Script error when navigating menu in TGML graphic following upgrade to 1.4
  • Script error when navigating menu in TGML graphic following upgrade to 1.4
‎2018-09-11 02:27 PM
Last Updated: Crewman ContentModerator ‎2025-08-11 04:00 AM
 Script error when navigating menu in TGML graphic in 1.4. Graphic was working fine in 1.3.
  • Workstation
  • Enterprise Server
  • Automation Server
In releases prior to 1.4, graphic objects were not unloaded when navigated away from. This has been fixed in 1.4.
As a result of this change, If a TGML has a navigate in a script (by using invoke) this could cause a script error if there are scripts on parent elements.
  1. Open the graphic
  2. Navigate to the script and edit, or view in source mode
  3. Add evt.stopPropagation(); before the invoke in the Click() function.
For an updated version of the component without the error, go to the community: Navigation Menu (JF/Denmark) rev 2.