Creating elevator controls

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Creating elevator controls
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood
  • Cody_Failinger
    Cody_Failinger
  • Roger_Bently
    Roger_Bently
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2398 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Creating elevator controls

Picard Product_Support
‎2018-09-10 01:02 PM

Last Updated: Administrator CraigEl Administrator ‎2022-11-28 04:22 PM

Issue

How to set up a controller for Elevator Controls.

Product Line

EcoStruxure Access Expert

Environment

Win Server 2012 and above

Cause

Steps to configure Elevator Controls from the beginning.

Resolution

To achieve this the following steps need to be followed:

  1. Open Access Expert
  2. Click on the main controller (SSC)
  3. Add interface - MR16 Out
  4. Set the address of the interface (dip-switches 1-5 on the panel)
  5. Add Reader interface and name accordingly (Elv Flr 1) for example
  6. Select the Elevator Tab and make the appropriate selections
  7. Go to the Elevator Tab
  8. Associate the MR16 Out (Floor Relays)
  9. Set Floor Relays (1 through 16)
  10. Create an Elevator Access Level - this would be used for floors that have access to this level
  11. An Elevator Override Access Level can be created as well if an Unlock Schedule is required
  12. Create the Door Group and assign the necessary  reader or readers
  13. Go to General Configuration and select the System Settings
  14. Select the Hardware Tab
  15. On the Elevator settings, change the Elevator Relay  Time and Elevator Push Button times from 1 to 5 seconds
  16. Once configured, select the elevator reader, right click and choose the Pulse option to test the relays
  17. If correct, the assigned readers will Pulse
  18. Assign users to the Elevator individually or through the User List.

 

Note: Please keep in mind that if there are multiple readers for multiple floors, it is best that a reader be associated with its own MR16 Out, it is best practice as the relays cannot be shared between the readers. Meaning that if Reader 1 uses relays 1-8 the second reader would not be able to use 9-16 on that same MR 16 Out. It would need its own MR16 out for those floors.

Note 2: When creating Elevators in Access Expert, the outputs used on the MR16Out should not be added as an Output once defined in the Reader. These are automatically assigned, if they are added then the Floor selections will not function properly. 

Labels (1)
Labels:
  • EcoStruxure Access Expert
Tags (2)
  • Find more articles tagged with:
  • 19016
  • AlanWood22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore