How to upgrade a first Generation CX to a Netcontroller 2

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to upgrade a first Generation CX to a Netcontroller 2
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5964 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to upgrade a first Generation CX to a Netcontroller 2

Picard Product_Support
‎2018-09-10 06:21 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:46 AM

Issue

What is the process to replace a CX9400 with a CX9680 NC2?

Product Line

Andover Continuum

Environment

  • Upgrading a CX9200, CX9400 Eclipse, CX9900, CX9940 to a NCII Netcontroller. CMX9924.
  • Model Number, Type change.

Cause

Where can I get the process to upgrade my obsolete CX controller.

Resolution

Cyberstation V1.74 SP2 or above is required to support the upgrading process of a CX9200, CX9900 and CX9940 up to a Netcontroller 2.

The upgrade process for this is detailed in Appendix B or the NetController II Operating and Technical Reference Guide.

For the CX9400 Eclipse controller they require a minimum of V1.91 to support the upgrade.

For the older versions of Cyberstation that do not support direct upgrading of a model number, you will need to bring the Netcontroller II on line as a new controller, then in offline editing copy /paste (or Drag /Drop) all objects over to the Netcontroller II. Then go online and fully reload the Netcontroller II and any connected Infinet controllers. The old controller can then be deleted from the system.

The objects could also be copied over using edited ASCII dump files if you prefer that method, but either way you may still have to re-animate your Pinpoint graphics unless you upgrade to a version that supports the Netcontroller II replacement.

NOTE
ACC-LON RS-485 and ACC-LON FTT-10A protocol options
A CX9900 may be labeled CPU-8M and a CX9940 labeled CPU-4M. Later CX99 models may have FT added, eg. CPU-8M-FT
When replacing a CX9900 or CX9940 it is vital to know if it requires an RS485 or FTT10 IOU module port (if this port is being used) as this CANNOT be modified on site. See article titled No response from I/O module when learning in an IOU

This process cannot be used to upgrade the CMX9924 controllers. 

The available range of Netcontroller II controllers available has recently been reduced, see PA-00535 "Andover Continuum Offer Optimization"

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 7546
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore