Embedded license activation fails

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Embedded license activation fails
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
14309 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Embedded license activation fails

Janeway PeterEdvik Janeway
‎2020-03-19 02:35 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Issue

When trying to activate an embedded license on a SmartX Server using Device Administrator, the activation fails with the following error message:

Failure (error) received when reclaiming an embedded license on an Automation Server

 

"Embedded operation: Activate failed: ASEmbeddedAPI internal error: Capability request could not be created."

ErrorMessage2.png

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Automation Server Premium (AS-P)
  • Building Operation Automation Server Bundled (AS-B)
  • Building Operation Automation Server (AS)

All of the above v. 3.0 or higher

Cause

The cause of this problem is that the trusted storage, i.e., the embedded license database on the SmartX server, is corrupt. The embedded licensing framework undertakes internal checking and if it determines there is a consistency problem, it will consider the trusted storage to be corrupt. This means that no operations to the trusted storage, such as activating licenses, will succeed. At the time of writing, it is unclear why the consistency problems happen.

In the server log, you may also observe the following error message:

10:08:06: Executing licensing command
10:08:06: Executing embedded operation: Activate ActivationID: ACT-XXXXXXXXXX-XXXXXX-XXXXXXXX
10:08:11: Embedded operation: Activate failed: ASEmbeddedAPI internal error: Capability request could not be created
10:08:11: Licensing command completed
10:08:11: Activating licenses failed

(Real Activation ID replaced with ACT-XXXXXXXXXX-XXXXXX-XXXXXXXX)

 

Although this process is specific to the "Capability request could not be created" error, similar errors can be corrected by following the steps shown in the resolution. Please attempt all steps before contacting support.

 

Resolution

 

Building Operation 2022 v4.0.4  and above

Upgrading to the above versions will now resolve the trusted storage corruption and inhibit license activation.


Building Operation 3.2.X and up to EBO 2022 v4.0.3

 

Note:
Although this process is specific to the "Capability request could not be created" error, similar errors can be corrected by following the below steps. Please attempt all steps before contacting support. 

 

  1. Clear trusted storage within the server
    1. Using Device Administrator select the affected server and Open a PuTTY Console
      DA_Console.png
    2. An alternative way of connecting to the server is to use WinSCP.
    3. Use File protocol SCP and the admin user.
      WinSCP-Login.png
  2. When connected, follow the instructions as per the Word Document also attached below
  3. Warm or Cold Start the AS-P
  4. If failures still occur, attempt the Offline Activation of Licenses Workflow; The key step is that the license is activated offline and then transferred to the server in two different steps, allowing the license activation process to complete successfully.  
  5. Warm or Cold Start the AS-P
  6. If there are still failures with either of these options, send a support request through your local support center including the errors seen with each activation attempt.  

 

Building Operation version lower than 3.2.X

 

  1. If the embedded license is a Client license, there is no need to activate the license. Install the EBO Hotfix 3.0.3.2001 (CP1) or later. This will remove the enforcement of SmartX server Clients in the licensing system. See also article Embedded WebStaion client license when logging directly into a SmartX server no longer needed.
  2. Other licenses like SmartDrivers, SNMP, and Personal Dashboards may still need to be activated. Contact your local support center to fix this problem.



Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
Tags (8)
  • Find more articles tagged with:
  • HernanUruena24
  • JonasBrissman22
  • PeterEdvik20
  • PeterLarsen25
  • QC42070
  • RezaAmirzadeh22
  • RobertAndriolo22
  • RobertAndriolo23
Was this article helpful? Yes No
100% helpful (5/5)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore