Configuration of BACnet Foreign Device Registration
  • Configuration of BACnet Foreign Device Registration
  • David_Kendrick
    David_Kendrick
  • BillNeville
    BillNeville
  • sesa119747
    sesa119747
  • Carl_Slack
    Carl_Slack
  • Julio_Cortes
    Julio_Cortes
‎2018-09-06 02:47 PM
Last Updated: Sisko GavinHe Sisko ‎2022-10-10 03:11 AM
EcoStruxure Building Operation,  Andover Continuum
  • BACnet IP
  • BBMD
  • Foreign device
 Foreign Devices registration can be confusing
When configuring a Foreign Device Registration on a B/IP BACnet Network. The Foreign Device only needs to register with the one BBMD on its B/IP Network Segment. The BBMD that has the Foreign Device registered with it creates a table called FDT (Foreign Device Table) internally which is different from the BDT(Broadcast Distribution Table) that the BBMD uses to communicate with other BBMDs.
Once the FDT confirms the Foreign Device, it is up to that BBMD to distribute BACnet communications to and from the necessary BBMD's in its BDT. and the all Foreign Devices in its FDT.  In this way the Foreign Devices does NOT perform Broadcasts.
Tags (2)
  • 3065
  • DavidKendrick22
0% helpful (0/1)