Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

.MTA file does not get updated when changing values through Vista or Xenta OP panel

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • .MTA file does not get updated when changing values through Vista or Xenta OP panel
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • PeterLarsen
    PeterLarsen
  • sesa150561
    sesa150561
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2419 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

.MTA file does not get updated when changing values through Vista or Xenta OP panel

Picard Product_Support
‎2018-09-06 01:49 PM

Last Updated: Picard RobertAndriolo Picard ‎2022-11-29 02:24 PM

Issue

  • .MTA file not updated
  • .MTA file does not show the correct value when exported/imported
  • The Menta project does not have the correct value when imported into a new database

Product Line

TAC Vista

Environment

  • Vista
  • Menta
  • Xenta OP

Cause

The upload/download parameter does not save any changes in values to the .MTA file. It only saves it to the device and Vista database. This means that if you export a project and import it to a new database the .MTA file will contain the initial values chosen when you last saved the Menta project. To get the values saved to the .MTA file, you need to edit the Menta project and save it again. However, to trigger the save correctly, you need to change the project. For example, add a comment or move a block, then hit save.

Resolution

 Below is the correct way to edit a project in a new database. 

  1. On the client PC, start by doing an upload parameter; this ensures that the values stored in the Xenta are present in the Vista database.
  2. Edit the Menta project(s) and add a comment (This can be a comment like "John brings the project home to make some changes") now the project can be saved, and all new values will be stored in the .MTA file. 
  3. Export the database/project
  4. Import the database/project to the new PC
  5. Make the desired changes
  6. Edit the Menta project(s) and add a comment (This can be a comment like "John has made the following changes ....") now the project can be saved, and all new values will be stored in the .MTA file.
  7. Export the database/project
  8. Import the database/project into the client's PC
  9. Now make a download parameter; this ensures the Xenta will get updated with the changes you have made.
Labels (1)
Labels:
  • TAC Vista
Tags (3)
  • Find more articles tagged with:
  • 5186
  • PeterLarsen22
  • RobertAndriolo22
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore