Access Expert Upstream Mercury Bulk Erase (Factory Reset)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Access Expert Upstream Mercury Bulk Erase (Factory Reset)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1531 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Access Expert Upstream Mercury Bulk Erase (Factory Reset)

Admiral Alan_Wood Admiral
‎2022-11-15 03:13 PM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:33 AM

Issue

Instructions needed to perform a Factory Reset for Upstream Mercury Controllers

Product Line

EcoStruxure Access Expert

Environment

Access Expert software Hosted V3

Warning

Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source.

Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

Instruction steps are needed to reset Upstream Mercury controllers to Factory Default settings

Resolution

Bulk Erase Configuration Memory:

The bulk erase function can be used for the following purposes:

  • Erase all configuration and cardholder database (sanitize board)
  • Update OEM default parameters after OEM code has been changed
  • Recover from database corruption causing the board to continuously reboot

 

Bulk Erase Steps (Factory Reset):


Do not remove power during steps 1-8

 

  1. Set S1 DIP switches to: 1 & 2 "ON", 3 & 4 "OFF" (see DIP switch location and diagram below)
  2. Apply power to the board
  3. Watch for LEDs 1 & 2 and 3 & 4 to alternately flash at a 0.5 second rate
  4. Within 10 seconds of powering up, change switches 1 or 2 to "OFF". If these switches are not changed, the board will power up using the OEM default communication parameters
  5. LED 2 will flash indicating that the configuration memory is being erased
  6. Full memory erase takes up to 60 seconds
  7. When complete, only LEDs 1 & 4 will flash for 8 seconds
  8. The board will reboot 8 seconds after LEDs 1 & 4 stop flashing (no LEDs are on during this time) Mercury EP1501 Board.png

EP1501 DipSwitchOptions.png

All other switch settings are unassigned and reserved for future use.

Factory Default Communication Parameters:

Network: static IP address: 192.168.0.251

Subnet Mask: 255.255.0.0

Default Gateway: 192.168.0.1

DNS Server: 192.168.0.1

Host port: IP server, no encryption, port 3001, communication address: 0

Labels (1)
Labels:
  • EcoStruxure Access Expert
Tags (7)
  • Find more articles tagged with:
  • AlanWood22
  • bulk erase
  • dip switch
  • EP1501
  • factory reset
  • memory
  • reset
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore