Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Issues / Errors during server SSL certificate creation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Issues / Errors during server SSL certificate creation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
657 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Issues / Errors during server SSL certificate creation

RobertAndriolo Champion
‎2025-12-11 08:00 PM

on ‎2025-12-11 08:00 PM

Issue

The following issues have been seen when attempting to add and generate SSL Certificates via Device Administrator.

  • Servers appeared as "unknown” in the Device Administrator server list, even though the certificate state is shown as "OK”. (green tick)
    DA-Unknown-Server Name.png
  • The Server Certificates option is greyed out.
  • Selecting Server Certificates in Device Administrator (when available) displays an error:
    • Unable to get certificates from the device. Reason: Failed to read property ~/System/Security Manager/Certificates/ActiveCertificate.  AttributeError: 'ConnectionRefusedError' object has no attribute 'library.'

DA-CertificatesError-GettingCertificates.png

Product Line

EcoStruxure Building Operation.

Environment

  • EcoStruxure Building Operation server 
  • Building Operation Device Administrator 
  • Certificates enabled; HTTPS required end-to-end

Cause

The issue occurs due to an HTTPS port mismatch:

  • Servers were added in Device Administrator using port 443, but were actually communicating on a different HTTPS port (e.g., 445).
  • This port change is typically made via the Communications tab in WorkStation and does not automatically update in Device Administrator.
    WorkStation-Communication.png
  • Device Administrator does not validate the HTTPS port during server addition because it uses SSH and admin credentials for initial connection. However, certain features (such as certificate management) require the correct HTTPS port to be configured.
    DA-ServerAdd-2.png

 

Resolution

From WorkStation check the Communication tab for all servers:

  • Ensure HTTPS is enabled between all EBO servers when using certificates.
  • Confirm the active HTTPS communications port configured on each server (e.g., 445)

In Device Administrator

  • On affected servers, remove and re-add them in Device Administrator using the correct HTTPS port.
  • After re-adding, manage Server Certificates in Device Administrator as usual.

See: 

Certificates Managed using Device Administrator

Certificates Managed Using WorkStation 

 

Additional Note: 

Changing communication ports impacts connectivity and certificate bindings. Before modifying ports, confirm firewall rules, service bindings, and any reverse proxies. Always perform changes during a maintenance window and ensure full backups are available.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • RobertAndriolo25
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore