ZBuilder with two room sensors
  • ZBuilder with two room sensors
  • PeterEdvik
    PeterEdvik
  • MikaelKrantz
    MikaelKrantz
Guinan MikaelKrantz Guinan
‎2022-11-24 01:52 AM
on ‎2022-11-24 01:52 AM
How to configure two room sensors in ZBuilder.
ZBuilder
It is possible to configure TAC Xenta 121 or TAC Xenta 122 to use two room sensors via the ZBuilder tool.
In Zbuilder, under the tab Configuration, under Room unit, select the type of sensor you are going to use.
Select the tab I/O Setup,
Right click on the sensor and select Duplicate.
Move the sensors to the input you are going to use.
At the end of this session you will be able to:
  • Configure TAC Xenta 121/122 to use two room sensors.
  • Understand that the nvoSpaceTemp value is calculated as average value of the two sensors.
  • Understand that it is not possible to see the actual value of a single sensor when using two sensors.
[video]
Labels (2)
  • MikaelKrantz22