Migrating PostgreSQL/TimescaleDB (ebo_db)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Migrating PostgreSQL/TimescaleDB (ebo_db)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
5749 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Migrating PostgreSQL/TimescaleDB (ebo_db)

Lieutenant | EcoXpert Master SangKim Lieutenant | EcoXpert Master
‎2022-02-08 01:17 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:50 AM

Issue

How to migrate ebo_db from an old PostgreSQL/TimescaleDB PC to a new PostgreSQL/TimescaleDB PC

Product Line

EcoStruxure Building Operation

Environment

  • PostgreSQL
  • TimescaleDB
  • pgAdmin
  • Building Operation Workstation

Cause

When using External log Storage (the TimescaleDB in PostgreSQL server) in EcoStruxure Building Operation, it is often required to migrate the TimescaleDB (ebo_db) to a new PC or a different HDD due to the hard-disk space issue.  

Resolution

  1. Stop the External Log Storage (TimescaleDB) from all the EBO servers (ES & AS’s).
    1. Using the attached zip file, extract the XML TimescaleDB Search Export and import this to the root location of your server.  
      1. The resulting search results will provide ALL servers' Timescale objects and show the status of the Event and Trend configurations. allowing you to multi-select and change the Event and Trend configuration settings quickly.  Use the CRTL key to only select the relevant servers. Alternatively, follow the steps below to locate these properties manually.   
        Note the Export is for version 3.2.3
    1. Expand the ES Server, expand the System folder, and expand the External Log Storage folder.
    2. Right-click the TimescaleDB and select the Properties.
    3. Disable the Event Configuration & Trend Configuration and save.
    4. Repeat the above operation for all the other servers (AS’s) that are enabled for the External Log Storage.
  1. Create a new database in the destination External Log Storage server PC using the “EBO External Log Storage Installer” tool.
    1. Refer to page 5 “Database Management” section of the “EBO External Log Storage Installer.pdf” document for detail.
  2. Backup the “ebo_db” from the source TimescaleDB server PC using the pgAdmin 4 (refer to https://www.pgadmin.org/docs/pgadmin4/development/backup_dialog.html ), or refer to page 8 “Backup” section of the “EBO External Log Storage Installer.pdf” document for detail.
  3. Copy the DB backup file to the destination TimescaleDB server PC and restore the database using the pgAdmin4 tool (refer to https://www.pgadmin.org/docs/pgadmin4/development/restore_dialog.html ).
    1. DB Restoration may take a couple of minutes to a couple of hours depending on the size of the database.
    2. DB restoration results may show an error caused by pre-existing information in some tables, but it can be ignored.
    3. Once DB restoration is completed, make sure to check the timestamp of the oldest log data and the latest log data to verify the result.
  4. Start the External Log Storage (TimescaleDB) from all the EBO servers (ES & AS’s) using the search provided in Step 1 or manually as follows:
    1. Expand the ES Server, expand the System folder, and expand the External Log Storage folder.
    2. Right-click the TimescaleDB and select the Properties.
    3. Change the Database name, Host address, User name, and Password for the new (destination) External Log Storage server PC
    4. Enable the Event Configuration & Trend Configuration and save.
    5. Repeat the above operation for all the other servers (AS’s) that were disabled in the above step 1.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
TimescaleDB Search.zip
Tags (2)
  • Find more articles tagged with:
  • RobertAndriolo22
  • SangKim22
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore