Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,848
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 331
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 15
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 23
    • 24
    • 25
    • …
    • 508
  • Next »

Remove old and or disabled Alarms from Alarm Pane

Issue In the Workstation, old alarms are showing in the alarm pane. Recheck does not remove, and the only option left is to "Hide". The same goes for disabled alarms. Is there a way to erase or scrub these 8-month-old alarms? When checking disabled alarms, there are a lot of alarms that have been disabled, but no one has disabled any alarms. When right-clicking on the alarms to get the context menu, most of the alternatives are greyed out. Product Line EcoStruxure Building Operation Environment StruxureWare Building Operation version 1.2 or higher Cause First, check the disabled cause to see what disabled the alarms. If it is "user," a person has disabled them. If it is "system," the system has automatically disabled them because the alarm object has lost its monitored value. Resolution Alarms in the alarm view "Recheck" command does not help then try the "Alarms Integrity Check" commend, please see LL Removing invalid alarms  Check the source path on the alarms, do they point to actual alarm objects? If the alarm objects that triggered the alarm in the first place still exist, you should be able to disable them then just enable them again. If you cannot, use the disable button in the alarm viewer then you can use the Disable alarm property in the editor (assuming version 1.2 or higher). If you can’t disable them then try to trigger them back and forth once. If the alarm objects don’t exist anymore, create alarms that would fit the source path, then just trigger those. After that, it should be safe to delete the alarm objects again. Basically, the alarms you create will take ownership of the old alarms in the viewer. Also, add the column Type in the alarm viewer and see what type they are. It would be helpful to know what the Source path and System alarm id (if there is one) are. Remove old Alarms in Alarm Pane Disabled alarms If the monitored values are not used anymore delete the alarm object that monitors the value If this is not enough make sure the path exists in the system, it can be needed to recreate the alarm in the correct path meaning the folder structure needs to be recreated. There is also the choice of right-clicking on the Alarm which gives the following menu: From this menu, one can Disable the alarm or alternatively, Hide the alarm. To view Hidden or Disabled alarms once they are not shown in the Alarms window, select one of the two Icons from the Alarms window icons as shown below:
View full article
Picard Product_Support
‎2018-09-10 10:53 PM

Last Updated: Guinan RandyDavis Guinan ‎2021-10-26 07:43 AM

Labels:
  • EcoStruxure Building Operation
4311 Views

Migrating PostgreSQL/TimescaleDB (ebo_db)

Issue How to migrate ebo_db from an old PostgreSQL/TimescaleDB PC to a new PostgreSQL/TimescaleDB PC Product Line EcoStruxure Building Operation Environment PostgreSQL TimescaleDB pgAdmin Building Operation Workstation Cause When using External log Storage (the TimescaleDB in PostgreSQL server) in EcoStruxure Building Operation, it is often required to migrate the TimescaleDB (ebo_db) to a new PC or a different HDD due to the hard-disk space issue.   Resolution Stop the External Log Storage (TimescaleDB) from all the EBO servers (ES & AS’s). Using the attached zip file, extract the XML TimescaleDB Search Export and import this to the root location of your server.   The resulting search results will provide ALL servers' Timescale objects and show the status of the Event and Trend configurations. allowing you to multi-select and change the Event and Trend configuration settings quickly.  Use the CRTL key to only select the relevant servers. Alternatively, follow the steps below to locate these properties manually.    Note the Export is for version 3.2.3 Expand the ES Server, expand the System folder, and expand the External Log Storage folder. Right-click the TimescaleDB and select the Properties. Disable the Event Configuration & Trend Configuration and save. Repeat the above operation for all the other servers (AS’s) that are enabled for the External Log Storage. Create a new database in the destination External Log Storage server PC using the “EBO External Log Storage Installer” tool. Refer to page 5 “Database Management” section of the “EBO External Log Storage Installer.pdf” document for detail. Backup the “ebo_db” from the source TimescaleDB server PC using the pgAdmin 4 (refer to https://www.pgadmin.org/docs/pgadmin4/development/backup_dialog.html ), or refer to page 8 “Backup” section of the “EBO External Log Storage Installer.pdf” document for detail. Copy the DB backup file to the destination TimescaleDB server PC and restore the database using the pgAdmin4 tool (refer to https://www.pgadmin.org/docs/pgadmin4/development/restore_dialog.html ). DB Restoration may take a couple of minutes to a couple of hours depending on the size of the database. DB restoration results may show an error caused by pre-existing information in some tables, but it can be ignored. Once DB restoration is completed, make sure to check the timestamp of the oldest log data and the latest log data to verify the result. Start the External Log Storage (TimescaleDB) from all the EBO servers (ES & AS’s) using the search provided in Step 1 or manually as follows: Expand the ES Server, expand the System folder, and expand the External Log Storage folder. Right-click the TimescaleDB and select the Properties. Change the Database name, Host address, User name, and Password for the new (destination) External Log Storage server PC Enable the Event Configuration & Trend Configuration and save. Repeat the above operation for all the other servers (AS’s) that were disabled in the above step 1.
View full article
Lieutenant | EcoXpert Master SangKim Lieutenant | EcoXpert Master
‎2022-02-08 01:17 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2022-02-08 06:53 PM

Labels:
  • EcoStruxure Building Operation
4336 Views

Upgrading AS (Classic) to AS-P-NL

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue Need to replace and upgrade AS (Classic) to AS-P-NL. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server (AS) Building Operation Automation Server Premium non-LON (AS-P-NL) Cause From EBO v3.2 the AS-P-NL is available, there is a need to upgrade an AS (Classic) but the AS is only supported up to v3.1. Resolution A lower version of EBO can be installed into the AS-P-NL e.g. from v2.01, but this must only be for the purpose of upgrading the database.   Therefore the upgrade path can be as this example shows, there is a requirement to upgrade an AS from v1.6: Upgrade AS v1.6 to v3.1.x) . Backup the AS. Install v3.1.x) on AS-P-NL ( x needs to be same as in step 1). Note: Installing 3.1.x on an AS-P_NL is only for the purposes of upgrading the database, the following steps 4. and 5. must be completed . Restore backup on AS-P-NL. Upgrade to v3.2 or later.   For details regarding upgrade paths see article - Upgrade path from version 1.0 to current version 
View full article
Sisko DavidChild Sisko
‎2021-04-01 07:09 AM

Labels:
  • EcoStruxure Building Operation
4352 Views

Changing the BACnet device instance of the SE7000 series room controllers.

Issue The Device ID and name in a BACnet SE7000 room controller is factory set to the model number plus the MAC address. By default the MAC is set to 254 in the room controller, meaning the device does not communicate since valid MAC addresses need to be in the range 0-127. In cases where multiple BACnet networks containing SE7000 BACnet room controllers are connected to the same BACnet internetwork there could be duplicate ID's when using this schema. In these instances a T7600 Device Configurator Tool can be used to change these fields. Product Line EcoStruxure Building Operation, EcoStruxure Building Expert Environment • Building Operation Workstation • Building Operation Automation Server • SSL SE7000 Cause The Device ID and name in a BACnet SE7000 room controller is factory set to the model number plus the MAC address. By default the MAC is set to 254 in the room controller, meaning the device does not communicate since valid MAC addresses need to be in the range 0-127. For example when a VT7200F5000B room controller with a MAC address of 41 is connected to a network, its default Device Name will be VT7200F5x00B-41 and its default Device ID will be 72041. The device ID and name will change as soon as the MAC address is changed at the controller. The MAC address is set in the Installer configuration parameter menu using the Com Addr parameter. These fields can also be set by any BACnet management tool that can access these properties. Resolution The goal of this document is to give simple instructions on how to change the Device Instance of the VT7000 series thermostats using the T7600 Device Configurator tool and the recommended connections and wiring. 1. Converter (can be other models): Model 485OT9Lor USOTL4 from B&B Electronics. A USB-to-RS485 converter, like one used for MSTP captures, will work as well.  2. Recommended wiring for the configuration of Device Instances: The SE7000 room controllers have to be connected only to the converter (which has to be powered up) and disconnected from the network controller. The EOL resistors should remain at both ends of the trunk. 3. Setting up the software The software is supplied as a simple installer file download the software from here and run the installer. Prior to running the program for the first time setup steps 4 and 5 must to be accomplished. 4. Setting Windows Compatibility mode The T7600 Device Configurator Tool is legacy tool and therefore is only supported in a Windows 9X operating system, It has been tested and found to work in later versions of Windows by setting the compatibility mode to Windows 95 Locate the executable file T7600_MSTP_Config.exe in the C:\Program Files\Fastek\T7600 Config\ folder. Right click the file and select properties Go to the compatibility tab and change select Run this program in compatibility mode for: "Windows 95" from the drop down menu then click OK 5. Set the PC communications port Open the BACDOCM.ini located in the C:\Windows folder and enter communications port number in the line highlighted below and save the file. If a valid com port is not entered here the program will generate errors when launched and will not operate. Instructions on how to use the converter (file T7x00 MSTP Config.exe): 1. Open the configuration Tool 2. Double click on the BACDOOR icon in the icon tray on the bottom right of the PC. 3. On the window BACDOOR OEM MSTP Client status, click configure and in the configuration window set the Device instance to any number that does not conflict with any other device instance on the network.: 4. Close the BACDOOR configuration window and in the T7000 Device Configurator, click refresh device list. 6. All the devices on the trunk should appear and you can start changing the device instances one after the other. To do that: a. A- Select the first device.     B- Click Connect to device. The connection process can be long, wait for all the objects to be discovered.     C- change the instance ID using the keyboard.     D- click Apply changes. b. Select the next device and do the same. c. Repeat this action for all the discovered devices. 7. After making all the recommended changes, remove the RS-485 to 232 converter and reconnect the network.
View full article
Picard Product_Support
‎2018-09-11 06:13 AM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2022-04-05 06:48 AM

Labels:
  • EcoStruxure Building Expert
  • Field Devices
4365 Views

How to Create TAC Vista Interface to SmartStruxure

Issue How to transfer data from TAC Vista to EBO(EcoStruxure Building Operation) as a temporarily solution while a transition between TAC Vista and EBO is done?    Product Line EcoStruxure Building Operation, TAC Vista Environment TAC Vista SmartStruxure Solution EcoStruxure Web Services TAC Vista SmartStruxure Interface 1.5 Cause If EBO need data from TAC Vista during a transition period the TAC Vista SmartStruxure interface can be used.   Resolution Please see the video or follow the instructions below:   On the Vista server(s) install the TAC Vista SmartStruxure Interface first. Refer to TAC Vista to SmartStruxure Interface will not connect when TAC Vista and SmartStruxure are installed on the same machine if there are any issues installing or getting the two programs to communicate when on the same PC. In StruxureWare Workstation, on the Enterprise server object or the Automation server object right click and create new interface, and select the EcoStruxure Web Service interface in Workstation. Click next. In the Server, enter the IP address of Vista server. If it is local, just use localhost. Enter the username and password of Vista Server. Pay attention that only the user in the default System user group can be used. Don't try to create other System group. And all the letters in the password field need to be in capital letters. This is a defect that will be addressed in the next release of TAC Vista to SmartStruxure interface. Please be selective with the port that you are using. If the Vista to SmartStruxure Interface program is on the same PC as the Enterprise server than a different port other than 80 or 443 will have to be used. Please refer to TAC Vista to SmartStruxure Interface will not connect when TAC Vista and SmartStruxure are installed on the same machine if the two softwares need to be on the same machine. Click Create. The next step is to Host TAC Vista objects into SmartStruxure. Refer to How to host TAC Vista objects using Web Services in StruxureWare Building Operation for the guide of how to host Vista objects into SmartStruxure. NOTE: There is a defect for Version 1.0 of TAC Vista to SmartStruxure interface under Non-English operation system. The EcoStruxure Web Services interface will not come online in SmartStruxure. Refer to TAC Vista to SmartStruxure Interface does not connect in non-English Operation System for solution.
View full article
Picard Product_Support
‎2018-09-11 05:52 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 03:15 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
4334 Views

WorkPlace Tech Tool software does not start and a Windows fatal error box is displayed

Issue When attempting to open the WorkPlace Tech Tool software, a Windows fatal error box is displayed: WptEd has encountered a problem and needs to close. We are sorry for the inconvenience. If you were in the middle of something, the information you were working on might be lost. Please tell Microsoft about this problem. We have created an error report that you can send to help us improve WptEd. We will treat this report as confidential and anonymous. Product Line EcoStruxure Building Operation, TAC IA Series Environment WorkPlace Tech Tool software WorkPlace Tech Editor Cause This problem can occur when you use an unsupported version of Visio, such as Visio 2000, prior to starting WorkPlace Tech Editor. Only Visio 2010 SP1, Visio 2007 SP2, and Visio 2003 SP3 can be used with the WorkPlace Tech Tool or WorkPlace Tech Editor. Resolution In the warning message, click [Don't send]. Close Visio. Open Visio 2010 SP1, Visio 2007 SP2 or Visio 2003 SP3.  This causes Windows to initialize and configure that specific version of Visio. When Visio opens, confirm that the selected version opens.  If the wrong version opens, you may need to repair the installation of the selected version. Close Visio. Restart WorkPlace Tech
View full article
Picard Product_Support
‎2018-09-11 06:29 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
4327 Views

Script error when navigating menu in TGML graphic following upgrade to 1.4

Issue  Script error when navigating menu in TGML graphic in 1.4. Graphic was working fine in 1.3. Product Line EcoStruxure Building Operation Environment Workstation Enterprise Server Automation Server Cause In releases prior to 1.4, graphic objects were not unloaded when navigated away from. This has been fixed in 1.4. As a result of this change, If a TGML has a navigate in a script (by using invoke) this could cause a script error if there are scripts on parent elements. Resolution Open the graphic Navigate to the script and edit, or view in source mode Add evt.stopPropagation(); before the invoke in the Click() function. For an updated version of the component without the error, go to the community: Navigation Menu (JF/Denmark) rev 2.
View full article
Picard Product_Support
‎2018-09-11 02:27 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-09-03 07:38 AM

Labels:
  • EcoStruxure Building Operation
4442 Views

Error displayed when importing a device XIF into SmartStruxure

Issue When importing an XIF into SmartStruxure, errors can be generated that vary in nature. Product Line EcoStruxure Building Operation Environment SmartStruxure Enterprise Server SmartStruxure Automation Server Building Operation Workstation Cause The XIF does not import successfully for a variety of possible reasons: There exists a device template in the server already that contains the same device ID as the XIF that is being imported.  The XIF does not comply with the LonMark Device Interface File Reference Guide published by LonMark. Resolution Before performing any of the steps below: Import the XIF file provided by the manufacturer of the Lon controller - if the manufacturer did not provide a XIF, try searching the LonMark product catalog If the provided XIF does not work, upload the XIF from the device to ensure that it is the correct file by following How to extract an XIF out of a Lon controller. Use the SBO SNVT Support tool found on The Exchange to identify unsupported SNVT's. Work through the troubleshooting steps below.   Device Template Fails without an Error This issue has been seen in some of the older versions of SmartStruxure (1.5 and older) and upgrading to the latest version will resolve the issue in many cases. If the issue occurs at the latest version of SmartStruxure: Use the SBO SNVT Support tool located on The Exchange to identify unsupported SNVTs. If the SBO SNVT Support tool does not identify any unsupported SNVTs, then send the XIF in to Product Support for further investigation.    Device Template Already Exists In order to complete the import of the XIF, follow these steps. Delete all controllers in that database that are using the device template that has the same device ID as the XIF file you are trying to import.  Now import the XIF again. Select the server in the system tree on the left and go to File > LonWorks import > Device Template. Click the Browse button and select the XIF you want to import. Click Import. Note: When the import is complete it will have overridden the old device template with that device ID. Two device templates with the same device ID will not be able to reside in the same database. For more information about device templates see Delete Device Templates.   Detailed Error Prompt with Specific Fields Listed Some examples of the detailed errors include but are not limited too: "Field X has error(s). The string must between X and X characters. nvoActualCapacity has X characters" on row X. "Field X has error(s). The number must between X and X. Field X has value X." on row X. "Field X has error(s). The value must be X but was X." on row X. Space or tab are not allowed in field 0Node Object on row X.   To Address these issues: Download Notepad++ to be able to better navigate the XIF by row number. Using Notepad++, open the XIF. NOTE: Backup the original XIF just in case there is a mistake when modifying. Find the row and field number prompted by the error messages and modify them accordingly. All the rules can be found in LonMark Device Interface File Reference Guide published by LonMark. Import the XIF again to verify whether it works. If not, contact Product Support for further investigation.
View full article
Picard Product_Support
‎2018-09-11 09:41 AM

Last Updated: Administrator CraigEl Administrator ‎2023-09-11 01:40 AM

Labels:
  • EcoStruxure Building Operation
4352 Views

Unresolved BACnet References causing slow startup and configuration performance on Enterprise and Automation Servers

Issue Automation / Enterprise Server configuration very slow Attempting to make any configuration changes in the AS such as creating a new point/value or modifying existing objects is extremely slow. Note: This applies to the ES as well although less of a problem since the ES has better resources than the AS. CPU usage as seen in the Status Information of the server is very high. (above 80%) Question marks are shown on many objects in the application folder of third party BACnet devices that have been uploaded to the AS Enterprise Server takes a long time to startup (15 minutes) before allowing users to log on with Workstation.  Deleting the BACnet Interface allows log on with 2 - 3 minutes on a restart. Product Line EcoStruxure Building Operation Environment Automation Server Enterprise Server BACnet Cause Uploaded BACnet devices contain unresolved references to notification class object(s) Resolution Ask for SE.SBO.ES-AS-1.5.0.1501-Hotfix. (SE.SBO.WS-1.4.1.16001-Hotfix for 1.4.1, there is no hot fix for versions before 1.4.1) After applying the hot fix the server should become responsive. The unresolved references can typically be cleaned up by creating a BACnet Notification object in the application folder of the third party BACnet device proxy that reside in SBO and manually setting the Instance ID to 0 (zero) NOTE: Cases have been seen where multiple notification class objects must be created using instance IDs 0,1,2,3,4 in order to clean up all the unresolved references. A few minutes after the notification class object with the proper instance ID is created the question marks should disappear from the icons and created notification class object will show up in the intrinsic alarm property as seen below.   If creating the notification class objects with the above instance IDs does not resolve all the references a backup of the server can be provided to PSS, a PSS/R&D engineer can look directly at the database to determine the proper instance IDs the unresolved references are looking for.
View full article
Picard Product_Support
‎2018-09-11 10:09 AM

Last Updated: Sisko GavinHe Sisko ‎2022-09-14 06:22 AM

Labels:
  • EcoStruxure Building Operation
4388 Views

Sigma - Advantech touch screen, can this be used as a Sigma server?

Issue Can the Advantech touch screen be used as a Sigma server? Environment Sigma WinCE Advantech Touch screen Panel mounted Cause System has been installed without a Sigma server. Resolution The Advantech touch screen, or any other WinCE device can only be used for general display functions, low level editing, contingency logging review and time updates, it does not have the functionality of a Sigma server. To review the latest Release note, please click HERE. To review the WinCE User guide, please click HERE.
View full article
Picard Product_Support
‎2018-09-10 02:00 AM

Labels:
  • Satchwell BAS & Sigma
4399 Views

Xenta Server (Xenta 5/7/913) serial cable guide

Issue If the Xenta Server IP address is unknown or lost, how can the user retrieve or reset the IP address? Product Line Satchwell MicroNet, TAC INET, TAC Vista Environment Xenta Servers Xenta 511, 527, 555, 701, 711, 721, 731, 913 Cause Once the Xenta Server IP address is lost, the user has to use a serial connection cable to connect the Xenta Server to the HyperTerminal in order to retrieve the IP address. The serial cable is a RS-232 to RJ10 cable which can be purchase from Schneider Electric order entry (Part number: 00730920). For some reason, if the cable need to be home made, please follow the steps below to connect correct pins. Note: some third party IP search/scan software can be used to search all IP addresses in a range. User can also use this type of software to retrieve Xenta Server’s IP addresses. Resolution Xenta Server serial cable guide: Connect RJ10 pin 1 to RS232 pin 2. Connect RJ10 pin 2 to RS232 pin 3. Connect RJ10 pin 4 to RS232 pin 5. Connect RS232 pin 1, 6, 4 together. Refer to IP setup for a Xenta server (Xenta 5/7/9xx) through serial communication for how to set up HyperTerminal in order to retrieve/setup Xenta Server IP address.
View full article
Picard Product_Support
‎2018-09-10 05:15 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 06:38 PM

Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
4358 Views

Backup and Restore MongoDB for Windows for Access Expert On-Premise

Issue Access Expert On-Premise setup needs procedures and tools to backup and restore the database Product Line Access Expert Environment Access Expert Premise Software V3 MongoDB Cause The procedures for backing up and restoring the MongoDB is documented online at the link below. https://docs.mongodb.com/manual/tutorial/backup-and-restore-tools/ However, these instructions do not outline how to use the commands (mongodump and mongorestore) within the Windows OS environment using specific examples. Resolution The following procedures are designed to fill in the gap for Access Expert administrators who need to do manual MongoDB Backup and Restore. These procedures assume that Access Expert V3 has been installed and is functioning normally. You will need 2 separate Command Prompts, run as Administrator, open for these procedures. Mongo DOS Shell to attach to and run commands within MongoDB environment Standard DOS Shell to run the Mongo backup and restore commands MongoDB Backup Ensure MongoDB service is running (Start> Run> services.msc) Open a Command Prompt as Administrator (referred to as the Mongo DOS Shell) Type mongo(command) Type show dbs (command) - shown above, to give a list of the dbs available) If the MongoDB service is "Running," but the client cannot connect when typing mongo, it's probably because the path to the mongo bin folder hasn't been added to the PC's environment. To Add a local path locations variable to a PC environment https://docs.microsoft.com/en-us/previous-versions/office/developer/sharepoint-2010/ee537574(v%3Doffice.14) Ex. C:\Program Files\MongoDB\Server\3.6\bin (This will vary based on the version of Mongo) Open another Command Prompt as Administrator (Standard DOS Shell) Use the CD command to navigate to where you would like the backup files to be created Ex. C:\Data mongodump (command) The mongodump command creates the dump folder with admin, Keep, Signalr subfolders MongoDB Restore In the (Mongo DOS Shell) Prompt show dbs (command) use Keep (command) (Case sensitive) db.dropDatabase() (command) Use the Command Prompt as Administrator (Standard DOS Shell) mongorestore (command) The window should indicate "Finished Restoring Keep.Events," "done" and RESTORE COMPLETE If there are “E11000 duplicate key error collection” Keep.Events errors, it’s because the collection events are already in the folder and need to be deleted first.   Steps to correct the E11000 duplicate issue: (Stop the service, delete and recreate the DB folder, restart service) Right-click on the MongoDB service and Stop (you can’t delete files while the service is running) Delete C:\Data\db folder (not the Data, only DB) MANUALLY CREATE THE DB FOLDER - Right Click > New Folder and name it DB Restart the MongoDB service - this creates the necessary files in the DB folder Once these steps have been done, rerun the mongorestore command mongorestore (command) Verify that users can log into Access Expert with this database
View full article
Picard Product_Support
‎2018-09-10 07:56 AM

Last Updated: Administrator DavidFisher Administrator ‎2023-09-11 01:50 AM

Labels:
  • EcoStruxure Access Expert
4337 Views

How to upgrade a first Generation CX to a Netcontroller 2

Issue What is the process to replace a CX9400 with a CX9680 NC2? Product Line Andover Continuum Environment Upgrading a CX9200, CX9400 Eclipse, CX9900, CX9940 to a NCII Netcontroller. CMX9924. Model Number, Type change. Cause Where can I get the process to upgrade my obsolete CX controller. Resolution Cyberstation V1.74 SP2 or above is required to support the upgrading process of a CX9200, CX9900 and CX9940 up to a Netcontroller 2. The upgrade process for this is detailed in Appendix B or the NetController II Operating and Technical Reference Guide. For the CX9400 Eclipse controller they require a minimum of V1.91 to support the upgrade. For the older versions of Cyberstation that do not support direct upgrading of a model number, you will need to bring the Netcontroller II on line as a new controller, then in offline editing copy /paste (or Drag /Drop) all objects over to the Netcontroller II. Then go online and fully reload the Netcontroller II and any connected Infinet controllers. The old controller can then be deleted from the system. The objects could also be copied over using edited ASCII dump files if you prefer that method, but either way you may still have to re-animate your Pinpoint graphics unless you upgrade to a version that supports the Netcontroller II replacement. NOTE ACC-LON RS-485 and ACC-LON FTT-10A protocol options A CX9900 may be labeled CPU-8M and a CX9940 labeled CPU-4M. Later CX99 models may have FT added, eg. CPU-8M-FT When replacing a CX9900 or CX9940 it is vital to know if it requires an RS485 or FTT10 IOU module port (if this port is being used) as this CANNOT be modified on site. See article titled No response from I/O module when learning in an IOU This process cannot be used to upgrade the CMX9924 controllers.  The available range of Netcontroller II controllers available has recently been reduced, see PA-00535 "Andover Continuum Offer Optimization"
View full article
Picard Product_Support
‎2018-09-10 06:21 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 06:21 PM

Labels:
  • Andover Continuum
4395 Views

Configuring Xenta I/O module inputs when used as stand alone Lonworks devices

Issue Unable to read the Analog Inputs / Universal Inputs values in StruxureWare Building Operation. Product Line EcoStruxure Building Operation Environment Xenta I/O Modules Xenta  421A, 422A, 451A, 452A as standalone LON nodes StruxureWare Building Operation (SmartStruxure) Cause When using the Xenta Input Output modules 421A, 422A, 451A, 452A as stand alone Lonworks node, the UCPTConfiguration must be set to the necessary integer value for the required input, by default the values are set to zero so can not be configured. Resolution Please see the supporting documentation for the TAC Xenta 421A/422A and TAC Xenta 451A/452A that gives each nci value for the needed input type. To configure each input to the correct type please follow these steps: Navigate to the node in your Lonworks network Expand the controller to view all of the inputs, outputs, and configuration properties. Find the Universal Input module for the input you need to configure, and locate the nciInput(x) variable within that module Set the value of Absolute count to one of the following : 1 = 1.8 kohm thermistor 2 = DI with green indication 3 = 0-10 vdc 4 = 0-20 mA 5 = 10 kohm thermistor 6 = DI with red indication 7 = DI with green inverted indication 8 = DI with red inverted indication   Up to SBO Version 1.7.x     SBO Version 1.8.x and on in the "Variable Fields" tab overwrite the string "Min" with for example 6 
View full article
Picard Product_Support
‎2018-09-11 06:06 AM

Labels:
  • EcoStruxure Building Operation
4319 Views

SmartXKiosk PIN Reset

Issue The 6 character PIN for the SmartXKiosk has been forgotten so the user cannot exit Kiosk mode Note the PIN is case sensitive Product Line EcoStruxure Building Operation Environment SmartXKiosk Advanced Display v1 Advanced Display v2 SmartX Controller Cause The 6 characters PIN for the SmartXKiosk has been forgotten or lost and the user cannot locate it. Resolution In order to reset your SmartXKiosk PIN, follow the steps below:   In the SmartXKiosk application, click on Exit Kiosk Mode in the bottom right corner of the screen. In the Exit Kiosk Mode window, click on Forgot PIN?. An 8 characters or 15 characters Session ID will be generated.  Take note of this Session ID.    Open a ticket with Support to request a SmartXKiosk PIN reset and provide them with the Session ID. Once Support sends you back the Recovery PIN, click Continue on the Session ID window. In the next window fill in the Session ID from step 2. and the Recovery PIN that Support has provided. Click Continue. You can now reset your PIN. Enter your new 6-digit PIN number and confirm it before clicking Submit. The PIN is case sensitive. It must be exactly 6 characters, otherwise an error will occur.  Important Note: The Session ID generated and the Recovery PIN provided to you by Support will expire at midnight on the day that the Session ID was generated.   Note: For Advanced Display v3 please see How to recover the password for Advanced Display version 3
View full article
Picard Product_Support
‎2018-09-06 08:45 AM

Last Updated: Sisko GavinHe Sisko ‎2023-10-25 07:48 AM

Labels:
  • EcoStruxure Building Operation
4305 Views

Ethernet port is AutoSensing (No Crossover Cable required)

Issue Need to perform autosensing on an ethernet port but do not have a cross over cable. Product Line Andover Continuum, EcoStruxure Building Operation, TAC INET, TAC Vista Environment Ethernet connection to an Automation Server Xenta device ACX BCX Auto-Sensing, Auto Sensing direct connect Auto uplink and trade Universal Cable Recognition Cause Need to direct connect with a straight through or normal patch cable from a computer or laptop to the AS, Xenta, BCX, ACX  Resolution Since 1998, the distinction between uplink and normal ports and manual selector switches on older hubs and switches are obsolete. If one or both of two connected devices has the automatic MDI/MDI-X configuration feature there is no need for crossover cables. Now you can plug your laptop right into the Ethernet port of the device with just a regular patch cable. 
View full article
Picard Product_Support
‎2018-09-06 03:48 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • TAC INET
  • TAC Vista
4293 Views

Error during the SQL Configuration step for EBO WebReports (v1.8)

Issue The following error is generated during the SQL Configuration step for 1.8 Reports Server Product Line EcoStruxure Building Operation Environment WebReports Installer Cause This can happen for various reasons: Possible cause 1 The Microsoft .NET Framework installation is damaged after installing Microsoft SQL Server. Possible cause 2 In one of the steps during SQL installation, we have to configure NT AUTHORITY\SYSTEM. If user fails to change this and move ahead with default user then create database step would fail. Possible cause 3 The operating system is not using English as its selected language. Resolution Solution 1 Quit the WebReports Installer Package Remove/reinstall or repair .NET Framework 4.5 (Available from Microsoft .NET download site or direct download - WebInstaller - OfflineInstaller) Repeat the installation of WebReports Solution 2 Set the SQL server service log on properties to "Local System" (NT AUTHORITY\SYSTEM) Restart the SQL server service Repeat the installation of WebReports Solution 3 Replace the WebReports OS with an English version of Windows. 
View full article
Picard Product_Support
‎2018-09-11 11:52 AM

Last Updated: Sisko GavinHe Sisko ‎2023-04-25 07:11 AM

Labels:
  • EcoStruxure Building Operation
4274 Views

How to use AutoCAD layout in TGML Graphic Editor 5.1.9 and earlier

Issue How to use AutoCAD layout in TGML Graphic Product Line TAC Vista Environment Vista 5.1.9 and earlier versions of Vista 5 TGML Graphic AutoCAD Cause Sometimes it is necessary to use the AutoCAD layout in TGML graphic, for example, to use the plant layout as a background. The official support for importing AutoCAD files was removed early in the life of TGML. It can’t be guaranteed that EVERY file will import without a problem, so it is an unsupported feature. Resolution The following steps need to be followed: Open the drawing in AutoCAD Save as .DXF Open TGML Editor File Open the .DXF A screen should pop up saying converting DXF to SVG followed by converting SVG to TGML It is recommended to use the "Create path" command in the Object window in TGML for the converted graphic. Because the response speed of the computer will be very slow if used without this action. Note: Line widths and text will be in disorder because they are not imported along with the object. If the DXF file fails to import, here are some steps to try: Move every object in AutoCAD to a single layer Delete all unused layers in AutoCAD "Explode" complex objects in AutoCAD
View full article
Picard Product_Support
‎2018-09-06 01:01 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2022-11-06 06:31 PM

Labels:
  • TAC Vista
4215 Views

EcoStruxure Energy Expert (formally Power Manager) Licensing

Issue After upgrading from EcoStruxure Energy Expert (formerly Power Manager) from version 1.0 to 1.x or newer, the licensing no longer works. Product Line EcoStruxure Building Operation EcoStruxure Energy Expert Environment Energy Expert (formerly Power Manager) License Administrator Power Monitoring Expert Cause There can be some confusion on what licenses are required to run Energy Expert. There are also differences between version 1.0 and 1.x or newer licensing.  Resolution EcoStruxure Energy Expert License In order to use Energy Expert, an Energy Expert license is needed to be purchased before the previous 90-day trail license expires.  The EcoStruxure temporary license (evaluation) is only for EcoStruxure Building Operation software and does not include Energy Expert   It is important to remember that EcoStruxure Building Operation licenses are needed to work along side Energy Expert (e.g. Workstation, Enterprise Server, etc). The EcoStruxure Building Operation licenses need to be activated separately.  How to activate, release and/or transfer a license in EcoStruxure.   Energy Expert Version 2 and 3 Licensing and Upgrading If upgrading from a previous Power Manager 1.x site to Energy Expert 2.x or 3.x a new license(s) will be required. In order to obtain your new license(s), please follow the procedure found in TPA-EBO-19-0001.00 - EcoStruxure Energy Expert v2.0 License Upgrade. (Full support ends 2022 and limited support ends 2024) Energy Expert Part numbers and Licensing The part numbers for version 1.x or newer are listed below. PSWPMNCZZSPEZZ -  Base Energy Expert license PSWDENCZZNPEZZ -  PME license entry range PSWDMNCZZNPEZZ - PME license mid range  PSWSANCZZSPEZZ -  Standard PME. license For a full list of both current date and obsolete part numbers please download the following spreadsheet https://ecoxpert.se.com/pme-digital-power-launch)   Activating a License Full guidance for activation of your licenses can be found on Page 55 of the Energy Expert 3.0 Solution Guide The Energy Expert 3.0 installer and documentation, can also be found here EE 3.0
View full article
Picard Product_Support
‎2020-12-17 05:51 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 10:16 PM

Labels:
  • EcoStruxure Building Operation
4256 Views

Configuration of BACnet Foreign Device Registration

Issue Configuration of BACnet Foreign Device Registration Product Line EcoStruxure Building Operation,  Andover Continuum Environment BACnet IP  BBMD Foreign device Cause  Foreign Devices registration can be confusing Resolution When configuring a Foreign Device Registration on a B/IP BACnet Network. The Foreign Device only needs to register with the one BBMD on its B/IP Network Segment. The BBMD that has the Foreign Device registered with it creates a table called FDT (Foreign Device Table) internally which is different from the BDT(Broadcast Distribution Table) that the BBMD uses to communicate with other BBMDs.   Once the FDT confirms the Foreign Device, it is up to that BBMD to distribute BACnet communications to and from the necessary BBMD's in its BDT. and the all Foreign Devices in its FDT.  In this way the Foreign Devices does NOT perform Broadcasts.
View full article
Picard Product_Support
‎2018-09-06 02:47 PM

Last Updated: Sisko GavinHe Sisko ‎2022-10-10 03:11 AM

Labels:
  • Andover Continuum
4264 Views
  • « Previous
    • 1
    • …
    • 23
    • 24
    • 25
    • …
    • 508
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now