UNC/ENC Tunneling to ASD Bus: Prevent XPSI Timeout Errors by Setting Baud Rate to 1200
  • UNC/ENC Tunneling to ASD Bus: Prevent XPSI Timeout Errors by Setting Baud Rate to 1200
  • CraigEl
    CraigEl
  • SESA113595
    SESA113595
‎2018-09-06 01:29 PM
Last Updated: Administrator CraigEl Administrator ‎2025-12-11 09:54 PM
When tunneling through a UNC (Niagara R2) or ENC (Niagara G3) to an ASD bus using XPSI, communication timeout errors occur.
TAC IA Series
  • PSI/XPSI software (any version)
  • UNC (R2) or ENC (G3) with ASD bus connected
  • Serial tunnel client (R2 or G3)
Delays introduced by the Internet between the PSI/XPSI computer and the remote tunnel client can result in communication timeout errors. These delays affect the ASD bus communication speed.
Set the baud rate of PSI/XPSI to 1200 to minimize or eliminate timeout errors:
  1. Open PSI/XPSI software.
  2. Navigate to Site Setup Configuration.
  3. Set Baud Rate = 1200 as recommended in the TAC I/A Series Enhanced ASD Driver Engineering Guide (F-27429, Chapter 5, Table 5.1).
Reference:
TAC I/A Series Enhanced ASD Driver Engineering Guide, F-27429.