Issue
Product Line
TAC IA SeriesEnvironment
- Niagara R2 UNC
- Viconics VT7600 Series Lon Thermostat
Cause
Resolution
- Ensure the VT7600 shadow object is commissioned in the UNC.
- Open the Workspace Editor and navigate to the page containing the VT7600 shadow object.
- Go to
/tridiumx/lonworks/conversionand copy the DynamicDemux object into the Workspace. - Link the VT7600 shadow object to the DynamicDemux object:
- Under VT7600 column, select nvoSccStatus.
- Under DynamicDemux column, select link and click OK.
- The DI statuses are mapped as:
- DI1 → bit18 of nvoSccStatus
- DI2 → bit17 of nvoSccStatus
- Link these bits to the desired monitoring objects in the UNC.
Tip: The DynamicDemux object allows individual bits from SNVTs to be exposed for monitoring, making it ideal for handling composite status points.