Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 501
  • Next »

Control Alarm Email Message Content in Niagara R2

Issue How can the information displayed in an alarm-generated email message be controlled in Niagara R2? Product Line TAC IA Series Environment Niagara R2 Cause The content of alarm-generated email messages is determined by the AlarmFields property in the MailRecipient object configuration. Resolution To customize the information displayed in alarm email messages: In WorkPlace Pro, locate the MailRecipient object. Right-click the object and select Properties. Go to the Config tab. Under AlarmFields, select the text fields you want included in the email body. Click Apply to save changes. The email will now contain only the selected fields.
View full article
Picard Product_Support
‎2018-09-06 01:36 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-11 10:08 PM

Labels:
  • TAC IA Series
1262 Views

Temperature Readings from I/A Series Micronet LON Controller Displayed in Fahrenheit on I/A Series R2 UNC

Issue Temperature values from an I/A Series Micronet LON controller appear in Fahrenheit within an I/A Series R2 UNC station, even though the default unit of measure is set to Metric in WorkPlace Tech. Product Line TAC IA Series Environment I/A Series R2 Micronet LON Controllers (MNL) Cause The LonWorksService in the UNC station converts SNVTs defined as temperature to Fahrenheit when the temperatureUnits property is set to Fahrenheit. This occurs regardless of the Metric setting in WorkPlace Tech. Resolution Update the temperatureUnits property in the LonWorksService to Celsius: In the UNC station, right-click LonWorksService and select Properties. Navigate to General > Config tab. Change temperatureUnits to celsius. Click Apply. Note: When set to Celsius, no conversion is performed; values are assumed to be in degrees Celsius as per LonTalk protocol. If set to Fahrenheit, SNVTs defined as temperature are converted accordingly.
View full article
Picard Product_Support
‎2018-09-06 01:35 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-11 10:06 PM

Labels:
  • TAC IA Series
1353 Views

Niagara R2: Required Lon JAR Files for Integrating ProView Display into UNC

Issue When integrating a ProView display into a Niagara R2 UNC for the first time, which Lon JAR files are required? Product Line TAC IA Series Environment Niagara R2 ProView display Cause The integration requires specific Lon JAR files and wizards to enable communication and configuration between the ProView display and the Niagara R2 UNC. Resolution Ensure the following JAR files are installed in the UNC: lonDistech-2.307.529.v1.jar lonDistechWizards-2.306.515.v111.jar wizard-2.301.529.v1.jar lonworks-2.301.529.v1.jar Additional Notes: These files must match the Niagara R2 version for compatibility. Refer to the Niagara R2 documentation for steps to install JAR files in the UNC.
View full article
Picard Product_Support
‎2018-09-06 01:35 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-11 10:03 PM

Labels:
  • TAC IA Series
1499 Views

Niagara R2: Can Alarm Notifications Be Resent Until Acknowledged?

Issue Is there a way to keep resending alarm notifications in Niagara R2 until the alarm is acknowledged? Product Line TAC IA Series Environment R2 WorkPlace Pro (all versions) Cause The system does not include a built-in mechanism to automatically resend alarm notifications for alarms that remain active and unacknowledged. Resolution Niagara R2 does not provide a way to resend an alarm that is already in an alarm state until it gets acknowledged. Once an alarm is generated and the notification is sent, it will not automatically resend unless the alarm transitions back to normal and then returns to alarm state. For repeated notifications, consider implementing external logic or using Niagara G3 (which supports this feature).
View full article
Picard Product_Support
‎2018-09-06 01:34 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-11 10:00 PM

Labels:
  • TAC IA Series
983 Views

Niagara R2: Cisco Mediator BACnet Controller Cannot Write to Exposed Objects

Issue A Cisco Mediator BACnet/IP controller connected to a Niagara R2 UNC can read exposed BACnet objects but cannot overwrite setpoints or issue commands. Product Line TAC IA Series Environment Niagara R2 all versions Cause The Niagara R2 station requires a specific BACnet user configuration to allow external BACnet devices to write values or send commands. Without this user, write requests are rejected. Resolution Create a special BACnet user in the Niagara R2 station: Open the Niagara R2 station configuration. Navigate to Security → Users. Add a new user with the following properties: User Type: BACnet Assign appropriate permissions for writing to exposed objects. Save and restart the station if required. Refer to Tridium BACnet Integration Guide, pages 4-6 and 4-7, for detailed steps.
View full article
Picard Product_Support
‎2018-09-06 01:34 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-11 09:58 PM

Labels:
  • TAC IA Series
1355 Views

Niagara R2: How to Change MailService SMTP Port from Default 25

Issue Can the Niagara R2 MailService (SMTP) port number be changed to something other than its default port 25? Product Line TAC IA Series Environment Niagara R2 CoreRuntime 2.301.429.v1 and later Cause Local IT policies may require SMTP messages to be sent on a port other than the standard port 25. Resolution Starting with CoreRuntime 2.301.429.v1, MailService supports custom SMTP ports. To configure: Navigate to Service container → MailService Properties → Config tab. In the smtpHost property, enter the SMTP server address in the following format: hostname:port Examples: ourMailSrv:40 10.10.9.4:40 Restart the station after making changes. If the port number is omitted, MailService defaults to port 25.
View full article
Picard Product_Support
‎2018-09-06 01:31 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-11 09:57 PM

Labels:
  • TAC IA Series
1534 Views

UNC/ENC Tunneling to ASD Bus: Prevent XPSI Timeout Errors by Setting Baud Rate to 1200

Issue When tunneling through a UNC (Niagara R2) or ENC (Niagara G3) to an ASD bus using XPSI, communication timeout errors occur. Product Line TAC IA Series Environment PSI/XPSI software (any version) UNC (R2) or ENC (G3) with ASD bus connected Serial tunnel client (R2 or G3) Cause Delays introduced by the Internet between the PSI/XPSI computer and the remote tunnel client can result in communication timeout errors. These delays affect the ASD bus communication speed. Resolution Set the baud rate of PSI/XPSI to 1200 to minimize or eliminate timeout errors: Open PSI/XPSI software. Navigate to Site Setup Configuration. Set Baud Rate = 1200 as recommended in the TAC I/A Series Enhanced ASD Driver Engineering Guide (F-27429, Chapter 5, Table 5.1). Reference: TAC I/A Series Enhanced ASD Driver Engineering Guide, F-27429.
View full article
Picard Product_Support
‎2018-09-06 01:29 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-11 09:54 PM

Labels:
  • TAC IA Series
1175 Views

Niagara R2: How to Indicate Override on GxText by Changing Color

Issue Need to visually indicate when a linked object is in an override condition by changing the color of a GxText object in Niagara R2 graphics. Product Line TAC IA Series Environment Niagara R2 WorkPlace Pro graphics using GxText objects Cause Operators require a clear visual cue on graphics when an object is overridden. By default, GxText does not automatically change color based on override status. Resolution Niagara R2 provides objects in the programLib JAR that can detect override conditions and trigger color changes: Detect Override Condition Use objects from programLib/hvac folder: AoCheckForOverride BoCheckForOverride These objects output a Boolean flag when an override exists. Change Color on Override Use objects from programLib/util folder: ColorOvBinary ColorOvFloat Connect the priority input of these objects to the overridden object. When an override occurs, the linked object changes color (e.g., magenta). Update GxText Modify the Active Text as needed. Connect the color-changing object to the GxText on the graphic. The GxText will now change color when the override condition exists.
View full article
Picard Product_Support
‎2018-09-06 01:25 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-11 09:47 PM

Labels:
  • TAC IA Series
1234 Views

Niagara R2: How to Modify Multiple Object Property Values at Once Using AdminTool

Issue Need to change the booleanKey property value from “overridden” to “value” for hundreds of GxBoolean objects. Is there a way to update multiple objects simultaneously without editing each one individually? Product Line TAC IA Series Environment Niagara R2 (all versions) Cause Manually updating each object’s property is time-consuming. Niagara R2 includes an AdminTool utility that provides an admin-level command to Search and Replace property values across multiple objects in the station database. Resolution Locate AdminTool Found in the Local Library: tridium/apps/AdminTool (JAR file). Add AdminTool to Station Copy the AdminTool app into the station. Configure AdminTool Open AdminTool and go to the Config tab. Set parameters as follows: rootNode: /db/ propertyName: booleanKey elementName: (leave blank) newValue: Value recurseChildren: true Explanation: When set to true , the tool will traverse all child nodes under the specified rootNode and apply changes to matching properties. If set to false , only the root node is modified. objectTypeFilter: (optional) nodeNameFilter: (optional) propertyValueFilter: (optional) Execute Search and Replace Right-click AdminTool and select searchAndReplace. All GxBoolean objects’ booleanKey will now be set to “value”. Additional Info: Refer to WorkPlace Pro Help: Help > Index > General Index > AdminTool for more details.
View full article
Picard Product_Support
‎2018-09-06 01:24 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-11 09:44 PM

Labels:
  • TAC IA Series
1305 Views

How to Determine the HostId of a Computer in Niagara R2

Issue Niagara R2 is installed on a computer, but the HostId is unknown. The user needs an alternative method to find the HostId without accessing the license.properties file. Product Line TAC IA Series Environment Niagara R2 Cause The HostId is required for licensing or troubleshooting, but the usual method (checking license.properties ) is unavailable. Resolution Open the Niagara Console (found in the Niagara R2 Program Group). Type the following command: nre -hostid Press Enter. The HostId will be displayed on the screen. Additional Info: The nre command can also display other system details. Use nre -help to view available options.
View full article
Picard Product_Support
‎2018-09-06 01:24 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-11 09:39 PM

Labels:
  • TAC IA Series
2861 Views

Issues / Errors during server SSL certificate creation

Issue The following issues have been seen when attempting to add and generate SSL Certificates via Device Administrator. Servers appeared as "unknown” in the Device Administrator server list, even though the certificate state is shown as "OK”. (green tick) The Server Certificates option is greyed out. Selecting Server Certificates in Device Administrator (when available) displays an error: Unable to get certificates from the device. Reason: Failed to read property ~/System/Security Manager/Certificates/ActiveCertificate.  AttributeError: 'ConnectionRefusedError' object has no attribute 'library.' Product Line EcoStruxure Building Operation. Environment EcoStruxure Building Operation server  Building Operation Device Administrator  Certificates enabled; HTTPS required end-to-end Cause The issue occurs due to an HTTPS port mismatch: Servers were added in Device Administrator using port 443, but were actually communicating on a different HTTPS port (e.g., 445). This port change is typically made via the Communications tab in WorkStation and does not automatically update in Device Administrator. Device Administrator does not validate the HTTPS port during server addition because it uses SSH and admin credentials for initial connection. However, certain features (such as certificate management) require the correct HTTPS port to be configured.   Resolution From WorkStation check the Communication tab for all servers: Ensure HTTPS is enabled between all EBO servers when using certificates. Confirm the active HTTPS communications port configured on each server (e.g., 445) In Device Administrator On affected servers, remove and re-add them in Device Administrator using the correct HTTPS port. After re-adding, manage Server Certificates in Device Administrator as usual. See:  Certificates Managed using Device Administrator Certificates Managed Using WorkStation    Additional Note:  Changing communication ports impacts connectivity and certificate bindings. Before modifying ports, confirm firewall rules, service bindings, and any reverse proxies. Always perform changes during a maintenance window and ensure full backups are available.
View full article
Picard RobertAndriolo Picard
‎2025-12-11 08:00 PM

on ‎2025-12-11 08:00 PM

Labels:
  • EcoStruxure Building Operation
72 Views

BACnet Points Displayed as Overridden (Purple) on I/A Series R2 Graphics

Issue BACnet controller objects that have not been overridden appear in purple on I/A Series R2 graphic screens, indicating an override condition incorrectly. Product Line TAC IA Series Environment I/A Series R2 graphic screens BACnet controller inputs displayed on Niagara graphics MNB controller firmware version 1.2 or higher Cause Purple color indicates the BACnet OVERRIDDEN flag is set to TRUE. This behavior is normal and results from compliance with BACnet Specification 135-2004 for BTL certification. Read-only BACnet objects (e.g., Analog Value, Binary Value) must indicate an override condition because their Present Value cannot be changed via BACnet services. Niagara interprets this as overridden, even though it is simply read-only. Resolution Two approaches to prevent purple override indication: Buffer the Value Using Native Niagara Objects Use a Niagara AI object to display the value without transferring the override condition. If BACnet points are in a poll-on-demand container, add a gx type object linked to the BACnet point (invisible) to initiate polling. Display the value using another gx object linked to the AI object. Disable Status Color on GxText Objects Configure the statusColorEnabled property of the GxText object to false. This prevents the purple background from appearing.
View full article
Picard Product_Support
‎2018-09-06 01:23 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-11 07:28 PM

Labels:
  • TAC IA Series
2175 Views

Lost Sync with System Clock – Resetting Control Engine in Niagara R2 Enterprise Server

Issue Enterprise Server displays repeated warning messages: Lost Sync with system clock - resetting control engine Product Line TAC IA Series Environment Niagara R2 Enterprise Server UNC-520, UNC-410 controllers Cause The warning occurs due to incorrect or inconsistent time synchronization settings between the Enterprise Server and UNCs. This can result from: Improper serverEnabled or clientEnabled configuration Missing or incomplete time protocol server entries Tight clientResetTolerance values Resolution Verify and adjust the following settings: Enterprise Server (ES): serverEnabled = true if syncing with UNC clientEnabled = true if ES gets time from an internet or site server; otherwise set to false clientResetTolerance : Default is 30 sec (too tight). Set to 60 sec or more (enter value in seconds) timeProtocolServer* : If clientEnabled = true , all three slots must contain a time server address. If only one server is used, repeat the same address in all slots. No blank slots allowed UNCs (TimeSyncService): serverEnabled = false clientEnabled = true clientResetTolerance : Same as ES (≥60 sec) timeProtocolServer* : Same rule as ES Reboot the UNC after making changes
View full article
Picard Product_Support
‎2018-09-06 01:22 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-11 07:25 PM

Labels:
  • TAC IA Series
1092 Views

Enterprise Server Error: “Cannot Subscribe – Invalid Node” in I/A Series R2

Issue The I/A Series R2 (Niagara) Enterprise Server displays the error: ERROR: Cannot subscribe: Invalid node: (specifies node) Product Line TAC IA Series Environment I/A Series R2 Enterprise Server Cause This error occurs due to invalid subscriptions (swids). It typically happens when the parent container or object name on the UNC is changed without deleting and recreating the associated external link. The swid name changes, but the external link still references the old, invalid swid.  Resolution Review the links specified in the error message. Identify any external links referencing outdated swids. Delete and recreate these links to ensure they point to the correct node.
View full article
Picard Product_Support
‎2018-09-06 01:22 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-11 07:22 PM

Labels:
  • TAC IA Series
1276 Views

Exporting I/A Series R2 Logs (Error or Audit) to a Text File

Issue How can the entire I/A Series R2 Error Log, Audit Log, or any other system log be saved to a text file for easier review? Product Line TAC IA Series Environment I/A Series R2 Niagara (2.15 or later) Cause Log data often spans multiple screens, making troubleshooting cumbersome. A text file format allows easier searching, filtering, and sharing of log information. Resolution Access the UNC or Enterprise Server via a web browser using: http://<ipaddress>/log/index Replace <ipaddress> with the device’s IP address. Log in using the station username and password. The Log Index page will display available logs (e.g., ErrorLogService , AuditLogService ). For the desired log, select a display format such as: text/plain text/comma-separated-values text/tab-separated-values The log contents will appear in the browser. Use File > Save As to save the output as a text file. Example: Selecting text/plain for ErrorLogService generates a file with entries like: 2011-04-15T09:22:19.59-5,MESSAGE,/LON_BACnet_522services/ErrorLogService,ErrorLogService installed 2011-04-15T09:22:38.89-5,MESSAGE,/LON_BACnet_522,Station started successfully. (HTTP port=80)
View full article
Picard Product_Support
‎2018-09-06 01:19 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-11 07:19 PM

Labels:
  • TAC IA Series
1315 Views

Workplace Tech 5.10.1 Rtmonitor.exe Error

Issue When attempting a device browse in Workplace Tech 5.10.1, an error pop up, "CoCreateInstance(CLSID_RTApplication) failed" is invoked A critical error with Rtmonitor.exe when running Workplace Commissioning Tool Product Line TAC IA Series Environment Workplace Tech => 5.10.1  Workplace Commissioning Tool => 5.10.1 Windows OS 32 bit Cause Environment Variables /variable/path includes the incorrect path to the LonWorks\bin.  This doesn't allow the rtmonitor.exe to be executed. Resolution When the Workplace Tech 5.10.1 bundle of applications are installed, the Environment Variables is modified to include,  %ProgramFiles(x86)%\LonWorks\bin In a 32 bit OS, this ProgramFiles(x86) folder does not exist.  This path has to be modified so the assets can be found. Remove the "(x86)" so the path appears as below. Note: This is only applicable for 32 bit operating systems.
View full article
Guinan RandyDavis Guinan
‎2021-04-21 12:32 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-11 05:48 PM

Labels:
  • TAC IA Series
3141 Views

Error When Saving Station Information in Niagara Application Tunneling on Windows 7

Issue When saving station information in the Niagara Application Tunneling dialog window, the following error occurs: “Windows Shell Common DLL has stopped working.” This prevents proper configuration of the tunnel client. Product Line TAC IA Series Environment I/A Series R2 LON Tunnel Client I/A Series R2 Serial Tunnel Client Cause The issue is due to compatibility between the I/A Series R2 Tunnel Client DLL files and Windows 7 operating systems. Resolution Configure the Niagara Application Tunneling dialog box with the required station information: For Serial Tunnel: Select a valid COM port and enter host address, username, and password. For LON Tunnel: Select a valid LON port and enter host address, username, and password. Ensure the tunnel client is set to Silent Mode. Click OK to save the data. When the dialog box appears indicating Windows is checking for a solution, select Cancel before the timeout that prompts to “Close Program.” This action saves the station information successfully. Note: This is a workaround for Windows 7 compatibility issues.
View full article
Picard Product_Support
‎2018-09-06 01:18 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-11 04:34 PM

Labels:
  • TAC IA Series
1242 Views

BACnet Ethernet Driver Fails to Open Ethernet Device on I/A Series R2 Enterprise Server

Issue The BACnet Ethernet driver on an I/A Series R2 Enterprise Server cannot open the Ethernet device, preventing BACnet over Ethernet communication. The following error appears in the station's Standard Output: ERROR: Cannot start Ethernet Packet Driver tridium.nre.DriverException: Cannot open \\Device\\E100B1 [ethernet] Product Line TAC IA Series Environment I/A Series R2 Enterprise Server BACnet Ethernet communications Cause BACnet over Ethernet requires a special low-level network access driver. If this driver is not installed or configured correctly, the Enterprise Server cannot establish BACnet Ethernet communication. Resolution Verify that BACnet Ethernet communication is required for your application. Install and configure the host link-layer support driver as described in the BACnet Supervisor Reference: Refer to pages 1-20 to 1-24 in the BACnet Supervisor Reference. The document is located in: \\niagara\\docs\\BACnet Restart the Enterprise Server after configuration changes. Confirm that the Ethernet device is accessible and properly bound to the BACnet Ethernet driver. Note: This step is only necessary when using BACnet over Ethernet. For BACnet/IP, this configuration is not required.
View full article
Picard Product_Support
‎2018-09-06 01:17 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-11 04:29 PM

Labels:
  • TAC IA Series
1154 Views

Basic Configuration for R2 ASD (IbsASD) Driver

Issue The R2 ASD (IbsASD) driver may fail to communicate correctly with ASD devices if not configured properly. Product Line TAC IA Series Environment R2 ASD (IbsASD) driver (all revisions) Cause Incorrect driver configuration settings can lead to intermittent or failed communication with ASD devices. Resolution Configure the driver using the following recommended settings: General / Engineering retryCount = 3 responseTimeout = 2 sec Poll / Config cycleTime = 333 ms × number of devices on the ASD bus (Approx. 3 devices per second) Comm / Config commPort = COM4, COM5, COM6, or COM7 (depending on port used) maxBaudRate = 19200 (Use 9600 if PEM1 controllers exist on the ASD bus) DeviceStatus / Config deviceStatusPingDelay = 60000 ms Tip: Always verify baud rate compatibility with connected devices and ensure proper port selection for stable communication.
View full article
Picard Product_Support
‎2018-09-06 01:15 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-11 04:26 PM

Labels:
  • TAC IA Series
1090 Views

Monitor DI1 and DI2 Status on Viconics VT7600 Lon Thermostat via Niagara R2 UNC

Issue How can a Niagara R2 UNC be configured to monitor the DI1 and DI2 contact status of a Viconics VT7600 Series Lon thermostat? Product Line TAC IA Series Environment Niagara R2 UNC Viconics VT7600 Series Lon Thermostat  Cause The VT7600 thermostat reports its digital input (DI) statuses within a single SNVT (nvoSccStatus). These bits are not directly exposed in the UNC without additional configuration. Resolution Ensure the VT7600 shadow object is commissioned in the UNC. Open the Workspace Editor and navigate to the page containing the VT7600 shadow object. Go to /tridiumx/lonworks/conversion and copy the DynamicDemux object into the Workspace. Link the VT7600 shadow object to the DynamicDemux object: Under VT7600 column, select nvoSccStatus. Under DynamicDemux column, select link and click OK. The DI statuses are mapped as: DI1 → bit18 of nvoSccStatus DI2 → bit17 of nvoSccStatus Link these bits to the desired monitoring objects in the UNC. Tip: The DynamicDemux object allows individual bits from SNVTs to be exposed for monitoring, making it ideal for handling composite status points.
View full article
Picard Product_Support
‎2018-09-06 01:15 PM

Last Updated: Administrator CraigEl Administrator ‎2025-12-11 04:23 PM

Labels:
  • TAC IA Series
1145 Views
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 501
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore