Configuring and Adding Mercury Intelligent IP Controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Configuring and Adding Mercury Intelligent IP Controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1604 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configuring and Adding Mercury Intelligent IP Controllers

Admiral Alan_Wood Admiral
‎2022-11-28 05:00 PM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:33 AM

Issue

What steps are needed to configure and add Mercury Intelligent IP Controllers to Access Expert

Product Line

EcoStruxure Access Expert

Environment

Access Expert Hosted V3

Warning

Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source.

Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

Instruction steps are needed to configure and add Mercury Intelligent IP Controllers to Access Expert

Resolution

Overview

Intelligent Controllers synchronize with Access Expert in real time, but all access decisions are made locally and independently from the server. This means that the processing of events, actions, and alarms remains local and functional even if network connectivity is lost.

Configuring a Controller for IP Client

  1. Power the controller with an external power supply or by PoE and connect the controller via Ethernet cable to the network. Make sure all DIP switches are set to the off position.
  2. Enter the IP address of the controller in the web address bar of Microsoft Edge or Internet Explorer.
  3. Set DIP switch 1 to the ON position to leverage the default username and password. Log into the controller within 5 minutes of setting DIP switch 1 to the ON position with these default credentials. Username: admin Password: password
  4. From the menu located at the left of the configuration manager page, click on the ‘Network’ button to visit the network settings page
  5. Ensure ‘Use the following DNS server address is checked and enter 8.8.8.8. This is a Google DNS server. We recommend utilizing this to maintain the best operation.1501ConfigMgrNetwork.png
  6. Click on the Accept button in the ‘Network Settings’ page to save changes.
  7. Navigate to the menu and select the ‘Host Comm’ to open the page.
  8. Ensure the Primary Host Port is configured as follows. It should be noted the Alternate Host Port must be disabled:
    • Communication Address: 0.
    • Use IPv6: Unchecked.
    • Connection Type: IP Client.
    • Data Security: TLS if Available.
    • Host IP/Host Name: connect.feenics.com.
    • Port Number: 3001.
    • Connection Mode: Continuous.
    • Retry Interval: 20sec

    1501ConfigHostComm.png

  9. Click on the ‘Accept’ button in the ‘Host communication’ page to save changes.
  10. Navigate once again to the menu and select ‘Apply Settings’ to open the page.
  11. Click ‘Apply setting, Reboot’ (located at the top of the page). If a warning page appears, check both the ‘I understand' and 'wish to proceed’ boxes. Click 'Yes' to apply the changes and allow the controller to reboot.



Adding Controllers to Access Expert

Controllers are added to Feenics from the Hardware Provisioning tab. When adding a controller, you will need to select the controller type from the drop-down list. If the controller you are trying to add does not match one of the types listed, Access Expert does not support it.
IP ControllerList.png
When adding a controller, a name must be given to identify the controller and the UNIQUE MAC address of the controller. The MAC address is used to identify the controller within the Feenics system. Duplicate MAC addresses will not be allowed.   When adding a controller, the MAC address is optional. If no MAC address is provided, the controller will be marked as disabled upon save. The controller can only be enabled by providing a valid MAC address.   

Steps to add an IP Controller to Access Expert

  1. Select the ‘Hardware Provisioning’ Tab
  2. Click “Add Controller” and select your device type
  3. Enter a Display Name
  4. Enter the MAC Address in the correct format: “XX:XX:XX:XX:XX:XX”
  5. Select the time zone (This sets the Controller Time)
  6. (OPTIONAL) Assign Card Formats as needed (Can be added later)
  7. (OPTIONAL) Add Custom EOL Tables 8. Click “Save” or “Save & Close” ControllerAdded.png
    The Port configurations will be grayed out initially until you commission Interfaces and Downstream Devices. At that point, the port configuration section will automatically be configured. Baud Rate is configurable but all devices on the bus must share a baud rate.
    ***Important Note: It is important to choose the correct controller type when adding a new controller.
     
Labels (1)
Labels:
  • EcoStruxure Access Expert
Tags (6)
  • Find more articles tagged with:
  • Access Expert
  • adding
  • AlanWood22
  • configure
  • controllers
  • ip
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore