Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

How to perform the online activation of an embedded license at EBO 2022

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to perform the online activation of an embedded license at EBO 2022
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • Reza
    Reza
  • RobertAndriolo
    RobertAndriolo
  • Hernan_Urueña
    Hernan_Urueña
  • Sampath_Konda
    Sampath_Konda

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
8 Likes
14477 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to perform the online activation of an embedded license at EBO 2022

Lt. Commander Reza Lt. Commander
‎2022-12-08 08:59 AM

Last Updated: Picard RobertAndriolo Picard ‎2023-08-28 05:07 PM

Issue

Users may want to know how to perform the online activation of an embedded license 

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Automation Server Premium (AS-P)
  • Building Operation Automation Server Bundled (AS-B)

Cause

From Building Operation 2022, the Automation Server (Classic/Secure boot AS-B or AS-P) and features like Smart Drivers, SNMP notifications, Personalized dashboards, TimescaleDB, MQTT Publish/Subscribe, Modbus, Serial MS/TP, ES Connection, Server I/O, Field Devices, SAML Authentication, Zoning, and BACnet IP require a license.

Customers need to know how to activate their embedded licenses to enable these features.

Resolution

This video will demonstrate how to

  • Find the list of supported features by each activation ID.
  • Activate an embedded license on an Automation Server
  • Verify the embedded license status via the Device Administrator, Workstation, and the Flexnet operation license portal.

[video]

Notes

  1. Check each activation ID's supported features using the part number or license description through the Features and Licensed Products Table. 
  2. The Flexnet operation license portal is a public FlexNet Login (flexnetoperations.com) accessible from anywhere with an Internet connection. 
  3. The Automation Server and the PC running the Device Administrator must have outbound connectivity to the license activation server over the Internet. Check the resolution section of this article Could not establish contact with License Server using SmartX Server - Communities to verify if the Automation Server has access to the Flexnet license activation server.
  4. For troubleshooting, refer to Embedded license activation fails.
  5. Web helps:  Assigning Licenses and Activating Licenses Online.
  6. An Embedded DEMO license is available for temporary use during project engineering and installation until you know each device's specific licensing needs. Please visit How to activate a demo license on an Automation Server at EBO 2022.
  7. If the Automation Server does not have access to the Flexnet license activation server (no Internet connection), you can perform the steps in the following article Offline activation of embedded licenses. 
    Please take note that starting from Building Operation 2023 version 5.0.3 and higher, Automation Servers are no longer required to be connected to the Internet. The Device Administrator can access the internet and manage communication and license activation for the 'offline' Automation Servers.  
  8. A shorter version of the Online Activation of Embedded Licenses for Automation Servers-Digital Job Book (nampss.com). is available on the NAM PSS site. (Note: Registration for access to this site may be required.)  
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • HernanUruena23
  • HernanUruena24
  • RezaAmirzadeh22
Was this article helpful? Yes No
75% helpful (6/8)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore