Do Not Display Read Raw Data Events

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Do Not Display Read Raw Data Events
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • GavinHe
    GavinHe

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1631 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Do Not Display Read Raw Data Events

Sisko GavinHe Sisko
‎2022-11-23 03:57 PM

on ‎2022-11-23 03:57 PM

Issue

Read Raw Data events are being shown in the Event view when a valid card is presented at a reader

1. Read Raw On Both Doors.png

Product Line

EcoStruxure Security Expert

Environment

Security Expert

Cause

If a User does not have an access level for at least one object on an SP-C controller then the user record is not downloaded to the controller

Resolution

If the requirement is to stop the message appearing there is a setting on the Reader Expander that can be unset.  If using this method, there is no indication the user has attempted to access the door.

 

Navigate to Expanders -> Reader Expanders and select the appropriate Expander.  Select the Reader tab for the door that the Read Raw Data event should be removed from.  At the bottom under Misc Options un-check the ‘Display Card Detail when Invalid’ option.

2. Uncheck Display Card Detail.png

This option will need to be set for each reader connected to a door where the Read Raw Data event is to be removed. In this example the option was un-checked for the Office 01 Entry door and as seen in the image below, in comparison to the same sequence of events shown in the Issue section, the Read Raw Data event is only recorded for the Office 01 Stores door and not recorded for the Office 01 Entry door.

3. Read Raw Data for Office Entry Not Shown.png

Note: When the ‘Display Card Detail when Invalid’ option is enabled (by default) the reader expander will send the details of any unrecognized card (facility and card number) to the controller.  Un-checking the option means that Read Raw Data will not appear for that reader.

Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (3)
  • Find more articles tagged with:
  • AdamSteele24
  • GavinHeward22
  • HernanUruena23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore