Way of checking if TAC Vista is logging to SQL server?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Way of checking if TAC Vista is logging to SQL server?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Jonas_Brissman
    Jonas_Brissman
  • sesa177673
    sesa177673
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1551 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Way of checking if TAC Vista is logging to SQL server?

Picard Product_Support
‎2018-09-10 04:50 AM

Last Updated: Janeway Jonas_Brissman Janeway ‎2023-08-21 05:22 AM

Issue

There was a problem with the SQL server and the logs and events were queued in the $Queues folder.  The SQL problem is resolved but the $Queues folder has grown so much that it can't be opened to check.
Is there a way of checking if Vista has restarted logging to SQL?

Product Line

TAC Vista

Environment

  • TAC Vista Server
  • Microsoft SQL Server

Cause

When a problem occurs with the SQL server, the log values and events are saved in the $Queues folder in the TAC Vista database, so that no information is lost. As long as there is no connection to SQL, the logs and events will be queued in $Queues. Once a connection to SQL is re-established, Vista will start logging all the values in the $Queues folder, gradually emptying the folders, although this may take some time if the SQL server has been down for a while.

Resolution

Query the SQL database and check for logs with today's date.

  1. Download & install Microsoft SQL management studio (2005 or 2008 depending on which version of SQL is being used)
  2. Query the trend log table for logs using the following query:
    1. Start SQL management studio and log in to the TACVISTA sql instance.
    2. Click on New Query and type in the following query:
      use taclogdata
      go
      select *
      from TrendLogValue
      where LogTime > '2011-11-03 00:00:00.000'

Note: if you have a custom configured SQL database change taclogdata to your database name.

-Change the date to today's date and execute the query. If the query doesn't return any matches, change the date to an earlier date and repeat.

 

-Keep going until the date when contact with SQL was lost.

If no matches are returned, check that the service TAC DSS writer is running. If it is then it maybe that the Vista is till trying to clear the backlog. Try again later.

Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 6624
  • JonasBrissman23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore