Error displayed when importing a device XIF into SmartStruxure

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Error displayed when importing a device XIF into SmartStruxure
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5159 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Error displayed when importing a device XIF into SmartStruxure

Picard Product_Support
‎2018-09-11 09:41 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:02 AM

Issue

When importing an XIF into SmartStruxure, errors can be generated that vary in nature.

Product Line

EcoStruxure Building Operation

Environment

  • SmartStruxure Enterprise Server

  • SmartStruxure Automation Server

  • Building Operation Workstation

Cause

The XIF does not import successfully for a variety of possible reasons:

  1. There exists a device template in the server already that contains the same device ID as the XIF that is being imported. 

  2. The XIF does not comply with the LonMark Device Interface File Reference Guide published by LonMark.

Resolution

Before performing any of the steps below:

  1. Import the XIF file provided by the manufacturer of the Lon controller - if the manufacturer did not provide a XIF, try searching the LonMark product catalog
  2. If the provided XIF does not work, upload the XIF from the device to ensure that it is the correct file by following How to extract an XIF out of a Lon controller.
  3. Use the SBO SNVT Support tool found on The Exchange to identify unsupported SNVT's.
  4. Work through the troubleshooting steps below.

 


Device Template Fails without an Error

This issue has been seen in some of the older versions of SmartStruxure (1.5 and older) and upgrading to the latest version will resolve the issue in many cases. If the issue occurs at the latest version of SmartStruxure:

  1. Use the SBO SNVT Support tool located on The Exchange to identify unsupported SNVTs.
  2. If the SBO SNVT Support tool does not identify any unsupported SNVTs, then send the XIF in to Product Support for further investigation. 

 


Device Template Already Exists

In order to complete the import of the XIF, follow these steps.

  1. Delete all controllers in that database that are using the device template that has the same device ID as the XIF file you are trying to import. 
  2. Now import the XIF again. Select the server in the system tree on the left and go to File > LonWorks import > Device Template.
  3. Click the Browse button and select the XIF you want to import. Click Import.

Note: When the import is complete it will have overridden the old device template with that device ID. Two device templates with the same device ID will not be able to reside in the same database. For more information about device templates see Delete Device Templates.

 


Detailed Error Prompt with Specific Fields Listed

Some examples of the detailed errors include but are not limited too:

  • "Field X has error(s). The string must between X and X characters. nvoActualCapacity has X characters" on row X.
  • "Field X has error(s). The number must between X and X. Field X has value X." on row X.
  • "Field X has error(s). The value must be X but was X." on row X.
  • Space or tab are not allowed in field 0Node Object on row X.

 

To Address these issues:

  1. Download Notepad++ to be able to better navigate the XIF by row number.
  2. Using Notepad++, open the XIF.
    NOTE: Backup the original XIF just in case there is a mistake when modifying.
  3. Find the row and field number prompted by the error messages and modify them accordingly. All the rules can be found in LonMark Device Interface File Reference Guide published by LonMark.
  4. Import the XIF again to verify whether it works. If not, contact Product Support for further investigation.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
Tags (6)
  • Find more articles tagged with:
  • 16486
  • based
  • commit
  • devices
  • qc25913
  • remove
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore