Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

How to read the accuracy and repeatability on CO2 sensors

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to read the accuracy and repeatability on CO2 sensors
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PeterEdvik
    PeterEdvik
  • MikaelKrantz
    MikaelKrantz

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2544 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to read the accuracy and repeatability on CO2 sensors

Guinan MikaelKrantz Guinan
‎2022-11-24 01:44 AM

on ‎2022-11-24 01:44 AM

Issue

How to read and understand the accuracy and repeatability on CO2 sensors.

The sensors shows 380 ppm, is it defect?

Product Line

Field Devices

Environment

CO2 Sensors

Cause

Accuracy +- 30ppm +-2% of measured value

Repeatability +- 20ppm +-1% of measured value

Resolution

 

Accuracy

The accuracy of a unit is defined as the tolerance between the actual absolute gas concentration and the measured value. For example, if a unit has a specified accuracy of ±30ppm, this implies that the displayed value will be within 30 parts‐per‐million of the actual gas concentration under standard ambient operating conditions. If the gas concentration in a room is 400ppm, then the sensor is operating within rated parameters if it reads anywhere between 370ppm and 430ppm on average.

 

Repeatability

Repeatability is closely related to precision. Repeatability is defined as the variance in measured values of a known, unchanging gas sample upon repeat measurements. To put it another way repeatability is the range of acceptable values the sensor will read, relevant to a previous measurement, when measuring a gas, independent of the actual gas concentration. 

For example, if the gas concentration in a room is 400ppm and the sensor has a rated repeatability of ±10ppm, then if originally the sensor reads 420ppm, upon future measurements the sensor will read between 410ppm and 430ppm. 

Repeatability is generally specified as having a tighter tolerance than accuracy. Even if a sensor is reading a value that is slightly high when compared to the actual gas concentration, it is likely that it will read close to the same slightly higher value upon repeat measurements.

 

How to understand the accuracy and repeatability

Accuracy +- 30ppm +-2% of measured value
Repeatability +- 20ppm +-1% of measured value

Accuracy at 400ppm:

  •                     Min =  – (30 + 400*0.02) = -38
  •                     Max = + (30 + 400*0.02) = 38

Repeatability at 400pm:

  •                     Min = - (20 + 400*0.01) = -24
  •                     Max = (20+400*0.01) = 24

 

This means that in a 400ppm environment, the sensor output can vary between

  •                     400-38-24 = 328 ppm
  •                     400+38+24 = 462 ppm

Finally, based on the explanation given above, 380ppm would still be in spec.

However, another reason could be that the calibration was done in an environment that was not the “purest” and by doing so, an offset was created on the 400-baseline explaining why values below 400ppm are reported.

 

As said 380ppm is still in spec but the customer could try to recalibrate the CO2 sensor to see if it changes anything.

Labels (1)
Labels:
  • Field Devices
Tags (1)
  • Find more articles tagged with:
  • MikaelKrantz22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore