/TP tab, and set the baud rate of the MNB-1000 MS/TP port. See the example below.
View full article
Picard Product_Support
‎2018-09-10 11:01 PM

Last Updated: Guinan RandyDavis Guinan ‎2023-09-06 09:48 AM

Labels:
  • TAC IA Series
1718 Views

No Individuals Displayed in Editor

Issue Opened the Individuals Editor, and nothing is listed in there. The Individual list editor is blank Product Line TAC INET Environment All versions of I/Net Seven Cause The Option Selection was used and not reverted back to the original setting that allows all individuals to show in this Editor. Resolution Open the Individuals Editor by selecting Edit>Access>Individuals. If there is more than one Tenant, select a valid Tenant.  Avoid selecting the All Tenant option. Select the Options button at the bottom of the Editor. In the Display field, from the drop-down, select Individual. In the options for all the fields, ensure it has an asterisk (*) and not a name or anything else. Click on the OK button, and now all the individuals for that Tenant will be displayed.
View full article
Picard Product_Support
‎2018-09-06 01:29 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2023-09-04 06:48 PM

Labels:
  • TAC INET
1404 Views

Clean db for Enterprise Server or Enterprise Central

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue How does one get a clean database for the Enterprise Server or Enterprise Central? Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Cause Need for clean database either for testing or start from scratch.  Resolution Stop Enterprise Server or Enterprise Central using Software Administrator Go to the location of your database using Windows Explorer. In EBO V3.2 or higher, software administrator has a shortcut button for the databse folder. For this example it is C:/ProgramData/Schneider Electric EcoStruxure/Building Operation 2.0/Enterprise Server/db Delete the following folders if (some might not exist): Configuration, Historical, Persistent, System, UDT Start Enteprise Server or Enterprise Central using Software Administrator, the system will create a new folders and files as needed. Note: Restoring a different database over the current database does not require the clean database state. Using the backup and restore procedure allows you to switch databases.
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2023-08-28 01:51 AM

Labels:
  • EcoStruxure Building Operation
3121 Views

How to perform the online activation of an embedded license at EBO 2022

Issue Users may want to know how to perform the online activation of an embedded license  Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium (AS-P) Building Operation Automation Server Bundled (AS-B) Cause From Building Operation 2022, the Automation Server (Classic/Secure boot AS-B or AS-P) and features like Smart Drivers, SNMP notifications, Personalized dashboards, TimescaleDB, MQTT Publish/Subscribe, Modbus, Serial MS/TP, ES Connection, Server I/O, Field Devices, SAML Authentication, Zoning, and BACnet IP require a license. Customers need to know how to activate their embedded licenses to enable these features. Resolution This video will demonstrate how to Find the list of supported features by each activation ID. Activate an embedded license on an Automation Server Verify the embedded license status via the Device Administrator, Workstation, and the Flexnet operation license portal. Notes Check each activation ID's supported features using the part number or license description through the Features and Licensed Products Table.  The Flexnet operation license portal is a public FlexNet Login (flexnetoperations.com) accessible from anywhere with an Internet connection.  The Automation Server and the PC running the Device Administrator must have outbound connectivity to the license activation server over the Internet. Check the resolution section of this article Could not establish contact with License Server using SmartX Server - Communities to verify if the Automation Server has access to the Flexnet license activation server. For troubleshooting, refer to Embedded license activation fails. Web helps:  Assigning Licenses and Activating Licenses Online. An Embedded DEMO license is available for temporary use during project engineering and installation until you know each device's specific licensing needs. Please visit How to activate a demo license on an Automation Server at EBO 2022. If the Automation Server does not have access to the Flexnet license activation server (no Internet connection), you can perform the steps in the following article Offline activation of embedded licenses.  Please take note that starting from Building Operation 2023 version 5.0.3 and higher, Automation Servers are no longer required to be connected to the Internet. The Device Administrator can access the internet and manage communication and license activation for the 'offline' Automation Servers.   A shorter version of the Online Activation of Embedded Licenses for Automation Servers-Digital Job Book (nampss.com). is available on the NAM PSS site. (Note: Registration for access to this site may be required.)  
View full article
Lt. Commander Reza Lt. Commander
‎2022-12-08 08:59 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2023-08-28 05:07 PM

Labels:
  • EcoStruxure Building Operation
11524 Views

How to use Google for your SMTP Mail Server

Issue Unable to send emails using Google's SMTP Server Product Line EcoStruxure Security Expert Environment Security Expert Server Security Expert Controllers (SP-C-WEB, SP-C) Google SMTP Server Cause SMTP server settings in Controller and/or Google account settings are incorrect. Resolution When configuring the Email SMTP settings under Global | Global settings confirm that the correct SMTP server address and settings are used: SMTP Mail Server: smtp.googlemail.com SMTP Port: 25 Use SSL: Enabled SMTP login: <your Google account> SMTP password: <the app password created in section below> Email SMTP settings Google has removed the "less secure app access" ability and replaced it with "app passwords" where you create a unique 16-digit passcode for each individual app requiring access. See details on how to Sign in with app passwords. To use app passwords Google requires the account to be setup for 2-Step Verification. If you do not see the App passwords item under your Google accounts Security section you can also find this by typing "app passwords" in the "Search Google Account" search bar at the top of the window, select the first item "App passwords". App passwords In App passwords press Select app and choose Other (Custom name). Add a descriptive name for the app and click GENERATE. Copy the resulting 16-digit passcode as this will be the passcode used for the SMTP server credentials. Add App password Ensure Firewall settings are not blocking access to the mail server, especially if the McAfee firewall is being used. If there is a Firewall try temporarily disabling this to test.
View full article
Guinan AdamSteele Guinan
‎2020-10-25 10:32 PM

Labels:
  • EcoStruxure Security Expert
2588 Views

ODBC (Open Database Connectivity) with EcoStruxure Building Operation

Issue ODBC used with EcoStruxure Building Operation Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Building Operation Edge Server - Standard Cause ODBC (Open Database Connectivity), a standard C programming language middleware API. is used to access database management systems (DBMS). Resolution ODBC is not supported with the current or previous releases of EcoStruxure Building Operation.
View full article
Picard Product_Support
‎2018-09-06 10:35 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2023-08-21 05:00 AM

Labels:
  • EcoStruxure Building Operation
1825 Views

What substitution codes are available to embed data into alarm text?

Issue How can I insert the points name or path into the alarm text? Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Central Building Operation Enterprise Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Building Operation Edge Server Building Operation WorkStation Cause Require dynamic text insertion in the alarm text. Resolution The following substitution codes exist for alarm messages: All SBO/EBO versions:  @(F) – The path of the monitored variable.  @(O) – The monitored object name.  @(P) – The monitored variable. In addition to the above, Version 1.2 also includes: @(V) - Displays the value of the monitored variable at the time of the state change. e.g. If you create an alarm that is monitoring a temperature object named Room1Temp and write an alarm message that says: “The point @(O) is too hot.” When the alarm is triggered it will display: “The point Room1Temp is too hot.” Refer to: Alarm Messages  
View full article
Picard Product_Support
‎2018-09-06 10:36 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2023-08-21 04:50 AM

Labels:
  • EcoStruxure Building Operation
1955 Views

Set the time for a time schedule in TAC Vista from a OPC client?

Issue Is it possible to set/change the time for a time schedule in TAC Vista from a OPC client? Product Information TAC Vista Environment Vista Server Vista OPC Server Cause  In the OPC standard supported by TAC Vista time schedules are not included Resolution No it is not possible to set/change the time for a time schedule in TAC Vista from a OPC client?
View full article
Picard Product_Support
‎2018-09-06 01:14 PM

Last Updated: Janeway Jonas_Brissman Janeway ‎2023-08-21 04:49 AM

Labels:
  • TAC Vista
1454 Views

Extended LonTalk in Vista 5.1.5 not working

Issue Extended LonTalk is supported In Vista 5.1.5 but it doesn't work, it is possible to read but not write to the device. Error message when writing: "Local network management failure" Product Line TAC Vista Environment Vista Server Cause When adding a Extended LonTalk device in to TAC Vista, TAC Vista will see in the xif file that this is a Extended LonTalk device and set a Extended LonTalk device flag for that device. It is possible to see the flag if hold down shift+Ctrl and click in properties for the lon device, it is called "EXTENDEDLONTALK".  If the xif file is imported to a TAC Vista with a version earlier than Vista 5.1.5 the Extended LonTalk will not work. Resolution Make sure the "EXTENDEDLONTALK" flag for the lon device is set, if not import the xif file again in Vista 5.1.5.  
View full article
Picard Product_Support
‎2018-09-06 02:00 PM

Last Updated: Administrator CraigEl Administrator ‎2023-08-21 05:19 PM

Labels:
  • TAC Vista
1522 Views

OGC Graphics Editor Will Not Open

Issue Nothing happens when starting the OGC editor Product Line TAC Vista Environment Vista Server Vista Workstation Cause The issue is with data execution prevention (DEP) not allowing the tacdraw application to run.  Resolution If DEP is not required on your system follow these steps: Go to Control Panel > System > Advanced > Performance Settings > Data Execution Prevention Choose "Turn on DEP for essential Windows programs and services only" Reboot the computer and the editor should launch like normal.  If DEP is required on your system follow these steps: Go to Control Panel > System > Advanced > Performance Settings > Data Execution Prevention Choose "Turn on DEP for all programs and services except those I select" Then click the add button and navigate to: For Vista 5.1.4 and up: C:\Program Files\Schneider Electric\TAC Vista 5.1.4 and choose the tacdraw.exe file. For Vista 5.1.3 and prior: C:\Program Files\TAC\TAC Vista 5.1.X and choose the tacdraw.exe file. Reboot the computer and the editor should launch like normal.  
View full article
Picard Product_Support
‎2018-09-06 02:23 PM

Last Updated: Janeway Jonas_Brissman Janeway ‎2023-08-21 12:02 AM

Labels:
  • TAC Vista
1644 Views

Error "Not enough space in RTI device"

Issue Error "Not enough space in RTI device"   Product Line TAC Vista Environment Aladdin Privilege Administrator 2.01 Vista IV Licensing Cause Memory in PSU is corrupt. Resolution Run Dongleutil, a dongle reset utility software. This utility resets the memory in the PSU that is connected to the PC. You need to install the license file again after this operation. This problem is usually seen when Inhouse PSU is used. In TAC Vista version 4.10 and later, it’s no longer necessary to install the engineering file when Inhouse PSU is in use. Just connect the PSU to the PC, and everything should work fine.
View full article
Picard Product_Support
‎2018-09-07 03:29 AM

Last Updated: Janeway Jonas_Brissman Janeway ‎2023-08-21 01:01 AM

Labels:
  • TAC Vista
1591 Views

TGML numeric presentations rounded to whole integers

Issue TGML numeric presentations rounded to integers with no decimals displayed. Product Line TAC Vista Environment Vista Workstation Vista Server   Cause Depending on the component being used to display the numeric data, it may be as simple as a property not set to display decimals. It may also be due to presentation values. Resolution If using the default Numeric Presentation from the provided Snippets library, change the property in TAC Graphics Editor for 'Decimals' to the number of decimals to be presented i.e. 4 decimals = .0001, 2 decimals = .01, etc. If not using this Snippet, check to see if getPresentationValue() is being used in a script, or if the binding itself has the Format attribute set to Presentation instead of None. Presentation value will inherit all formatting from the Vista database and not from the TGML source file.
View full article
Picard Product_Support
‎2018-09-06 02:45 PM

Last Updated: Janeway Jonas_Brissman Janeway ‎2023-08-20 11:57 PM

Labels:
  • TAC Vista
1717 Views

Way of checking if TAC Vista is logging to SQL server?

Issue There was a problem with the SQL server and the logs and events were queued in the $Queues folder.  The SQL problem is resolved but the $Queues folder has grown so much that it can't be opened to check. Is there a way of checking if Vista has restarted logging to SQL? Product Line TAC Vista Environment TAC Vista Server Microsoft SQL Server Cause When a problem occurs with the SQL server, the log values and events are saved in the $Queues folder in the TAC Vista database, so that no information is lost. As long as there is no connection to SQL, the logs and events will be queued in $Queues. Once a connection to SQL is re-established, Vista will start logging all the values in the $Queues folder, gradually emptying the folders, although this may take some time if the SQL server has been down for a while. Resolution Query the SQL database and check for logs with today's date. Download & install Microsoft SQL management studio (2005 or 2008 depending on which version of SQL is being used) Query the trend log table for logs using the following query: Start SQL management studio and log in to the TACVISTA sql instance. Click on New Query and type in the following query: use taclogdata go select * from TrendLogValue where LogTime > '2011-11-03 00:00:00.000' Note: if you have a custom configured SQL database change taclogdata to your database name. -Change the date to today's date and execute the query. If the query doesn't return any matches, change the date to an earlier date and repeat.   -Keep going until the date when contact with SQL was lost. If no matches are returned, check that the service TAC DSS writer is running. If it is then it maybe that the Vista is till trying to clear the backlog. Try again later.
View full article
Picard Product_Support
‎2018-09-10 04:50 AM

Last Updated: Janeway Jonas_Brissman Janeway ‎2023-08-21 05:22 AM

Labels:
  • TAC Vista
1484 Views

Summary view for Forced Value on I/O

Issue Summary view for Forced Value on I/O Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Building Operation Automation Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Cause Automation Server or any of connected devices can potentially have many points or values. Need to discover which ones are in Forced state. Examples: A Digital Output with default value: Digital Output with Forced value and ON: Digital Output with Forced value and OFF: Resolution You can search for forced values using the search function in WorkStation. Enabling In device option will enable finding forced values on devices hosted under EBO, as SpaceLogic and EasyLogic devices, MP and RP controllers, IP-IO modules and RP-IO modules. For more information, see Searching for Forced Values . You can also view the search in WebStation:   In EBO 2023 or later, You can search for forced values in WebStation using Diagnostics. For more information, see Displaying a List of Forced Values in WebStation .  
View full article
Picard Product_Support
‎2018-09-06 12:06 PM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2023-08-21 04:38 AM

Labels:
  • EcoStruxure Building Operation
1906 Views

The Entitlement ID has been upgraded - Please use your new Entitlement ID

Issue When an attempt is made to activate a License, the following error is displayed, and the license is not activated.   Product Line EcoStruxure Building Operation Environment Building Operation License Administrator Cause In this case the Entitlement was inactivated due to a double registration made by mistake by the Orders Dept.  Resolution Used the second active Entitlement ID to activate the license.   For more information, refer to WebHelp articles 6367 and 7440.
View full article
Picard Product_Support
‎2018-09-11 02:04 PM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2023-08-21 02:05 AM

Labels:
  • EcoStruxure Building Operation
1756 Views

Offer Creation Roadmap

Issue What new features are planned for inclusion in future product releases? Product Line Andover Continuum, EcoStruxure Building Operation, Field Devices, Satchwell BAS & Sigma, Satchwell MicroNet, TAC IA Series, TAC INET, TAC Vista, EcoStruxure Access Expert, EcoStruxure Security Expert Environment All product ranges Cause Information required on future Product Marketing plans. Resolution This document is no longer published on the Download Center by Product Management. For further information on the future product planning please contact the Product Manager for the specific product in your region. Americas: Americas.EcoStruxureBuilding@schneider-electric.com EMEA: EMEA.EcoStruxureBuilding@schneider-electric.com Asia Pacific & India: AsiaPac.EcoStruxureBuilding@schneider-electric.com
View full article
Picard Product_Support
‎2018-09-06 10:23 AM

Last Updated: Administrator CraigEl Administrator ‎2023-08-20 05:37 PM

Labels:
  • Andover Continuum
  • EcoStruxure Access Expert
  • EcoStruxure Building Operation
  • EcoStruxure Security Expert
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
2981 Views
  • « Previous
    • 1
    • …
    • 48
    • 49
    • 50
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of