How to use Google for your SMTP Mail Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to use Google for your SMTP Mail Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • AdamSteele
    AdamSteele

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
4 Likes
3279 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to use Google for your SMTP Mail Server

Guinan AdamSteele Guinan
‎2020-10-25 10:32 PM

Issue

Unable to send emails using Google's SMTP Server

Product Line

EcoStruxure Security Expert

Environment

  • Security Expert Server
  • Security Expert Controllers (SP-C-WEB, SP-C)
  • Google SMTP Server

Cause

SMTP server settings in Controller and/or Google account settings are incorrect.

Resolution

  1. When configuring the Email SMTP settings under Global | Global settings confirm that the correct SMTP server address and settings are used:
    1. SMTP Mail Server: smtp.googlemail.com
    2. SMTP Port: 25
    3. Use SSL: Enabled
    4. SMTP login: <your Google account>
    5. SMTP password: <the app password created in section below>Email SMTP settingsEmail SMTP settings
  2. Google has removed the "less secure app access" ability and replaced it with "app passwords" where you create a unique 16-digit passcode for each individual app requiring access. See details on how to Sign in with app passwords.
    1. To use app passwords Google requires the account to be setup for 2-Step Verification.
    2. If you do not see the App passwords item under your Google accounts Security section you can also find this by typing "app passwords" in the "Search Google Account" search bar at the top of the window, select the first item "App passwords".App passwordsApp passwords
    3. In App passwords press Select app and choose Other (Custom name). Add a descriptive name for the app and click GENERATE. Copy the resulting 16-digit passcode as this will be the passcode used for the SMTP server credentials.Add App passwordAdd App password
  3. Ensure Firewall settings are not blocking access to the mail server, especially if the McAfee firewall is being used. If there is a Firewall try temporarily disabling this to test.
Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (2)
  • Find more articles tagged with:
  • AdamSteele20
  • AdamSteele23
Was this article helpful? Yes No
50% helpful (1/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore