Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,838
  • TAC IA Series 1,821
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 325
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 147
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Advisor 12
  • EcoStruxure Building Activate 11
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 68
    • 69
    • 70
    • …
    • 507
  • Next »

Uploading Database files to an MPM (Cloning)

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue How can I clone an MPM? How can I upload config.db to an MPM? Product Line EcoStruxure Building Expert Environment SmartStruxure Lite Multi-Purpose Manager Cause Unable to upload config.db to an MPM Resolution An MPM can be cloned from Building Expert by exporting default.db from one MPM and importing it to another (using the "Export Database" and "import Database" buttons) Note: Allow MPM a few minutes before attempting to access Building Expert. MPM will reboot automatically and install Database files. If it is necessary to clone the system configuration objects as well, refer to the procedure below: This procedure show you how to upload the Database to an MPM. To download a backup of the database, refer to MPM database information. Power up the MPM and ensure either its IP address can be pinged or Building Expert is accessible. In address bar of browser, enter 10.50.80.3/test.html. (assuming IP address of MPM is set to default) In Remote Path field of File Upload section, enter config.db. Click Browse and Navigate to the backup config.db file and select it. Click Submit Query. Wait for {“success”: true} to show before you proceed. Note: Uploading the config.db file first does not cause the MPM to reboot; which is why it is uploaded first On Browser, click to return to previous page. In Remote Path field of File Upload section, enter default.db. Click Browse and Navigate to the backup default.db file and select it. Click Submit Query. Wait for {“success”: true} to show before you proceed. Allow MPM a few minutes before attempting to access Building Expert. MPM will reboot automatically and install Database files. Note: MPM must not powered off during this time In address bar, enter 10.50.80.3 to connect to Building Expert and validate Database upgrade is correct.
View full article
Picard Product_Support
‎2018-09-10 06:57 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:57 PM

Labels:
  • EcoStruxure Building Expert
2110 Views

SER8000 series room controllers communications options

Issue SER8000 series room controllers communications options Environment SER8000 series room controllers Cause Integration to SER8000 room controllers via Modbus is required.  Resolution Currently, the SER8000 series room controllers communications options are Zigbee Pro or BACnet MS/TP. Refer to the SER8300 datasheet.  To communicate on Modbus RS-485, an option would be to use the multi purpose manager (MPM-UN) as a gateway device.    * Updated July 2015 As per Product Annoucement PA-00428, the SE8000 with firmware 1.3 can now act as a Modbus slave using the RS-485 port. 
View full article
Picard Product_Support
‎2018-09-11 06:27 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:49 PM

Labels:
  • EcoStruxure Building Expert
  • Field Devices
4599 Views

Unable to connect to Infinet Roam IO 2 tool using Windows 7 / Update fix

Issue When using the Roam IO 2 tool, you are unable to connect to the controller using the infinet tool, but you can connect using the BACnet tool. Bluetooth has connected fine using both tools. Environment Windows 7 Roam IO 2 Infinet BACnet Cause This issue is due to a firmware mismatch. Resolution There is a new version of the RoamIO tool firmware available,  You must update to this version for the tool to connect correctly. Download the update RoamIO tool here. Using a 3rd party unzip program, Unzip the file. Update the Roam IO 2 tool with the Roam IO 2 connected Using the BACnet RoamIO software, goto tools and then update. Select the update .UPD file you have just downloaded, this will flash upgrade the Roam IO 2 to the latest firmware
View full article
Picard Product_Support
‎2018-09-10 01:38 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:46 PM

Labels:
  • Andover Continuum
2024 Views

VisiSat version 2.1 Build 196 service pack 2

Issue Service Pack 2 provides the following correction: MicroNet VisiSat import file replaces all non-ASCII chars with replacement character( Defect 31467). Fix applied so that the characters are converted correctly.  Fix applied so that points with alarms and trends results in the import file being generated. Product Line Satchwell MicroNet Environment VisiSat 2.1 Build 196 201 Cause Correction of raised defects. Resolution This Service Pack should only be added to VisiSat 2.1.196 or 2.1.200 if service pack 1 has been installed. Note: When installed, the VisiSat 2.1.96 or 200 installation (200 if service pack 1 has been installed), the build number increases to 2.1.201. (due to one of the files in 'Program Files'). VisiSat will still show as Build 2.1.196 in Control Panel - Programs - Programs and Features - Uninstall or change program. Installing VisiSat Service Pack 2 =============================== Shutdown VisiSat and the VisiSat-Server. Run "VisiSat 2.1.196 Service Pack 2.exe". Extract to VisiSat installation root drive. (or extract to another location and move the Satchwell folder, created when extracted to the root of the C: drive). To the question 'Would you like to replace the exiting file', select 'Yes to All' Restart VisiSat. Download VisiSat 2.1 Build 196 Service Pack 2. See VisiSat version 2.1 Build 196 service pack 1 where information on VisiSat 2.1 Build 196 Service Pack 1 can be found and the service pack downloaded.
View full article
Picard Product_Support
‎2018-09-11 04:53 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:45 PM

Labels:
  • Satchwell MicroNet
2154 Views

SSL and Graphical Programming

Issue Issue1: Unable to use some of the function blocks in the Graphical Editor when creating a graphical program. Issue2: Unable to find some of the function blocks in the Graphical Editor Product Line EcoStruxure Building Expert Environment SmartStruxure Lite Multi-Purpose Manager Cause Description of each function block is not available in Building Expert Resolution Resolution 1: A detailed explanation of each function can be found in the StruxureWare Building Expert Graphical Block Programming User Guide. Resolution 2: Upgrade MPM firmware to 2.16
View full article
Picard Product_Support
‎2018-09-11 12:28 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:38 PM

Labels:
  • EcoStruxure Building Expert
1917 Views

Replacing Xenta 400 series I/O Modules With Xenta 400A series I/O Modules

Issue Replacing an older style 400 I/O with 400A series hardware, the Digital Inputs need changed to reflect the newer style of Universal Input. Product Line TAC Vista Environment Xenta 400 I/O Xenta 421, 422, 451, 452 Xenta 421A, 422A, 451A, 452A LonMaker Replace Cause Hardware changes in the Xenta 400 "A" series I/O will not function as a replacement to a non-"A" series without additional changes to Menta and LonMaker. Resolution Part 1- Changes needed within Menta Open the controller’s application (a Menta file). For ES projects, this file should be stored within C:\TAC\Vista\Applications. Note the I/O module that needs to be replaced. A list of I/O modules can be found under the Options menu on the Device Specification page:   Find and record all input points on the I/O module to be replaced. This list is found in the I/O Configuration Table under the Options menu. For example, write the "Name" and "Bound To" address for every point referencing M2.   After you have noted all of the addresses for input points on the I/O module that will be replaced, you can edit the device type for the I/O module to reflect the new type (421A or 451A). Making this change WILL remove all DI mappings (421: X1-X4) and all thermistor mappings (451: B1-B4) affected by the change in module type.   Double-Click on each DI block from the 421 (X#) or on each AI thermistor input block from the 451 (B#) that you are updating to a 421A or 451A.   The following window will appear. Click the Bind button.   Update Menta FOR 421A POINTS: The controller’s DI points are now UI points. Select the Terminal Ref based on the old mapping: X1-U1, X2-U2, X3-U3, X4-U4 After selecting the new Terminal Ref, click the OK button and then the OK button again for the Edit Block window. FOR 451A POINTS: The controller’s thermistor inputs (B#) are now additional Universal Inputs. Select the Terminal Ref based on the old mapping: B1-U5, B2-U6, B3-U7, B4-U8 After selecting the new Terminal Ref, click the OK button and then the OK button again for the Edit Block window. **Repeat step 7 for all affected points on the I/O module you’ve updated. Repeat steps 2-7 for every I/O module that needs to be replaced by a 421A or a 451A. PART II - Integration Within LonMaker locate the controllers that you want to change out for a 421A or 451A   Right click on them one by one, a click "Delete."   Open the Vista System Plug-In. Right click on the controller in which you want to change the .MTA application. Click "Configure."   Click "Browse," and locate the updated .MTA file you saved   Click "NO" when asked if you want to remove the devices   Click "Add and Match"   Click "Apply"   Re-Synchronize LonMaker   Your controllers should now be 421As or 451As
View full article
Picard Product_Support
‎2018-09-07 01:43 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:33 PM

Labels:
  • TAC Vista
2958 Views

How does time sync function in AS-P react with BACnet MSTP devices?

Issue Customers question the time sync function in AS-P for BACnet devices Environment SE8650, Viconic, SBO, AS-P, SmartStruxure, Room Controller, MSTP, 3rd Party BACnet Devices Cause It is important to understand what happens when AS-P or Room Controller lose power. Resolution SE8650 firmware version 1.7.1-56d and SBO 1.9.3.24 were used in the test. The testing was done with the fieldbus speed at both 38400 and 76800 baud. 1. The first test was to confirm AS-P sends out time sync signal 38 minutes after each hour periodically. A review of all the timeSync data packets during the capture reveals that the time sync packets are sent every hour when the time in AS-P is 38 after the hour minutes mark. 2. The second test was to confirm that the AS-P will send out a timeSync data packet if a device comes back online after a power outage. First the time was synchronized between the SE8650 with AS-P. SE8650 was then powered down and the AS-P server time changed so that the times in the two devices would not match.   A review of the time synchronization packets in the packet capture confirms that the AS sends out a time synchronization once the SE8650 is powered and boots up. 3. If the AS-P and SE8650 both lost power the SE8650 will boot up before the AS-P. The AS-P will then sends out a timeSync once the BACnet communication is settled.
View full article
Picard Product_Support
‎2018-09-10 06:31 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:12 PM

Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
2678 Views

Display values/objects from a remote MPM on dashboard of the monitor MPM

Issue Cannot select data points of remote nodes to be references in a graphic on the monitor MPM Environment SmartStruxure Lite Multi-Purpose Manager MPM-VA MPM-UN MPM-GW Cause Feature not built-in Resolution When building dashboards on monitor MPMs, only local points can be used in the graphics. To be able to select points of remote MPMs, The Object_Copy script must be used. The script will copy points from the remote nodes to the monitor and make them local to that monitor MPM. This method can be used in ZigBee, Canbus and UDP networks. For example, to copy a point from each of the remote MPMs to the monitor, the script would have to be modified as follows object_list[1] = {tag = "zone1", source_device = "DEV200", source_point = "AV11", destination_device = "ME", destination_point = "AV1"} object_list[2] = {tag = "zone2", source_device = "DEV300", source_point = "AV22", destination_device = "ME", destination_point = "AV2"} object_list[3] = {tag = "zone3", source_device = "DEV400", source_point = "AV33", destination_device = "ME", destination_point = "AV3"}   Important notes: This script increase the monitor's CPU % usage and increases the traffic on the network. Therefore, depending on the size of the network, it is critical not to use more than a couple of points per remote MPM
View full article
Picard Product_Support
‎2018-09-10 01:55 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:02 PM

Labels:
  • EcoStruxure Building Expert
2483 Views

SE(R)8000 series short and long messages

Issue SE(R)8000 series short and long messages Product Line EcoStruxure Building Expert, EcoStruxure Building Operation Environment SE8000 Series Room Controllers SER8000 Series Room Controllers Ex. Viconics branding VT8000 Series EcoStruxure Building Operation Cause Configuration of the SE(R)8000 series short and long messages Resolution The short and long messages are set via BACnet. Take note that the short and long messages do not hold when power to the SE8000 is turned off. This is because currently, the messages are stored in RAM. The workaround is to change the name (from the AS) and back again then save to get it to display on the unit again. Below is the procedure to change the short and long messages in EcoStruxure Building Operation. Short Message: The Short Message can be written to the SE8000 room controller by populating the "Location" Property with the message   Long Message: The Long Message can be written to the SE8000 room controller by populating the "Description" Property with the message The message however will not get displayed until the "Display Long Screen Message" has been activated. Optional: you can also choose the color of the long message background by changing the "Long Message Background Color".     Discrepancy on the text written to the device, and the text shown on the device In some cases when using non-English characters in the messages, the text on the SE8000 will not be rendered as expected. The issue is caused by SE8300 not conforming to BACnet standard in string encoding and decoding. The workaround is to set "BACnet string encoding" property of the device to "ISO 8859-1(Latin-1)", or other encoding the device supports. SE8300 claims to support BACnet protocol revision 10, which requires the conforming device to interpret Character Set 0 as UTF-8 string. In 1.9, SBO started to write to devices using Character Set 0 for unicode strings, but the SE8300 fails to decode it. Setting the "BACnet string encoding" to Latin-1 for the devices fixes the problem. 
View full article
Picard Product_Support
‎2018-09-11 01:54 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 06:57 PM

Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
2302 Views

Requirements for connecting Pelco's Endura to TAC I/NET Seven

Issue The Pelco Endura system with cameras at a location and integrating with the TAC I/NET Seven system. Product Line TAC INET Environment Check the system requirements for the version of TAC I/NET Seven and Pelco Endura  Cause Configuration requirements of the Pelco Endura and TAC I/NET Seven are specific for the functionality in I/NET. Resolution Once your Pelco Endura system is configured and the Workstation has discovered all the devices and the System Manager is online with the cameras correctly configured, there are four basic requirements to connect TAC I/NET. Cameras have to have a unique friendly name other than default. Cameras have to have a unique camera number. Netframework 3.5 has to be installed. Windows Media Player 11 has to be installed.   If using I/NET Seven Release 2.40a then the following applies: Once INET and the requirements above are installed the Endura Install can be run. The installer for these files is located on the INET CD in the folder: Support\EnduraSDK. Note: Endura video does NOT work on Windows Vista or Windows 7.   If using I/NET Seven Release 2.40 or above: Dual NIC support is now available. For Endura, 100GB NIC and Router are suggested. 1 for I/O Server, 1  for video   Equipment used: NSMS200 Pelco Endura Network System Manager & Network Video Manager SM5000 Pelco Endura System Manager WS5070 Pelco Endura Workstation with Advanced Management Software WS5000 Pelco Endura Work Station Software package NET5301T Pelco Endura Video Encoder Spectra IV Pelco Camera Visit Pelco.com for more information. Click here to view an extended compatibility matrix for Endura and I/NET.
View full article
Picard Product_Support
‎2018-09-07 07:40 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 06:52 PM

Labels:
  • CCTV
  • TAC INET
3350 Views

Security Expert SX-KLCS Touch Keypad cannot be brought online

Issue The SX-KLCS Keypad is offline in the Client and shows ' Keypad 256 error address size' on screen If you attempt to adjust the Keypad Address in the Client it is not even visible Product Line EcoStruxure Security Expert Environment Security Expert SX-KLCS-B, SX-KLCS-W Cause SX-KLCS Keypads are normally delivered brand new to site with a default Keypad Address of 256 which the SP-C controllers cannot use and the Security Expert Client cannot even recognize to change the address via software Resolution The Keypad's address must be manually changed to a value between 1 - 254 using its touch pad. Keypad Address   Please refer to the full SX-KLCS_Security_Expert_Touch_Sense_LCD_Keypad_Installation_Manual from which this extract was taken.   Once the Keypad Address has been set to a value between 1- 254 the Keypad should then be visible to the Client and you should be able to bring it online as usual.       The SX-KLCS Keypad will now display 'Security Expert by Schneider' by default.
View full article
Picard Product_Support
‎2018-09-10 07:46 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 06:46 PM

Labels:
  • EcoStruxure Security Expert
2337 Views

How to latch an output with one input and unlatch with another input.

Issue If one Input is required to activate an Output and another Input to de-activate the Output, this Output can be defined by Input Types. The below is a simple scenario where when the first Input turns ON the Control Output turns ON, when the second Input turns ON the Control Output turns OFF. In this scenario we are activating a Duress alarm when an Input goes on and resetting that Alarm when the reset Input is triggered. Product Line Security Expert Environment Security Expert SP-C Cause Require detailed instructions on how to program a latching duress alarm scenario. Resolution Objects required:   1x Area - "Duress_Area" 2x Input Types - "Duress Enable", "Duress Reset" 2x Inputs - "VI Duress Trigger", "VI Duress Reset" 1x Output - "VO Duress Alarm"   Note: The above object names are what is used in this example, you can set these to whatever you require.     Instructions:   Creating the Area 1. Navigate to Programming > Areas. Add a new area (Duress Area), set the Entry and Exit Delay Times to 0. All other settings can be left default.   Creating the Input Types 1. Navigate to Programming > Input Types. Create a new Input Type (Duress Enable) 2. Set the Control Output to your Output (VO Duress Alarm). 3. Under Options 1 enable Generate Alarms. 4. Under Options 2 enable Activate Control Output on Alarm . 5. Set any other options that may be required. 6. Create a new Input Type (Duress Reset) and redo steps 2 - 5 above except under Options 2 enable Deactivate Control Output On Alarm.   Configuring the Inputs 1. Navigate to Programming > Inputs select the Input (VI Duress Trigger) and set the following: 2. Set the Area to the Dummy Area (Duress_Area) created earlier. 3. Set the Input Type to the Input Type (Duress Enable). 4. select the Input (VI Duress Reset) and set the following: 5. Set the Area to the Dummy Area (Duress_Area) created earlier. 6. Set the Input Type to the Input Type (Duress Reset).   Testing 1. Arm both portions of the Area 2. Activate the Input (VI Duress Trigger) to confirm Alarm is generated and Output Activates. 3. Activate the Input (VI Duress Reset) to confirm Alarm is generated and Output Deactivates. 
View full article
Picard Product_Support
‎2018-09-10 07:20 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 06:38 PM

Labels:
  • EcoStruxure Security Expert
2761 Views

What is the replacement for a Drayton Theta YBL3 Valve Body / Actuator assembly?

Issue The Drayton Theta YBL3 Valve Body / Actuator assembly is to be replaced. Environment Replacement Drayton Actuator Valve YBL3 Cause The Drayton Theta YBL3 Valve Body / Actuator assembly is obsolete. Resolution OVERVIEW The Drayton Theta YBL3 Valve Body / Actuator assembly is obsolete, and there is no purpose built replacement. The Valve Body was available in 1.1/4", 1.1/2" and 2" B.S.P. sizes and was normally installed as a mixing valve in variable temperature, constant volume, compensated heating circuits. No Valve Body / Actuator assemblies are currently available in these sizes. Details of the YB Valve Body may be viewed here.   VALVE BODY REPLACEMENT To replace the YBL3 Valve Body the following is required:- S-E Satchwell MB Valve Body of appropriate size - MB1552 (1.1/4"), MB1602 (1.1/2"), MB1652 (2") Details of the MB Valve Body may be viewed here.   ACTUATOR REPLACEMENT (6-WIRE INSTALLATION) The YBL3 Actuator normally comprised a 6-wire electrical connection enabling it to be operated by a Theta Potentiometric Controller as follows :-  Terminal M1 – Open signal Terminal M2 – Close signal Terminal M3 – Common  Terminal M4 – 135 ohm Feedback Potentiometer – winding Terminal M5 – 135 ohm Feedback Potentiometer – wiper Terminal M6 – 135 ohm Feedback Potentiometer – winding Where 6 wires are connected to the YBL3 Actuator then the Actuator may be replaced by one or other of the following S-E Actuators :- MD10B-24 MD20B-24 (if MD10B-24 not available) Details of the MD10B-24 Actuator may be viewed here Details of the MD20B-24 Actuator may be viewed here. N.B. The YBL3 Actuator may also have included an additional 2-wire electrical connection associated with integral Transfer Switches wired as follows :-  Terminal M7 – M1 made to M7 when YBL3 Fully Closed (24Vac) Terminal M8 – M2 made to M8 when YBL3 Fully Open (24Vac) Where external wiring is connected to YBL3 Transfer Switch Terminals M7 or M8 then an Auxiliary Switch Kit containing two S.P.C.O. Auxiliary Switches should be installed on the MD Actuator. Auxiliary Switch Kit MD-S2 (914-1061-000) Details of the MD-S2 Auxiliary Switch Kit may be viewed here. Where external wiring is connected to YBL3 Terminal M7 then the MD-S2 Auxiliary Switch Kit should be wired as follows :- Terminal S1 (Common) - connect to 24Vac power source Terminal S2 (Normally Closed) - connect to 24Vac device previously connected to YBL3 Terminal M7 Terminal S3 (Normally Open) - no connection necessary Where external wiring is connected to YBL3 Terminal M8 then the MD-S2 Auxiliary Switch Kit should be wired as follows :- Terminal S4 (Common) - connect to independent 24Vac supply Terminal S5 (Normally Closed) - no connection necessary Terminal S6 (Normally Open) - connect to 24Vac device previously connected to YBL3 Terminal M8   LINKAGE KIT A Linkage Kit will also be required in order to enable the MD Actuator to be mounted on the MB Valve Body. Linkage Kit LMD/AR-MB (914-1071-000) Details of the LMD/AR-MB Linkage Kit may be viewed here   IMPORTANT NOTE In such 6-wire installations not only will the YBL3 Valve / Actuator assembly need to be replaced but the associated Theta Potentiometric Controller and its Sensors will also need to be replaced.   CONTROLLER REPLACEMENT The Theta Potentiometric Controller may be replaced by the S-E Satchwell CSC5252 or the CSC5352 Compensator Controller. Details of the CSC Controllers may be viewed here.   SENSOR REPLACEMENT Theta 3-wire Temperature Sensors may be replaced by S-E Satchwell 2-wire Temperature Sensors compatible with the S-E Satchwell CSC 5252 or CSC5352 Compensator Controllers selected from the following as appropriate. Outside Air Temperature Sensor (STO 600) Contact Temperature Sensor (STC 600), or alternatively :- Immersion Temperature Sensor (STP 660) + Sensor Pocket Adaptor (DWA 0001) Room Temperature Sensor (STR 600) – OPTIONAL ONLY Details of the STO 600 Outside Air Temperature Sensor may be viewed here Details of the STC 600 Contact Temperature Sensor may be viewed here. Details of the STP 660 Water Temperature Sensor may be viewed here. Details of the DWA 0001 Sensor Pocket Adaptor may be viewed here. Details of the STR 600 Room Temperature Sensor may be viewed here.   ACTUATOR REPLACEMENT (3-WIRE INSTALLATION) Should only 3 wires be connected to a YBL3 Actuator then the Actuator may be replaced by one or other of the following S-E Actuators :- MD10B-24 MD20B-24 (if MD10B-24 not available) Details of the MD10B-24 Actuator may be viewed here. Details of the MD20B-24 Actuator may be viewed here. N.B. The YBL3 Actuator may also have included an additional 2-wire electrical connection associated with integral Transfer Switches wired as follows :-  Terminal M7 – M1 made to M7 when YBL3 Fully Closed (24Vac) Terminal M8 – M2 made to M8 when YBL3 Fully Open (24Vac) Where external wiring is connected to YBL3 Transfer Switch Terminals M7 or M8 then an Auxiliary Switch Kit containing two S.P.C.O. Auxiliary Switches should be installed on the MD Actuator. Auxiliary Switch Kit MD-S2 (914-1061-000) Details of the MD-S2 Auxiliary Switch Kit may be viewed here Where external wiring is connected to YBL3 Terminal M7 then the MD-S2 Auxiliary Switch Kit should be wired as follows :- Terminal S1 (Common) - connect to 24Vac power source Terminal S2 (Normally Closed) - connect to 24Vac device previously connected to YBL3 Terminal M7 Terminal S3 (Normally Open) - no connection necessary Where external wiring is connected to YBL3 Terminal M8 then the MD-S2 Auxiliary Switch Kit should be wired as follows :- Terminal S4 (Common) - connect to independent 24Vac supply Terminal S5 (Normally Closed) - no connection necessary Terminal S6 (Normally Open) - connect to 24Vac device previously connected to YBL3 Terminal M8   LINKAGE KIT A Linkage Kit will also be required in order to enable the MD Actuator to be mounted on the MB Valve Body. Linkage Kit LMD/AR-MB (914-1071-000) Details of the LMD/AR-MB Linkage Kit may be viewed here In such 3-wire installations the YBL3 Valve / Actuator assembly only will need to be replaced, while any associated Controller and Sensors may be retained.
View full article
Picard Product_Support
‎2018-09-10 03:02 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 06:27 PM

Labels:
  • Field Devices
6265 Views

The device is applicationless, or is not associated with a program record. (Subsystem: NS, #5)

Issue The device is applicationless, or is not associated with a program record. (Subsystem:  NS, #5) The target device does not have a valid application loaded. To correct this problem, right-click on the device and select the "Load" option. Then, if necessary, repeat this operation. The device was discovered to be applicationless, or not associated with a program. If you encounter this error, load the application into the device. For host-based nodes, ensure that the host application is running Product Line Other, TAC Vista Environment LNS LonMaker Vista NL220 Cause Interrupting a download can cause the download to fail and render the controller applicationless.  Also, a corrupt Menta file can sometimes successfully download, but cause the controller to go into an applicationless state. Resolution An application must be downloaded through Menta while directly connected to the controller through the RS-232 serial port.  A blank Menta file with just one PVR is sufficient to restore an application to the controller and allow it to be downloaded; however, downloading the actual Menta file is better because it can expose parsing errors in the Menta file that need to be fixed before downloading it through the System Plug-in again. In some cases, an attempt to direct download can not establish communications to the controller and "timeout". In this event, download a new .mot file to the system using the Download Wizard. Instructions are located in Instructions on how to download an .MOT file into a Xenta Programmable controller. If the Download Wizard  is not able to establish communications with the device, the program should first be cleared using a Xenta Hardware Reset Tool. You can make one by following the instructions located in Xenta Controller Will Not Download / How to Clear the Xenta Application. If the Xenta firmware is older than 3.61, the method to clear the Xenta application is to power cycle the controller 10 consecutive times.
View full article
Picard Product_Support
‎2018-09-07 03:31 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 06:17 PM

Labels:
  • TAC Vista
2378 Views

Consolidated patch files for I/A Series G3 maintenance builds (3.6.406, 3.7.106, 3.8.37 - Updated 07-24-2015)

Issue How do I locate the consolidated patch files (modules) for the I/A Series G3 maintenance builds (3.6.406, 3.7.106, 3.8.37).  Please note:  I/A Series G3 maintenance builds (3.6.407, 3.7.108, and 3.8.41) are now available for download from the Schneider Electric Buildings Download Center and include all updates for the previous builds. Product Line TAC IA Series Environment I/A Series G3 maintenance builds - 3.6.406, 3.7.106, and 3.8.37 Cause Various issues have been resolved in I/A Series G3 however it is difficult to locate the modules individually. Resolution Please note:  New I/A Series G3 maintenance builds (3.6.407, 3.7.108, and 3.8.41) are now available for download from the Schneider Electric Buildings Download Center.  The new builds already include the consolidated patches listed below. Below the latest consolidated patch files for I/A Series G3 maintenance builds 3.6.406, 3.7.106, 3.8.37 are listed.  The files contain updated modules and a set of release notes.  The consolidated patch files are available for download on the Buildings Download Center.  Login to the Schneider Electric Buildings Download Center and enter Consolidated_Patches in the search area or the filename of the zip shown below.  Modules listed in bold have been modified or added since the previous patch. Note: This article will be updated with information to newer patch files as they become available for release. Consolidated_Patches_3.6.406_SE_05272015.zip  ...  Click here for Release Notes alarm 3.6.406.3 bacnet 3.6.406.3 baja 3.6.406.10 bajaui 3.6.406.3 control 3.6.406.1 docMbus 3.6.406.5 driver 3.6.406.1 fox 3.6.406.2 gx 3.6.406.1 kitLon 3.6.406.1 lonworks 3.6.406.5 mbus 3.6.406.5 modbusCore 3.6.406.3 modbusSlave 3.6.406.2 modbusTcp 3.6.406.2 modbusTcpSlave 3.6.406.2 ndedicatedMicros 3.6.406.3 niagaraDriver 3.6.406.3 obix 3.6.406.1 obixDriver 3.6.406.1 opc 3.6.406.1 pdf 3.6.406.1 provisioningNiagara 3.6.406.1 raster 3.6.406.1 report 3.6.406.1 schedule 3.6.406.1 snmp 3.6.406.1 weather 3.6.406.1 web 3.6.406.9 workbench 3.6.406.3 Consolidated_Patches_3.7.106_SE_07242015.zip   ...  Click here for Release Notes alarm 3.7.106.7 alarmOrion 3.7.106.2 bacnet 3.7.106.15 baja 3.7.106.10 bajaScript 3.7.106.1 bajaui 3.7.106.5 control 3.7.106.1 docMbus 3.7.106.5 driver 3.7.106.1 fox 3.7.106.3 gx 3.7.106.2 history 3.7.106.2 hx 3.7.106.2 kitControl 3.7.106.1 kitLon 3.7.106.1 kitPxGraphics 1.0.16 lonworks 3.7.106.5 mbus 3.7.106.5 mobile 3.7.106.1 modbusCore 3.7.106.3 modbusSlave 3.7.106.2 modbusTcp 3.7.106.2 modbusTcpSlave 3.7.106.2 ndedicatedMicros 3.7.106.3 niagaraDriver 3.7.106.5 niagaraLexiconZhcn 3.7.106.6 niagaraVirtual 3.7.106.3 obix 3.7.106.2 obixDriver 3.7.106.5 opc 3.7.106.2 pdf 3.7.106.1 platWifi 3.7.106.1 provisioningNiagara 3.7.106.2 raster 3.7.106.1 report 3.7.106.2 schedule 3.7.106.3 seriesTransform 3.7.106.7 smartTableHx 3.7.106.1 snmp 3.7.106.4 weather 3.7.106.1 web 3.7.106.17 workbench 3.7.106.5       Consolidated_Patches_3.8.37_SE_07242015.zip   ...  Click here for Release Notes alarm 3.8.38.5 bacnet 3.8.38.11 baja 3.8.38.10 bajaui 3.8.38.3 control 3.8.38.1 docMbus 3.8.38.5 driver 3.8.38.1 email 3.8.39 gx 3.8.38.1 history 3.8.38.2 hx 3.8.38.3 kitControl 3.8.38.1 kitLon 3.8.38.1 kitPx 3.8.38.1 kitPxGraphics 1.0.16 lonworks 3.8.38.5 mbus 3.8.38.5 modbusCore 3.8.38.3 modbusSlave 3.8.38.2 modbusTcp 3.8.38.2 modbusTcpSlave 3.8.38.2 nDriver 3.8.38.1 niagaraDriver 3.8.38.1 niagaraVirtual 3.8.38.2 obixDriver 38.38.1 platMstp 3.8.38.9 provisioningNiagara 3.8.38.1 raster 3.8.38.1 report 3.8.38.1 schedule 3.8.38.3 smartTableHx 3.8.38.1 snmp 3.8.38.4 web 3.8.38.11 workbench 3.8.38.5 zwave 3.8.38.1   ********* Previous Release History ********* Consolidated_Patches_3.6.406_SE_09112014.zip  ...  Click here for Release Notes alarm 3.6.406.2 bacnet 3.6.406.3 baja 3.6.406.7 bajaui 3.6.406.2 control 3.6.406.1 driver 3.6.406.1 fox 3.6.406.2 gx 3.6.406.1 lonworks 3.6.406.3 modbusTcp 3.6.406.2 ndedicatedMicros 3.6.406.3 niagaraDriver 3.6.406.3 obix 3.6.406.1 provisioningNiagara 3.6.406.1 raster 3.6.406.1 schedule 3.6.406.1 snmp 3.6.406.1 weather 3.6.406.1 web 3.6.406.6 workbench 3.6.406.2 Consolidated_Patches_3.6.406_SE_11112014.zip  ...  Click here for Release Notes alarm 3.6.406.3 bacnet 3.6.406.3 baja 3.6.406.7 bajaui 3.6.406.2 control 3.6.406.1 driver 3.6.406.1 fox 3.6.406.2 gx 3.6.406.1 lonworks 3.6.406.3 modbusTcp 3.6.406.2 ndedicatedMicros 3.6.406.3 niagaraDriver 3.6.406.3 obix 3.6.406.1 provisioningNiagara 3.6.406.1 raster 3.6.406.1 schedule 3.6.406.1 snmp 3.6.406.1 weather 3.6.406.1 web 3.6.406.6 workbench 3.6.406.2   Consolidated_Patches_3.7.106_SE_09112014.zip   ...  Click here for Release Notes alarm 3.7.106.5 alarmOrion 3.7.106.2 bacnet 3.7.106.13 baja 3.7.106.5 bajaui 3.7.106.4 control 3.7.106.1 driver 3.7.106.1 fox 3.7.106.3 gx 3.7.106.2 history 3.7.106.1 kitControl 3.7.106.1 lonworks 3.7.106.3 modbusTcp 3.7.106.2 ndedicatedMicros 3.7.106.3 niagaraDriver 3.7.106.5 niagaraLexiconZhcn 3.7.106.6 niagaraVirtual 3.7.106.1 obix 3.7.106.2 obixDriver 3.7.106.4 pdf 3.7.106.1 platWifi 3.7.106.1 provisioningNiagara 3.7.106.2 raster 3.7.106.1 report 3.7.106.2 schedule 3.7.106.2 seriesTransform 3.7.106.7 snmp 3.7.106.2 weather 3.7.106.1 web 3.7.106.14 workbench 3.7.106.4 Consolidated_Patches_3.7.106_SE_11112014.zip   ...  Click here for Release Notes alarm 3.7.106.6 alarmOrion 3.7.106.2 bacnet 3.7.106.13 baja 3.7.106.5 bajaui 3.7.106.4 control 3.7.106.1 driver 3.7.106.1 fox 3.7.106.3 gx 3.7.106.2 history 3.7.106.1 kitControl 3.7.106.1 lonworks 3.7.106.3 modbusTcp 3.7.106.2 ndedicatedMicros 3.7.106.3 niagaraDriver 3.7.106.5 niagaraLexiconZhcn 3.7.106.6 niagaraVirtual 3.7.106.1 obix 3.7.106.2 obixDriver 3.7.106.4 pdf 3.7.106.1 platWifi 3.7.106.1 provisioningNiagara 3.7.106.2 raster 3.7.106.1 report 3.7.106.2 schedule 3.7.106.2 seriesTransform 3.7.106.7 snmp 3.7.106.2 weather 3.7.106.1 web 3.7.106.14 workbench 3.7.106.4 Consolidated_Patches_3.7.106_SE_01222015.zip   ...  Click here for Release Notes alarm 3.7.106.6 alarmOrion 3.7.106.2 bacnet 3.7.106.14 baja 3.7.106.8 bajaui 3.7.106.5 control 3.7.106.1 driver 3.7.106.1 fox 3.7.106.3 gx 3.7.106.2 history 3.7.106.1 hx 3.7.106.2 kitControl 3.7.106.1 kitPxGraphics 1.0.16 lonworks 3.7.106.3 mbus 3.7.106.4 modbusCore 3.7.106.1 modbusTcp 3.7.106.2 ndedicatedMicros 3.7.106.3 niagaraDriver 3.7.106.5 niagaraLexiconZhcn 3.7.106.6 niagaraVirtual 3.7.106.3 obix 3.7.106.2 obixDriver 3.7.106.5 pdf 3.7.106.1 platWifi 3.7.106.1 provisioningNiagara 3.7.106.2 raster 3.7.106.1 report 3.7.106.2 schedule 3.7.106.2 seriesTransform 3.7.106.7 snmp 3.7.106.3 weather 3.7.106.1 web 3.7.106.16 workbench 3.7.106.5   Consolidated_Patches_3.7.106_SE_05272015.zip   ...  Click here for Release Notes alarm 3.7.106.7 alarmOrion 3.7.106.2 bacnet 3.7.106.15 baja 3.7.106.9 bajaScript 3.7.106.1 bajaui 3.7.106.5 control 3.7.106.1 docMbus 3.7.106.5 driver 3.7.106.1 fox 3.7.106.3 gx 3.7.106.2 history 3.7.106.2 hx 3.7.106.2 kitControl 3.7.106.1 kitLon 3.7.106.1 kitPxGraphics 1.0.16 lonworks 3.7.106.5 mbus 3.7.106.5 mobile 3.7.106.1 modbusCore 3.7.106.3 modbusSlave 3.7.106.2 modbusTcp 3.7.106.2 modbusTcpSlave 3.7.106.2 ndedicatedMicros 3.7.106.3 niagaraDriver 3.7.106.5 niagaraLexiconZhcn 3.7.106.6 niagaraVirtual 3.7.106.3 obix 3.7.106.2 obixDriver 3.7.106.5 opc 3.7.106.2 pdf 3.7.106.1 platWifi 3.7.106.1 provisioningNiagara 3.7.106.2 raster 3.7.106.1 report 3.7.106.2 schedule 3.7.106.2 seriesTransform 3.7.106.7 smartTableHx 3.7.106.1 snmp 3.7.106.4 weather 3.7.106.1 web 3.7.106.17 workbench 3.7.106.5         Consolidated_Patches_3.8.37_SE_09112014.zip   ...  Click here for Release Notes alarm 3.8.38.2 bacnet 3.8.38.3 baja 3.8.38.2 bajaui 3.8.38.1 control 3.8.38.1 driver 3.8.38.1 gx 3.8.38.1 kitControl 3.8.38.1 lonworks 3.8.38.3 modbusTcp 3.8.38.2 platMstp 3.8.38.6 raster 3.8.38.1 report 3.8.38.1 schedule 3.8.38.1 snmp 3.8.38.2 web 3.8.38.3 workbench 3.8.38.1 zwave 3.8.38.1     Consolidated_Patches_3.8.37_SE_10012014.zip   ...  Click here for Release Notes alarm 3.8.38.2 bacnet 3.8.38.3 baja 3.8.38.2 bajaui 3.8.38.1 control 3.8.38.1 driver 3.8.38.1 gx 3.8.38.1 kitControl 3.8.38.1 lonworks 3.8.38.3 modbusTcp 3.8.38.2 platMstp 3.8.38.8 raster 3.8.38.1 report 3.8.38.1 schedule 3.8.38.1 snmp 3.8.38.2 web 3.8.38.3 workbench 3.8.38.1 zwave 3.8.38.1       Consolidated_Patches_3.8.37_SE_11112014.zip   ...  Click here for Release Notes alarm 3.8.38.4 bacnet 3.8.38.6 baja 3.8.38.2 bajaui 3.8.38.1 control 3.8.38.1 driver 3.8.38.1 gx 3.8.38.1 kitControl 3.8.38.1 lonworks 3.8.38.3 modbusTcp 3.8.38.2 platMstp 3.8.38.8 raster 3.8.38.1 report 3.8.38.1 schedule 3.8.38.1 snmp 3.8.38.2 web 3.8.38.3 workbench 3.8.38.1 zwave 3.8.38.1     Consolidated_Patches_3.8.37_SE_01222015.zip   ...  Click here for Release Notes alarm 3.8.38.4 bacnet 3.8.38.9 baja 3.8.38.6 bajaui 3.8.38.2 control 3.8.38.1 driver 3.8.38.1 gx 3.8.38.1 hx 3.8.38.3 kitControl 3.8.38.1 kitPxGraphics 1.0.16 lonworks 3.8.38.3 mbus 3.8.38.4 modbusCore 3.8.38.1 modbusTcp 3.8.38.2 nDriver 3.8.38.1 niagaraVirtual 3.8.38.2 obixDriver 38.38.1 platMstp 3.8.38.8 raster 3.8.38.1 report 3.8.38.1 schedule 3.8.38.1 snmp 3.8.38.3 web 3.8.38.7 workbench 3.8.38.2 zwave 3.8.38.1 Consolidated_Patches_3.8.37_SE_05272015.zip   ...  Click here for Release Notes alarm 3.8.38.5 bacnet 3.8.38.11 baja 3.8.38.9 bajaui 3.8.38.3 control 3.8.38.1 docMbus 3.8.38.5 driver 3.8.38.1 email 3.8.38.1 gx 3.8.38.1 history 3.8.38.2 hx 3.8.38.3 kitControl 3.8.38.1 kitLon 3.8.38.1 kitPx 3.8.38.1 kitPxGraphics 1.0.16 lonworks 3.8.38.5 mbus 3.8.38.5 modbusCore 3.8.38.3 modbusSlave 3.8.38.2 modbusTcp 3.8.38.2 modbusTcpSlave 3.8.38.2 nDriver 3.8.38.1 niagaraDriver 3.8.38.1 niagaraVirtual 3.8.38.2 obixDriver 38.38.1 platMstp 3.8.38.9 provisioningNiagara 3.8.38.1 raster 3.8.38.1 report 3.8.38.1 schedule 3.8.38.2 smartTableHx 3.8.38.1 snmp 3.8.38.4 web 3.8.38.10 workbench 3.8.38.4 zwave 3.8.38.1 bajaui 3.8.38.2 bajaui 3.8.38.2 baja 3.8.38.6 baja 3.8.38.6               obixDriver 3.7.106.4 alarm 3.7.106.5 alarm 3.7.106.5 alarmOrion 3.7.106.2 hx 3.8.38.3 hx 3.8.38.3 hx 3.8.38.3   gx 3.8.38.1 gx 3.8.38.1 gx 3.8.38.1   hx 3.8.38.3   kitLon 3.8.38.1 kitLon 3.8.38.1   nDriver 3.8.38.1   nDriver 3.8.38.1
View full article
Picard Product_Support
‎2018-09-06 09:28 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 06:12 PM

Labels:
  • TAC IA Series
4283 Views

Alarm Email notifications with a 3rd party mail account (SMTP)

Issue Email notifications from 3rd party email account such as Gmail, Hotmail, Yahoo SMTP issues Event notification Product Line EcoStruxure Building Operation Environment StruxureWare Building Operation site with any of the following: AS, ES, Reports Server Cause Sending notifications to Gmail, Yahoo mail, Hotmail, or other outside email account. Wanting to use other SMTP than Schneider Electric E-mail Server: if wanting to setup an ES or AS to send email notifications with third party SMTP, an Exchange server using port 25 supports the notifications. In release 1.7.1 and earlier though Gmail, for example, suggests port 465 and 587, the workstations alarms that the email can not be sent since it cannot connect to email server. The problem is with the Gmail-account and often other 3rd party email providers both public and private, Google requires that you connect with SSL, which have been missing in the requirements and therefore these releases do not have this functionality. In release 1.8.1 and later, you can send emails not encrypted or encrypted using either the TSL or the SSL protocol. You can select one method for the primary email server and another method for the secondary email server. The Schneider Electric Email Server does not support encrypted emails. When logging on to the email server, the user is authenticated using an authentication protocol. If no user name is specified, no authentication protocol is specified. If a user name is specified, the SmartStruxure server tries to authorize the user using the CRAM-MD5 protocol. If the first authentication fails, the SmartStruxure server tries to authorize the user using the LOGIN protocol using the CRAM-MD5 protocol. Resolution In Email Notification put the 3rd party email address such as yourname@mailprovider.com. AS and ES will use the Schneider Electric SMTP server or the POP server of your choice to send the email notification. For multiple emails, check Multiple Email Addresses for Email Notifications or Alarm Recipients. Sometimes the mail is put in the Spam folder for the recipient. Check there and change settings to Not Spam. Installing a valid SSL certificate for the Enterprise Server to allow SSL operation is not planned in a future version. Currently, the default certificate does not identify the system and is not trusted, but nevertheless enables SSL operation. ESMTP (Extended) is not supported through current release. Base64 SMTP authentication is not supported. Wanting to use SMTP other than Schneider Electric E-mail Server: An Exchange server or SMTP server which supports POP and uses port 25 supports AS and ES Notifications. Other servers which would require the setting of Primary/Secondary E-mail server fails to login to SMTP Server require an encrypted (SSL/TLS) connection which is not supported in Struxureware Building Operation versions up to and including 1.7.1. A solution is to use an SMTP proxy on the ES or another computer on the network that will handle the TLS/SSL authentication. Release 1.8.1 and later support TLS and SSL for email authentication natively. Using SmtpProxy on an Enterprise Server SmtpProxy is a small freeware application that listens on a port you choose; the default port is 25. When SmtpProxy detects a connection on this port, it does the following: Connects to the SMTP server you configure (GMail / Microsoft Live Mail / any other SMTP server) Starts an encrypted connection with the SMTP server Returns the connection information to the ES After the initial connection is established, SmtpProxy acts as a middleman. Any SMTP data received from the ES is forwarded to the SMTP server and any data returned from the SMTP server is sent the ES. SmptProxy runs as a Windows service so it can be installed on a LAN server and used by multiple devices such as AS. Note that SmtpProxy does NOT login to the SMTP server but rather credentials are passed through from the ES or AS. Note: SmtpProxy is a third party application and therefore no support is provided by Schneider Electric. Installing SmtpProxy SMTPProxy can be downloaded from http://smtpproxy.codeplex.com/ The download is a Windows Installer (MSI) file that can be used to install SmtpProxy on any machine that supports the .NET Framework v4 – Client Profile. Configuring SMTPProxy for Gmail SmtpProxy is configured using a config file. A sample config file is installed with SmtpProxy, this is a plain text file that can be edited with Notepad. Create a copy of the sample config file and rename it to: On 32 bit machines: C:\Program Files\SmtpProxy\SmtpProxy.exe.config On 64 bit machines: C:\Program Files (x86)\SmtpProxy\SmtpProxy.exe.config The following items can be configured with SmtpProxy’s config file: SmtpProxy can write a log of all its activities. The default file to write the log file to is SmtpProxy.trace.log. SmtpProxy can log several different types of activities. You can control what is written to the log file by setting the log switches. By default, they are set to Off so nothing is written to the log file. Valid switch values are Off, Error, Warning, Info, and Verbose with each one providing more information than the last. Once you have SmtpProxy working, you should turn logging Off. The Url to the SMTP server. Default is smtp.live.com. The SMTP server port. Default is 587. The port to listen on. Default is 25. Scroll to the end of the config file and locate the section SmtpProxy.Properties.Settings section and find the string mail.live.com Edit this to smtp.gmail.com After modification, you must restart the Smtp Proxy service from the services control panel for the new settings to take effect. Configuring ES to use SmtpProxy Right click on the Server in the tree and select Properties then click the Email tab Select Primary/Secondary E-Mail Server Enter Sender E-mail (e.g. Mysite@gmail.com) Under Primary E-Mail Server Settings enter Host: localhost (or 127.0.0.1) Enter the users account information. User name: e.g. gmailaccountname@gmail.com Password: MyPassword Confirm: MyP
View full article
Picard Product_Support
‎2018-09-10 05:06 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 05:17 PM

Labels:
  • EcoStruxure Building Operation
16986 Views

Security Expert Client crashes when browsing to the Status Page Editor

Issue Security Expert Client crashes when attempting to browse to the Status Page Editor. Unable to create Status Pages for system monitoring. When viewing Status Pages none are shown and the word "Frame" is displayed in the view. Product Line EcoStruxure Security Expert Environment Security Expert Client Status Pages Cause The problem is due to the site database not containing the default id=0 objects.  As there is no id=0 Status Page for your site, the Client crashes when browsing to Monitoring | Setup | Status Page Editor.  This can occur when the original 'default controller' is not created during initial Site configuration. A number of default objects are also created as well as the first controller. If you look at the site database, you will also find that it does not contain any id=0 Event Filters or Actions which means that no events will be logged either. Status Page Resolution There are two options to resolve these missing default records: Start with a new Security Expert database and ensure that when creating your Site that the first 'default controller' is created with the Controller Wizard (when prompted). At the end of this process, the default id=0 site objects will also be created. Raise a case with Product Support to arrange for a remote connection.  PSS engineers will then attempt to create the missing id=0 records retrospectively. The site's SSN may need to be provided.. 
View full article
Kirk AdamSteele Kirk
‎2021-04-12 03:08 PM

Last Updated: Admiral David_Kendrick Admiral ‎2022-08-11 06:43 AM

Labels:
  • EcoStruxure Security Expert
1192 Views

SE8600 / SE7000 Room Controller's occupancy command does not follow the MPM's schedule

Issue We cannot get a SE8000 / SE7000 Room Controller’s occupancy command to follow the MPM’s schedule.   The controller’s display always displays unoccupied even when the schedule is set to occupied.    Product Line EcoStruxure Building Operation, EcoStruxure Building Expert Environment Building Operation Workstation Building Operation Automation Server SSL SE8000 SSL SE7000 SSL MPM Cause When the MPM's scheduler is in "unoccupied" mode (outside business hours), the default value is 0. However, that does not match any of the values of the "Occupancy cmd" parameter in the Room Controller Resolution The "Default Value" in the MPM's Scheduler object SCH1 must be changed to "3" to match the unoccupied value in the Room Controller. The Occupancy command point for each Room controller must also be ticked in the points list in the Scheduler object For SE8000 PIR ready models, set the "Occupancy src" (Occupancy Source) parameter to "Motion" The SE8000 /SE7000 Room Controller will now follow the MPM’s schedule.
View full article
Picard Product_Support
‎2018-09-11 08:55 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 03:02 AM

Labels:
  • EcoStruxure Building Expert
2357 Views

TSI Pressura RPM20 Hospital Room Pressure Monitors generate Modbus read errors

Issue Although data is read correctly from the TSI Pressura RPM20 Hospital Room Pressure Monitor when integrated to a SmartStruxure Solution Automation Server, Modbus read errors and framing errors are seen. Product Line EcoStruxure Building Operation Environment SmartStruxure Solution Automation Server SmartStruxure Solution Automation Server Premium Modbus RTU Cause The instruction manual from the manufacturer incorrectly lists  the Modbus communication parameters for the RPM20 as 9600 baud, 8 data bits, 2 stop bits and no parity. Resolution Investigation of the data from the device shows that the Modbus communications parameters are: 9600 baud 8 data bits 1 stop bit No parity Ensure that these parameters are set in the Automation Server Modbus Master Network configuration.
View full article
Picard Product_Support
‎2018-09-11 12:57 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 02:58 AM

Labels:
  • EcoStruxure Building Operation
2370 Views

What is the replacement for a Drayton Theta YBL1 Valve Body / Actuator assembly?

Issue The Drayton Theta YBL1 Valve Body / Actuator assembly is to be replaced. Environment Replacement Drayton Actuator Valve YBL1 Cause The Drayton Theta YBL1 Valve Body / Actuator assembly is obsolete. Resolution OVERVIEW The Drayton Theta YBL1 Valve Body / Actuator assembly is obsolete, and there is no purpose built replacement. The Valve Body was available in 1.1/4", 1.1/2" and 2" B.S.P. sizes and was normally installed as a mixing valve in variable temperature, constant volume, compensated heating circuits. No Valve Body / Actuator assemblies are currently available in these sizes. Details of the YB Valve Body may be viewed here.   VALVE BODY REPLACEMENT To replace the YBL1 Valve Body the following is required:- S-E SatchwellMB Valve Body of appropriate size - MB1552 (1.1/4"), MB1602 (1.1/2"), MB1652 (2") Details of the MB Valve Body may be viewed here.   ACTUATOR REPLACEMENT (6-WIRE INSTALLATION) The YBL1 Actuator normally comprised a 6-wire electrical connection enabling it to be operated by a Theta Potentiometric Controller as follows :-  Terminal M1 – Open signal Terminal M2 – Close signal Terminal M3 – Common  Terminal M4 – 135 ohm Feedback Potentiometer – winding Terminal M5 – 135 ohm Feedback Potentiometer – wiper Terminal M6 – 135 ohm Feedback Potentiometer – winding Where 6 wires are connected to the YBL1 Actuator then the Actuator may be replaced by one or other of the following S-E Actuators :- MD10B-24 MD20B-24 (if MD10B-24 not available) Details of the MD10B-24 Actuator may be viewed here. Details of the MD20B-24 Actuator may be viewed here.   LINKAGE KIT A Linkage Kit will also be required in order to enable the MD Actuator to be mounted on the MB Valve Body. Linkage Kit LMD/AR-MB (914-1071-000) Details of the LMD/AR-MB Linkage Kit may be viewed here   IMPORTANT NOTE In such 6-wire installations not only will the YBL1 Valve / Actuator assembly need to be replaced but the associated Theta Potentiometric Controller and its Sensors will also need to be replaced.   CONTROLLER REPLACEMENT The Theta Potentiometric Controller may be replaced by the S-E Satchwell CSC5252 or the CSC5352 Compensator Controller. Details of the CSC Controllers may be viewed here.   SENSOR REPLACEMENT Theta 3-wire Temperature Sensors may be replaced by S-E Satchwell 2-wire Temperature Sensors compatible with the S-E Satchwell CSC 5252 or CSC5352 Compensator Controllers selected from the following as appropriate. Outside Air Temperature Sensor (STO 600) Contact Temperature Sensor (STC 600), or alternatively :- Immersion Temperature Sensor (STP 660) + Sensor Pocket Adaptor (DWA 0001) Room Temperature Sensor (STR 600) – OPTIONAL ONLY Details of the STO 600 Outside Air Temperature Sensor may be viewed here. Details of the STC 600 Contact Temperature Sensor may be viewed here. Details of the STP 660 Water Temperature Sensor may be viewed here. Details of the DWA 0001 Sensor Pocket Adaptor may be viewed here. Details of the STR 600 Room Temperature Sensor may be viewed here.   N.B. ACTUATOR REPLACEMENT (3-WIRE INSTALLATION) Should only 3 wires be connected to a YBL1 Actuator then the Actuator may be replaced by one or other of the following S-E Actuators :- MD10B-24 MD20B-24 (if MD10B-24 not available) Details of the MD10B-24 Actuator may be viewed here. Details of the MD20B-24 Actuator may be viewed here.   LINKAGE KIT A Linkage Kit will also be required in order to enable the MD Actuator to be mounted on the MB Valve Body. Linkage Kit LMD/AR-MB (914-1071-000) Details of the LMD/AR-MB Linkage Kit may be viewed here In such 3-wire installations the YBL1 Valve / Actuator assembly only will need to be replaced, while any associated Controller and Sensors may be retained.
View full article
Picard Product_Support
‎2018-09-10 12:13 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 02:17 AM

Labels:
  • Field Devices
4258 Views
  • « Previous
    • 1
    • …
    • 68
    • 69
    • 70
    • …
    • 507
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of